Multiple temperatures on single zone with single circulator pump?

inaun
inaun Member Posts: 8

I am replacing non oxygen barrier pipe (polybutylene) for underfloor heating in a section of my house with 2 small bedrooms and an open concept space for dining room / office. Boiler output temp varies from 120 to 180 depending on demand / outside temps.

I don't have good access to the bedrooms to replace piping without significant tear-out and repair, so planning on putting baseboard radiators in them instead (8 feet of radiator per room). The open room will remain underfloor heat, with two loops approx 200 feet per loop. Underfloor piping will be sandwiched between subfloor and premium laminate flooring, so low temperature setting in floor. Because the total space is less than 1000 feet and has similar heating needs, one zone seems to make sense. I'd like to use a single circulator pump, since a standard pump supplies enough flow to run the radiators and the two loops. However, there does not seem to be a "textbook" way of providing separate temperatures without two pumps.

What I'm wondering is if something like this would be worth trying. I need to do the calculations to be sure, but I don't think the water returning from radiators will have lost enough temperature to drop below target temperature for underfloor. Apologies up front for the poor drawing.

multi-temp.png

Comments

  • inaun
    inaun Member Posts: 8

    I should have also noted this is just one zone in a larger system. The feed and return are from/to the primary loop.

  • hot_rod
    hot_rod Member Posts: 25,707

    what about using panel radiators and running one low temperature system. The lower the boiler operating temperature the better the efficiency. Even with cast or non condensing boilers

    Do you have a heatloss number for all the rooms? That would help size and select heat emitters

    In your drawing how would the radiators return to the “blue” return piping?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    PC7060
  • 109A_5
    109A_5 Member Posts: 2,821
    edited October 3

    I thinking that will be an interesting balancing act between emitter dissipation and the heat loss of the different rooms. You don't want one room 65 degrees and the other 72 degrees. You may need other 'local' control(s) to modulate or bypass the hotter room, assuming the boiler's zone thermostat is in the cooler room.

    " In your drawing how would the radiators return to the “blue” return piping? "

    I would say through the underfloor loops.

    To me, the added (?) circulator (circulator sizing ?) hopefully creates an added parasitic flow through the cold port of the mixing valve (Violet arrow) to lower the Underfloor supply temperature, assuming the return temperature is low enough to do so.

    If that is the only circulator in that loop the rooms with the radiators may go through wider temperature swings.

    image.png

    "open room will remain underfloor heat"

    What limits the water temperature to this zone now ?

    If making them two different zones is like major construction, I'd try it and see how it works out, if it fails well you know what you need to do.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 14,246

    A second circulator will be the least of your costs here.

    You could use the non oxygen barrier loops you can't replace by isolating them with a heat exchanger and using a nonferrous circulator instead of installing new emitters.

  • inaun
    inaun Member Posts: 8

    Thanks. That was my first thought, then I looked at the cost of panel radiators compared to baseboard for the size I'd need running at lower temperature. Not in the budget.

    Radiators would not return directly to the cold side. Rather they would return through the hot inlet of the mixing valve, through the radiant floor loops, then on to cold.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,598

    I think you will have problems balancing the system. I would use two pumps 1 for the radiant and 1 for the base board.

    mattmia2
  • inaun
    inaun Member Posts: 8

    Right now there are mixing valves on each line off the manifold (Watts tempering valves). I honestly don't quite know how they are working, because there is a single pump pushing into the manifold, thus pumping into the hot water inlet side of each valve. Each room and the open space have zone valves that turn on or off, controlled by thermostats in each room. Some time back I changed wiring so only the "main" thermostat can turn boiler on (which is in short hallway leading from open space to rooms). I still allow the room thermostats to shut down a zone, even though they can't activate the boiler or pump. One of the rooms will always be colder right now, because the installer apparently didn't put any insulation under piping — and didn't fix after realizing his mistake (I met him some time back, and he was kind enough to tell me why that room is always cold). There is a basement under the rooms. We don't really run the heat down there except on really cold days, but it still stays moderately warm just from the underfloor pipes above.

  • inaun
    inaun Member Posts: 8

    I agree about a second circ pump not adding a lot of cost to the project. I just started to think about how I don't need it from a flow perspective — only to pump out of the mix from the valve instead of in to the hot. So that got me thinking about if I could make it flow right with a single pump. My biggest concerns are the unknowns of

    1) Will the mixing valve open too much on the cold side to properly flow the radiators? If this does happen, the valve should close cold side back down fairly quickly to satisfy need for higher temp in the floor loops. But the radiators would then "surge" as they rely on draw from hot side of the valve.

