Friend's house. This is the 2nd one I've seen. Vent just laying of the floor next to the radiator. How does this happen?

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,172

    Sloppy threads. May need to drill it for a 1/4" pipe tap and retap and use a 1/4 x 1/8" bushing

    STEAM DOCTOREdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 15,067

    also may have been bumped hard numerous times and damaged the threads.

    EdTheHeaterMan
  • Steamhead
    Steamhead Member Posts: 18,147

    Try re-tapping 1/8" pipe thread first. Many times the threads just need cleaning out. If that doesn't work, tap 1/4" pipe thread and install a bushing as @EBEBRATT-Ed said.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    EdTheHeaterManLong Beach Ed
  • Intplm.
    Intplm. Member Posts: 2,795

    They sometimes rot out at the threads. Do what is said above for the fix.