Copper for condensate pipes? Your opinion
RayWohlfarth
RayWohlfarth Member Posts: 1,893
I would never recommend or use copper for steam piping but someone asked about using it for the condensate return pipes. I have always recommended using schedule 80 BI pipe for the condensate and this person insists copper is better for the return. Would love your thoughts or experiences. Thanks
Ray Wohlfarth
Boiler Lessons
  • ScottSecor
    ScottSecor Member Posts: 1,020
    We have used schedule 80 steel on occasion, most often schedule 40 steel, sometimes copper type L or M.
    The schedule 80 was used at two schools that suffered from rotted returns on a regular basis. Approximately every five years the four inch welded returns would start to get pitted. After using schedule 40 the first time, we switched to 80. Same results... We decided to modify the piping slightly. The modifications helped, that retutn pipe is fine and now over twenty years old.
    Today, we often replace rotted steel returns with copper. To date I cannot recall one failure. However, if it is just a small section of rotted steel pipe we will often use steel again.
    If using threaded steel on returns, I definitely prefer cast iron fittings over steel fittings.
  • ChrisJ
    ChrisJ Member Posts: 17,060
    Most recommend not using copper for steam piping due to greater expansion with temperature, as well as difficulty soldering larger piping though some feel brazing may be ok. It tends to want to twist it self apart and crack joints, as well as apply more pressure trying to push the boiler sections apart. I have two straight connections going to radiators that are copper and they haven't bothered anyone for decades, so I leave them alone. There's no twisting etc and they're very short lengths.
    What is your reason for never recommending it for condensate? On most if not all home heating systems even PVC would almost work, it's just a little too hot at times for it. Copper is the perfect solution, really.
  • Waher
    Waher Member Posts: 361
    Galvanic corrosion could be an issue if the connection to cast iron/steel isn’t buffered by brass/bronze fittings. Providing a swing joint for thermal expansion might be a good idea if the run of copper is long enough.
  • Intplm.
    Intplm. Member Posts: 2,817
    Ive used copper with a brass transition. Seems to be a better result.
    ethicalpaul Member Posts: 8,077
    edited December 19
    Better in what way? ('m not challenging you, I just wondered what negative you saw from going copper to steel. Did you see a galvanic issue, or is it just something you are concerned about?)
    I did mine in steel just because it was easy and very short but really they should all be copper. The steel grows those corrosion bulge things which accelerates clogging (but it takes years). I can't even imagine a copper return ever clogging…condensate is far cleaner than people realize.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,506
    Definitely copper. As Paul said, steel is a breeding ground for sludge. And considering that the returns are always filled with water, there is no real concern of rapid thermal expansion.
    EBEBRATT-Ed Member Posts: 19,466
    edited December 19
    Its a hard thing to predict.
    Commercial building that use steam in some cases use higher pressures than the typical 2psi they should use. Higher pressure =higher temperatures. In many cases traps are neglected…….the whole system is neglected.
    Due to that steel pipe usually stands up to the abuse better. On commercial jobs it was common to spec #80 for condensate piping.
    I have seen old jobs with #40 that lasted for years with just normal issues.
    I have also seen 15ps steam jobs where the boiler feed pipe between the pump and the boilers were piped with schedule #40 and it rotted out in 2 years and replaced by schedule #80
    Copper is fine for residential.
    In my experience the largest factor is the make up water. A job that uses a lot of MU water will rot out fast. If the MU water is kept to minimum things are fine. No surprise I guess.
    On commercial jobs the boiler feed piping between the condensate or boiler feed tank and the boiler is always the first to go
    Not sure what the code is on this. Your not using copper on HP steam condensate that is for sure. That would never pass inspection.
  • ChrisJ
    I thought most high pressure steam systems use welded stainless steel pipe?
    I have never seen stainless on HP steam unless it was some type of food process boiler or something.
  • ChrisJ
    edited December 19
    Food processing, but I think power plants are also big on stainless, no?
    When I think high pressure steam, I think power generation.
  • RayWohlfarth
    Thank you all for your expertise.When I first got into the trade, the journeyman was an old steam guy and had rules, lots of rules. The first was no copper in a steam system anywhere. The second was schedule 80 for the condensate and schedule 40 for the steam. See you can teach an old dog new tricks.
    Ray Wohlfarth
    Boiler Lessons
    Gordo uses stainless steel now in parts of his Hartford loops and where it interfaces with the boiler, that is good because it's always rotting out there first
  • Intplm.
    Over the years, I have had a few issues with what seemed to be an electrolysis reaction. I wasnt sure what the cause of corrosion was for certain, but when I used a brass nipple transitioning to copper, most of the time the issues went away. I decided years ago to make it a habit. I had customers to answer to, not to mention a good reputation to maintain. I would sometimes use a brass coupling or even a stainless steel fitting that might have been left over from another job. It just worked (s), and that's good enough for me.
  • Intplm.
    I tried the Sch. 80 pipe/fittings. What I discovered was that it took twice as long for the corrosion to return from the Sch.40…go figure.
    mattmia2 Member Posts: 15,484
    ther's high pressure and then there's high pressure.