    2) Will the water temp from the radiators in real-world follow calculated loss to deliver sufficient temp to the floor (especially considering the output temp of the boiler varies…again in theory all good since boiler temp is higher in cold weather…but theory and reality don't always match!

    If this seems like something worth trying, I can do so knowing I might need to add the second pump if it does not work. I'll be working with PEX, and set up the layout to facilitate that modification without too much headache.

    But…if it's one of those "no way that's going to work" things…

  • inaun
    inaun Member Posts: 8

    Also considered the heat exchanger route…very seriously. What pushed me over is the polyb that is about 30 years old, combined with the insulation issue making my son's room cold (yea, he picked that one…have a portable electric he uses if it's too cold). I know a lot of the polyb issues were due to the fittings (checked and we have brass with crimp rings everywhere I can see, so should be fine there). But even if it doesn't leak at some point, when we sell the inspector is going to flag all that problematic pipe.

  • inaun
    inaun Member Posts: 8

    Appreciate all the thoughtful comments and thought here! I know this is one of those not-normally-done things, so definitely love that you are seriously considering the design instead of just razzing me for going off textbook!

  • inaun
    inaun Member Posts: 8

    Slight change based on comments about balancing out room temperatures, since I obviously can't just reduce flow on room radiators without impacting floor. Added a bypass line to allow reducing radiator flow in rooms as needed. Agree that balancing would still be fiddly to close down radiators and open up bypass line to get the right temps.

    multi-temp.png
  • mattmia2
    mattmia2 Member Posts: 14,246

    oh, i misread, i thought it was polyethylene. with pb abandonment is probably the right way to go.

  • hot_rod
    hot_rod Member Posts: 25,707

    the main issue with poly B was it did not have an oxygen barrier. Most of it anyways, Infloor had some with an O2 barrier

    Without a barrier It would allow O2 into the system dissolving any ferrous material. The hotter the fluid temperature the higher the rate of O2 ingress, so fin tube was a bad match. Certain chemicals in the water could make it brittle

    Then the breakdown of metals to magnetite and hematite would sludge the system. In some cases blocking the tube completely

    A mod con and or ECM circs will not fare well with PB

    Typical thermostatic mix valves are very low Cv, 2-3. What kind of flows are you needing for the two systems? What type of boiler?

    With the two systems in series, a manual 3 way valve might be a better option

    But we all agree two circs is the best, no guesswork, answer

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,129
    edited October 4

    I can only guess that since you have non Oxygen Barrier tubing, the boiler is a non ferrous material like stainless steel and the pump is stainless steel or bronze. I learned this the hard way by installing a cast iron boiler to replace a GloCore Stainless steel boiler on a non barrier tubing system. It was a disaster. After 2 years of operation, the tubing was caked with mud from all the oxygen entering the system and causing the CI Boiler to turn to rust. Once I figured out the floor heat was non barrier tubing, I needed to flush all the tubes individually with high pressure water (and there were 4 zones with 16 or more loops per zone) then I purchased a stainless steel heat exchanger to separate the boiler from the floor system. I could go on forever about that job, but needless to say I learned an expensive lesson there.

    So now you have a 4 loop zone that has 2 loops that you need to replace for some reason. Your 3/4" fin tube low cost baseboard radiators will be a good choice however you need a second circulator in order to get the proper flow thru the baseboard radiators and you need to get the lower temperature loop to operate independently of the high temperature loop. I can illustrate this using hypothetical flow rates and temperatures using your drawing

    The exact temperatures and flow rates will vary based on your actual as-built system.  The temperatures and flow rates are for illustration purposes only.

    Screenshot 2025-10-03 at 8.13.02 PM.png

    I am guessing that the zone you are referencing may have looked like the top zone in this illustration. Radiant loops on average have a flow rate of 1/2 GPM and the low temperature should not go over 120° With that in mind that zone will circulate about 2 GPM under normal steady state conditions. the temperature drop across that floor will be about 10°. So that is how I guesstimated the temperatures and flow rates

