Trying to see what would make the most sense on my subtractive pressuretrol. Should I do 2psi main & 1psi differential, 2psi main & 0.5psi differential, or 1psi main & 0.5psi differential? It is a one pipe system, No insulation in the house (located in Northeast too), EDR of all radiators is about 605, have a gorton #2 for main venting, and varivalves at radiators (planning on replacing over the next few years)
    Jamie Hall Member Posts: 27,188
    Any of those would work… my own whimsy would be 1.5 psig main, 0.7 psig differential.
    EBEBRATT-Ed Member Posts: 20,044
    Try running 1.5 cut off and make the differential as wide as possible. If you make it too wide the boiler won't restart.