Heat Exchanger vs Full Replacement
BMcGahan
BMcGahan Member Posts: 9
edited October 2025 in Strictly Steam
I have a quote to replace the heat exchange for $ or full boiler replacement for $$ for steam boiler. Boiler is 18 years old. Thoughts?
    mattmia2 Member Posts: 17,206
    please edit to remove prices. we cant' discuss prices here although you could describe the relative costs. i'd just replace the hx if they are going to do it right and the current system works well.
    HeatingHelp.com
    pecmsg Member Posts: 7,188
    address the reason you’re replacing it at 18 years that’s a young life for a boiler
    mattmia2GGross
    HVACNUT Member Posts: 7,507
    edited October 2025
    I'd sign up for 3 HX replacements and still keep $2K in my pocket.
  • BMcGahan
    Sorry about adding the prices. Im thinking I might go with replacing the heat exchange. The original installers also used copper piping. Should I have that replaced? Its not leaking but apparently copper is no good.
  • GGross
    GGross Member Posts: 1,940
    post pics of the piping I'd wager folks here can come up with a laundry list of install issues
    as said if it’s a Burnham then that might be the life. I’d replace it.
    anyone else find out why it failed.
  • BMcGahan
    Attached is the piping and the heat exchanger.
  • BMcGahan
    It's a Dunkirk.
    ethicalpaul Member Posts: 8,922
    Pardon my ignorance but isn't the "heat exchanger" basically the whole cast iron part of the boiler, which is to say, the whole boiler?
    How could you replace the "heat exchanger" for less than 1/3 the cost of a boiler? I must be missing something.
  • ChrisJ
    ChrisJ Member Posts: 17,481
    edited October 2025
    If they buy an assembled boiler it's actually more work to change just the block.
    I don't think the sheet metal and trim etc cost much.
    The pricing does seem peculiar.
  • KC_Jones
    KC_Jones Member Posts: 5,936
    I'd be more concerned with proper piping techniques than if it's copper instead of black pipe. The bit I see in the pics the boiler is piped wrong, and maybe even the wrong pipe size. That style boiler is very sensitive to proper piping. Now if they put a new one in and pipe it properly, they better use black pipe for the steam side at least.
    I'm with Paul, I don't see how they replace the heat exchanger that much cheaper than the whole boiler considering they have to get into the same piping for either job.
    2014 Weil Mclain EG-40
    You’ve got a leak somewhere!
    Fix it.
    edited October 2025
    improper piping can pull the sections of the boiler apart, that may be what happened here but the pictures are way too close to see how it is piped. it is like those close up object puzzles.
    EBEBRATT-Ed Member Posts: 20,387
    I know we can't talk prices, but something seems out of wack to me. Not a very large boiler.
  • BMcGahan
    Here are better pictures of the piping
    it is only connected to one side of the boiler?
  • BMcGahan
    Yes, connected to the back.
    hopefully the cost difference is replacing the copper special with proper near boiler piping with the new boiler.