Makeup water causing boiler failure due to thermal shock
People ask me about this a lot so I wanted to get some good info to pass along instead of my own anecdotal opinion (shocker, right? 😅).
Have any of you fine folks ever, with your own two eyes, seen a boiler crack, burst, or otherwise fail due to someone adding cold/room temperature water to it when it was at a normal operating temperature (of 212F-220F for a steam boiler or let's say 180F for a water "boiler")?
Let me repeat:
- the boiler was at normal operating temperature
- someone added cold/room temperature water to it
- it cracked/failed at that moment in an obvious way
- you saw it with your own eyes (heard it from a guy definitely does not count)
Thanks!
Free NJ and remote steam advice:
https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos:
https://bit.ly/3sZW1el
If it causes a problem I think it is likely to be something that warps and leaks later and won't be something you can definitively tie to the thermal shock. Usually the feed is relatively slow compared to the volume of the boiler so the temp change isn't that fast unless the boiler was almost empty.
I think the speed and gpm flow would be a factor. Typical fill valves feed maybe 3 gpm, fast fill lever maybe 5 or so. A fast fill bypass, 1/2" could fill 8 gpm or more
I'm not sure where a steam boiler fills, or what type of valve, many hydronics fill at the expansion tank, so the water temperature to the boiler would be diluted somewhat.
Tank type water heaters can get hit with water temperature in the high 30°F temperatures, right against the burner plate at the bottom.
so I take it that means you’ve never seen it 🙂
Thanks! Do you believe it would crack if you didn't feed it very slowly?
I was told to always have an engine running as you add cold water to it if it had been overheating, allowing it to blend the water in. Obviously allowing it to cool some before messing around. No idea if it matters now, or, ever mattered. But cars etc hold a whole lot less water than a steam or HW boiler.
With a boiler, assuming it has a decent amount of water in it, it does seem a bit of a stretch to make it crack by adding a gallon of ice cold water to several gallons of boiling water.
engine blocks usually warp and you get head gasket failures soon after.
Do they warp from adding coolant, or from running overheated just before adding coolant?
This is why I asked the question the way I asked it. Correlation vs causation, etc 😅
my understanding is that about the only way that bmw inline 6's die is if the cooling system fails and you go with some option other than towing it/fixing it by the side of the road and the compromised cooling system causes the giant aluminum block to warp then you have head gasket problems.
I guess it's a good thing we don't heat our homes with them!
this happened wile i was typing. I'm not sure if people have narrowed down if it is the overheating or the trying to fix the overheating by adding water(or trying to continue to drive it with a leaking cooling system after you've added water). I think it can be both but your best bet is to be patient and let it cool down before adding water.
Well I like my old boiler since it is simple, works well and I can run it from just a battery in the event of a power failure.
So I'm not tempting fate. Just don't want to find out the hard way. So I feed it really slow.
If I feed it faster and it is not firing at the time you can hear some ticking like when you shut off a car engine.
One Pipe System0 -
I have seen a boiler crack form operating it than opening the water feed valve. The time it happened was not "Normal Operation" though. it was being dry fired when I arrived and I told the customer to shut off the switch. After they shut off the switch, they asked my why it was not heating the radiators, I told them the home was winterized and the boiler water was drained. There was no water in the system.
With that and before I could stop them the cold water feed was opened and Pop… Fizzz…. the boiler cracked then and there. Not covered under the warranty. The boiler needed to be replaced.
This was in a summer home that has a Weil McLain WGO-3 and the kids came down for spring break without the parents knowledge. That is, until the parents needed a new boiler.
Under normal conditions a boiler "at operating temperature" will not fail from thermal shock when adding makeup water. Unless the installer piped the makeup water in some stupid location. (Never say Never)
that had to be quite a facepalm moment Ed!
I imagine the boiler warranty was gone as soon as it was dry-fired (although that might be difficult to determine without the crack)
There was no question about the dry firing Paul, As soon as the WM rep looked at the front door opening, the warranty was voided. I still needed to try though.
Another boiler (a steamer) I installed in a church dry fired as a result of a run away gas valve. The clocks in the church were all stopped at 10:48 (PM) and I got a call at 2:00PM from the fire chief of Cape May. (the West Cape May fire chief was also the fuel oil dealer for the church and he was on scene.) I arrived at 2:45 to see a half dozen fire and police vehicles on scene and steam still blowing out of the boiler room door.
The best guess was that the electrical event that caused the clocks to stop must have been some type of surge that happened while the dual fuel burner was operating on natural gas. The gas velvet must have stuck open as a result of the surge. With all the electrical out and the gas valve stuck open. The flame kept going thru the burner even though there was no electricity to operate the combustion blower …Or the boiler feed pump. Eventually the boiler water line dropped below the minimum and the boiler cracked. Steam was pouring out of the boiler room chimney combustion air openings and a window that was left open for some reason. The gas continued to burn inside the boiler until the fire department shut off the gas at the gas meter.
