Filtration For Condensing Boilers?
scatgo
scatgo Member Posts: 75
From what i undersatnde mod cons have narrow passages that can clog easy. If you are going to set on up on a old cast iron system a flush is a must but is it possible to have some sort of filter on the retune water side to make sure things don't jam up?
    EBEBRATT-Ed Member Posts: 20,070
    Yes, you can get a combination filter and magnetic separator. See attached. Other companies make them including Caleffi.
    mattmia2scatgo
    mattmia2 Member Posts: 16,430
    more generically called a magnetic dirt separator though the issue is more with wet rotor circulators than with boilers. since they are magnetic, wet rotor circulators tend to get iron particles from the system building up in their bearings.
  • scatgo
    Thanks, brother. I just couldn't find anything like that with a goggle search.
    Happy thanksgiving.
    Peace
    i don't know anyone that would call it a filter but that is what the supplyhouse.com category calls them:
    https://www.supplyhouse.com/Magnetic-Boiler-Filters-28160000
    you could also put a strainer in the system.
    hot_rod Member Posts: 27,301
    High efficiency boilers and ECM circs need some good particular protection. They are a couple steps beyond a basic Y strainer.
    A separator forces particles into the bell of the unit, to flush out. Whereas as Y strainers trap particles in the flow stream. Y strainers cannot grab the tiny magnetite particles.
    A mag separator does both particle, down to 5 micron, and magnetic particles .05 micron.
    Screenshot 2025-11-28 at 4.37.22 PM.png Screenshot 2025-11-28 at 4.43.31 PM.png
  • jumper
    jumper Member Posts: 2,522
    When replacing or installing boilers I'd recommend at least some sort of sidestream filter. Often that recommendation was declined.