    ************************************************

    Looking at the second (middle) zone is your proposed piping arrangement with only one circulator. The pump will have only 2 of the original 4 loops to push water thru.  Since that pump will end up a little higher on the pump curve, let’s say that the pump will try to force ¾ GPM thru that remaining two loops and that will be a total of 1.5 GPM to the zone.  But that is thru the radiant floor loops after it gets mixed.  So how does that hot water get to the mix hot in port?  You pull it thru the baseboard radiators and that 160° water will drop in temperature as it goes thru each of the two radiators.  As those radiators give off their heat from the 160° supply water, the exiting water from those radiators may drop below the 120° needed for the low temperature floor….  But let's not consider that possibility and think positive.  The water now entering the HOT inlet to the mix valve might be 130° and you will need to mix the 112° return water into the mix valve cold inlet to get the 120° low temperature.  The reason the return from the radiant floor is only 112 is because it moved thru the floor faster at ¾ GPM as a result of your redesign.  Now that lower temperature Hot water will need less Cold water to mix to get 120° the numbers might look like this:

    112° at .75 GPM and 130  @ .75 GPM will get you 120° 1.5 GPM so the hot water entering the zone is no longer 2 GPM but has dropped to 1 GPM and the temperature drop is less.  It might work fine in mild weather, but that equals less BTUh delivered to that zone. You will not find this out until the coldest days of the winter when you can least afford to turn off the heat to redesign the system. 

    ************************************************

    The bottom design will allow you to move 4 GPM 180° water thru the baseboard heaters in order to get maximum capacity from them. The radiant floor will also be able to have the flow adjusted to the 0.5 GPM for each of the two remaining loops. You will also need to add a circulator relay and a thermostat in that zone in order to operate the high temperature pump.  The high temperature pump must be stainless steel or bronze since it is located on the system that is connected to the non-barrier tubing.   

    If you ever get a new boiler for any reason, you will need to stay away from steel or cast iron boilers, or you will find out the hard way like I did about that problem. Stainless steel heat exchanger, copper heat exchanger, or aluminum heat exchanger boilers are the only ones you can choose from.  But check with the boiler manufacturer before you connect it to your non-barrier tubing system.   

    I hope this helps you to understand that your idea, in concept may make sense, but in reality may not work satisfactorily.

    Mr. Ed

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • DCContrarian
    DCContrarian Member Posts: 1,246

    As drawn, it can't work.

    There is nothing to drive cold water flow through the mixing valve. Water needs a pressure differential to flow, the pressure at the tee on the outlet is going to be lower than at the mixing valve, nothing is going to cause water to flow in that direction. Mixing valves don't suck.

    With no cold water flow, the mixing valve will shut if the water presented to it is warmer than the set point. The entire flow of the circuit flows through the mixing valve, so when that happens the entire circuit shuts off, dead-heading the circulator. Depending on the circulator type that might be something you want to avoid.

    The only way this can work with one circulator is if the two parts are in series. There is some chance — although vanishingly small — that both parts can deliver their optimal performance with the same flow. If not, you can put a bypass pipe with balancing valve on the part that needs less flow.

    I suspect that this system has never worked. As a general note — more to the other readers of the forum — the biggest mistake you can make with hydronics, and we see it all the time, is to assume that things will "just work." People are pouring a concrete slab, and they assume that so long as the put in as much tubing as will fit everything will work out. It won't. These systems need to be engineered.

    I know this is not the answer you want to hear, but before investing any time or money into this system I would do some back-of-the-envelope engineering to determine whether it's actually possible that it could ever work. That means doing a room-by-room heating load calculation and then estimating the heat-providing capacity of the radiators and the in-floor loops, and seeing if there is any combination of flows where both can provide the proper amount of heat needed for their respective rooms. This is important because there is no guarantee that they can; instead, I would say it's rather unlikely.

  • Kaos
    Kaos Member Posts: 736
    edited October 4

    As drawn by OP, the setup will work. The key is to have only a reasonable delta T across the high temp loop. 8' of baseboards won't drop the temp much and won't be all that much extra pressure drop. Essentially the baseboard will look like an extra long supply pipe to the low temp zone.

    I wouldn't bother with any bypass, get baseboards with adjustable louvers for local temperature control. If you want to get fancy, you can get a zone valve as a bypass with a local thermostat (you'll need a valve on the baseboard to add a bit of restriction for this to work).

    8' of baseboard is on the small side if you want to use lower water temps. I would go for a bit longer, never hurts.

  • hot_rod
    hot_rod Member Posts: 25,707

    is it worth the experiment for the cost of an additional circ?

    Find them on ebay for 35 bucks, usually.

    Then you have the flow and control you really desire

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,129

    @hot_rod, since this system operated with non barrier tubing, I'm guessing that the SS or Bronze pump is not going to be that low cost

    @Kaos says "it will work." but ALL of the water being pushed or pulled thru that zone (look at my middle illustration above) MUST flow thru 2 radiant floor tube loops. The existing pump was fine moving about 2 GPM thru 4 tubing loops. I don't believe that you can get the same BTUh thru just 2 loops using that same pump. My guess is that @inaun is not purchasing another pump with more GPM and pump head to do the job. My guess is that they are going to use the existing pump. The design is flawed.