I was called just to tell everyone the boiler was safe to keep shut down and after I turned off the gas to the boiler, I could relight all the pilots of the rest of the appliances in the building. Hartford Boiler Insurance paid for the replacement boiler and most of the labor. Got her back up and running within 5 days. They scrapped the dual fuel burner with the replacement boiler. Gas only this time. “Oil Company not happy”
I would think what could be a problem is if someone drained a hot boiler completely to flush it and quickly refilled it with cold water
my granny’s cast iron pot never minded
the coating usually flakes off my cast iron when i do stuff like that.
That's an odd statement.
My best answer to your question is "NO". (40+ years in the field). I did however one time see an H B Smith 4500 steam boiler lift off it's base, 3"-4" inches when a helper tried to drain that flooded off line and cold boiler. There were 2 other boilers that were carrying the steam load at that time. I would like to say that I remained calm but no, I did not. There was no boiler damage, just a lot of steam hammer.
I have seen quite a few melted cast iron sectional and steel fire tub boilers, and been in the room when 2 units in different boiler plants exploded due to fuel problems. One was an Erie City 20,000 lb/hr high pressure steam water tube boiler and the other was a small cast iron boiler. It is an experience that you never forget.
thanks @retiredguy !
now part 2: do you think it’s possible to hurt a residential steam or water boiler by adding water too fast (assuming no dry fire condition has occurred)
I think we should ask what too fast is.
60 PSI with 1/2" valve wide open? 3/4" valve wide open?
anything
Not really. The gas valve locked open as a result of the electrical event keeps fuel going. That same electrical event on an oil burner would stop the fuel from pumping from the tank to the combustion chamber.
True,
But I find it odd because IF it was a forced air system instead, it wouldn't have mattered at all.
There's a ton of IF's, like the classic "if your aunt had…….." joke.That's all.
-1 -
Warm air furnaces are off topic
Not many churches built in the 1800's have 1.5 million BTU furnaces to heat them. This one happens to have had a steam boiler, so I decided it was less expensive to replace the 1930's steam boiler with another steam boiler in 2008. It just seemed easier than ripping out all those steam radiators and installing a bunch of duct work. I thought you might agree too, but I could be wrong. the failure happened in 2019 so I got the same boiler again.
And didn’t this start out as a question about thermal shock? You certainly can't be thinking of letting a bunch of cold water cascade over a warm air heat exchanger. I can't imagine any reason for that to happen on purpose. Can You?
So cut to the chase - @ethicalpaul are you suggesting that damage to a boiler due to thermal shock is just an unfounded myth?
In my house there is a scenario that seems could lead to thermal shock:
- Zone1 calls for heat and the boiler water gets up to say 150. This is a small zone for just the family room with baseboard radiators.
- Zone2 calls for heat and introduces water into the boiler at say 65 (due to nightly setback). This is a large zone with lots of water and many floor standing radiators.
- Water temperature in boiler rapidly drops to 65, while cast iron jacket remains initially at 150, causing metal to rapidly drop in temperature - thermal shock or stress.
Is that a bad thing, or can the boiler handle it? - In my case I initially installed a system bypass, then later re-piped to use a thermostatic mixing valve, not just for thermal stress, but also to avoid condensation from low temperature return water.
Thoughts?
Eric Peterson0 -
Will thermal shock hurt a boiler and how much thermal shock? Who knows?
We were told in school that you could drain and refill a steel boiler with cold water but don't do it with CI. That's good enough for me.
I also have had the experience that @retiredguy mentioned about draining a boiler that the steam is connected to another operating boiler.
You will only do that one time believe me. The idle boiler is cold and the steam rushing in condenses and causes hammer. 1700 times a volume reduction it is a noise you never forget. It is a lot more powerful than you would think.
But as far as thermal shock why take the chance?
It will not help the boiler, it will cause stress to the cast iron.
We had a CI boiler Smith 2500 that the lwco failed. My coworker showed up and the boiler was red hot and glowing. He went back the next day after it had cooled and the boiler held water. He installed a new LWCO and fired it up and made steam. No leaks so we let it run.
A few days later it puked water all over.
2 -
No, but if it is not a myth I would think that someone here would have seen it at least one time in their long and storied carriers, hence my question.
It does seem unlikely to me that any cast iron vessel would really mind seeing its 212 degree water contents mixed with incoming water at 50-70F
The part above the water line in a steam boiler could be and likely is significantly above ~212 f since it won't be able to transfer heat to the steam gas nearly as efficiently as it can transfer to the liquid water. I wonder is surging and thermal shock and maybe particularly not resistant to thermal shock construction is how the problematic burnahms run in to problems.
Yeah, running a boiler to red hot condition seems like a real deal breaker to me. That's why I crafted my question the way I did 🙂
My brain just thawed out so now I remember when H B Smith series 28 sections would crack on hot water systems when they would switch from night set back to day time temps. This was before they added a pump that would pump water from the discharge to the boiler's inlet to temper the water. (this was similar to a primary/secondary loop set up) The company I worked for would usually add a 2" B&G pump to do the pumping' They originally tried using a series 100 B&G pump but they would not flow enough water. A few years later it became part of the boiler's specs and every other mfg that made similar boilers followed suit.
Wow, for a boiler to actually crack when seeing input water just from a nighttime setback must require some real creative engineering!!
Those are big boilers in big buildings. think the size of a medium size shed.
- 87.2K THE MAIN WALL
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 6.4K Radiant Heating
- 15.6K Strictly Steam