How does a radiator vent just fall off?
Options
CoachBoilermaker
Posts: 466
Friend's house. This is the 2nd one I've seen. Vent just laying of the floor next to the radiator. How does this happen?
0
Comments
-
-
-
Try re-tapping 1/8" pipe thread first. Many times the threads just need cleaning out. If that doesn't work, tap 1/4" pipe thread and install a bushing as @EBEBRATT-Ed said.
2 -
They sometimes rot out at the threads. Do what is said above for the fix.
0