Indirect water heater as steam(water) to hydro zone HX (poor heat transfer)

Options
wcs5050
wcs5050 Member Posts: 174

My heat exchange from 200k res steam boiler set at 190degF to a 30 gal superstor set at 180degF is pathetic… looking at interior water quality after replacing a circulator I’m suspecting the SSU30 corrugated coil is totally fouled. Tank is 11 yrs old now. I inherited (as the service babysitter) the setup about 2 yrs ago. I’m considering a TFI Everhot external water heater, but also considering perhaps just a different brand of indirect tank… I’m done with HTP.
There is about 45k btu hydronic load connected.
I don’t want to turn up boiler water limit because I’m already getting passive steam heating when not requested, and the system is already wasting so much gas/energy.

Can anyone weigh in some thoughts.

Thanks.

Comments

  • mattmia2
    mattmia2 Member Posts: 16,025

    clean the coil out with acid then raise the ph on the boiler so it produces little mud. pumping the coil full of mud isn't HTP's fault.

    if you are just using it as a shell and tube hx you could run it the other way, put the boiler water in the tank and run the hot water loop water through the coil, then there'd be a lot more space for the mud.

    GGross
  • Jamie Hall
    Jamie Hall Member Posts: 27,010

    Changing to a different brand of heat exchanger or even an indirect is not going to fix the problem: 11 years of lack of maintenance. As @mattmia2 suggests, spend a little time and effort to clean and descale the poor thing, and flush it out a couple of times.

    If you do decide to splurge instead and spend a lot of money on a new system, also decide to maintain it properly so you're not there again in a few years.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • wcs5050
    wcs5050 Member Posts: 174

    I am the technician/operator that recently inherited care of this neglected system.

    I wasn’t clear…I’m seeing significant fouling on the hydronic side of the system not the steam side… I expect steam side sludge… it has had wet side clearing service and water treatment, but I can absolutely appreciate the possibility of sludge on the inside of the coil.

    If anyone has cut open a superstor specifically, they will see the outside surface of the coil is fin-corrugated. I’m suspecting this is caked up. I’m pretty sure this system ran for years without adequate water content and/or functional air elimination. I’m trying to rehabilitate it now.

    I’ll be sure not to speak lowly of brands in the future. Thanks for the check. Not a good look.

  • wcs5050
    wcs5050 Member Posts: 174

    What I meant was, I’m considering changing to a different brand/style of indirect that has smooth faced coil.

  • wcs5050
    wcs5050 Member Posts: 174

    To cleanse the outer face of the coil would be impossible now, wouldn’t you agree??

  • mattmia2
    mattmia2 Member Posts: 16,025

    you could possibly loosen it up with acid and flush it out. does stuff come out of the bottom tapping of the tank? the better question is why is a hot water system making so much sludge?

    wcs5050
  • wcs5050
    wcs5050 Member Posts: 174

    That was my question as well. Small pex radiant zone via mixing valve, and small fin tube baseboard zone. There is hardly any iron in the system. Maybe isolated to the circulator by low water content and poor air elimination.

  • wcs5050
    wcs5050 Member Posts: 174

    Flush attempt on coil inside is a worthy endeavor because the hydronic setup barely achieves 130degF in 20degF outdoor.

  • mattmia2
    mattmia2 Member Posts: 16,025

    leaking and a ton of makeup water will do that.

    wcs5050
  • Jamie Hall
    Jamie Hall Member Posts: 27,010

    oxygen barrier PEX? I hope??

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2wcs5050
  • hot_rod
    hot_rod Member Posts: 27,080

    the sludge would be on the part of the indirect connected to the boiler. If that is the coil, then that is the sludged portion

    If the tank is just the hydronic water, mineral scaling is possible. That is generally from ongoing fill water being added

    Descaling the outside if the coil is not so easy

    At that age??

    Go with a smooth coil rank

    Laars, bradford white, Lochinvar, Bock are some brands

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    wcs5050
  • mattmia2
    mattmia2 Member Posts: 16,025

    whatever rusted the circulator is going to rust a steel tank too.

  • wcs5050
    wcs5050 Member Posts: 174

    Thanks everyone. Very good points.

    The pex appears to be the first stadler viega orange/white which I believe is barrier. Good call on that anyway. I have another job where I recently discovered bon-barrier on some radiant, after progressively changing noisy circulators that grew rust into the impeller.

    I have make up water off at the moment and it appears to be holding steady.


    I was looking at Bradford white or Ideal. Both are all stainless with smooth outer coil.
    I’ll def be cutting this one open to see what the coil looks like.

  • mattmia2
    mattmia2 Member Posts: 16,025

    what are the temps at the 4 ports of the tank?

    bjohnhy
  • hot_rod
    hot_rod Member Posts: 27,080

    you are sure both circulators are spinning?

    The coil could thermosiphon from the boiler imitating a plugged coil?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2bjohnhywcs5050
  • bjohnhy
    bjohnhy Member Posts: 186

    You could just drop an endoscope camera down the TPV orifice. But that doesn't seem as interesting as cutting it open

    mattmia2wcs5050
  • wcs5050
    wcs5050 Member Posts: 174

    Hydronic circ for sure turning. 3 speed Grundfos on steam loop showing water hammer at quick close of ball valve.
    190 at coil supply, 5-10 below on coil return. With hydronic flowing barely getting to 130. If I close off supplies tank slowly recovers… I mean slowly. Worth looking in on the primary/coil circ I suppose.
    $40 coil in there, $200 labor ;)

  • hot_rod
    hot_rod Member Posts: 27,080

    This was my experience with a finned coil tank, less than 1 year into the tank the owner started to notice DHW production falling off. I did the boiler work, a different plumber supplied the indirect. Guess who sorted it out.

    Yes it was hard water, but…

    Screenshot 2025-12-17 at 5.11.01 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    wcs5050
  • mattmia2
    mattmia2 Member Posts: 16,025

    if the coil is removable you can dip it in acid and clean it. or maybe get 2 and rotate them. only $40 for the coil? put anti seize on the bolts so it comes out again later.

  • mattmia2
    mattmia2 Member Posts: 16,025

    but as far as i know the coil on a superstore is not removable.

    bjohnhyGGross
  • wcs5050
    wcs5050 Member Posts: 174

    I’m saying cut it out for $40 scrap retrieval. Haha