    @DCContrarian indicated "I suspect that this system has never worked". I might disagree with this. 800 feet of polybutylene pipe was an older radiant floor system. look at the top piping design in my illustration above. I had a customer with one of these systems. The brand name was InFloor ™ and I found out the hard way about non barrier tubing when replacing a SS HX boiler with a CI boiler.(see my previous post). I have a feeling that the four 200 foot loop zone worked fine for many years, along with all the other zones that were most likely installed the same way.

    I believe that this project for replacing 2 of the 4 loops with baseboard MUST use 2 different pumps. One pump for the 4 GPM flow rate thru the high temperature loop, the existing circulator pump for the remaining two radiant floor loops.

    @inaun…. One more note to clarify the baseboard loop. Do not install the 16 ft of baseboard as two separate parallel loops. 16 feet of baseboard is small enough to be one series loop and will be easier to purge air from the single loop

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • DCContrarian
    DCContrarian Member Posts: 1,246

    In the original drawing, what would make any water flow down from the tee drawn in blue? To the extent there's any pressure difference, the pressure at the tee is going to be lower than at the mixing valve, water will want to flow up there.

  • DCContrarian
    DCContrarian Member Posts: 1,246

    Here's what I see as the fundamental problem with this layout: the water flow through the radiators is going to be the same as through the in-floor tubing. Which means that the control strategy for both has to be the same. But the optimal control strategies are very different. So even if you could get it working where the flows and temperature drops are what you want, it's not going to be able to deliver consistent comfort.

  • Kaos
    Kaos Member Posts: 736

    @EdTheHeaterMan The setup doesn't need the same flow as the extra heat now comes from higher supply temperature, instead of 4gpm 10f delta, you run 2gpm 20f delta. With a modcon, higher supply temperature is free as long as the RWT is about the same which would be in case of a series setup.

    @DCContrarian The pump creates a low pressure at the inlet, depending on the position of the mix valve, it will "suck in" water from the blue T without issues. Control can be a challenge but as long as the baseboard emitters are oversized, you can always close the louvers on it to reduce output. You don't have individual control of the series zone, but could be set up to get a reasonable balance.

  • 109A_5
    109A_5 Member Posts: 2,821

    If the series configuration has to be used, I would not fool with louvers I would have a normally closed (in series with the baseboard) and a normally open (in parallel (bypass) with the baseboard) zone valves controlled by a local thermostat in the baseboard room to limit the temperature.

    No call for heat it is 100% in bypass mode, with a call for heat the bypass is closed off and the full flow is through the baseboard. It would not control the circulator or the boiler.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,129

    There is a lot of ideas being floated here. I would like to know what @hot_rod, @109A_5, @mattmia2, @Kaos and @DCContrarian think regarding diagram B and Diagram C below. Without more input from @inaun I can only make assumption that in my illustration A = something that has been working fine for years and now has 2 bad poly tubing loops that need to be addressed.

    The poly tubing does not have an oxygen barrier

    That means that the boiler and all the accessories are not cast iron or steel. They all must be made of Copper, Bronze or Stainless steel. Can we all agree on that?

    Trying to fix the "failed tubing" heated area with copper baseboard it the lowest cost way to replace the heat in the rooms that no longer have working floor heat. Can we agree on that?

    Screenshot 2025-10-05 at 10.03.12 PM.png

    What @inaun wants to do is the lowest cost way that will work. One of the ideas floated is to use the existing circulator to move heated water through both the baseboard and the radiant floor tubing with no actual control over the flow rate except for the manifold connections from the working tubing loops, as illustrated in diagram B above. I personally don't see it providing 10,000 BTU of heat in the way that diagram A is providing. 10,000 BTU of heat (2 GPM @ 10° ∆T) You can not get the same amount of heat that 4 poly tubes can provide when you are trying to put that same amount of heat thru 2 poly tubes. It ain't gonna happen.

    Does anyone thing that you can? Really?

    Does anyone think that diagram C is not going to work? If not, why not? With the proper relay you can operate both pumps with the same thermostat. It is just gonna cost a little more to buy a new bronze or stainless pump and a relay to operate it. Not ideal for keeping cost down, but when the temperature drops to design temperature, @inaun will find out too late that diagram B was a mistake.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Member Posts: 2,821

    @EdTheHeaterMan personally I would go with your recommended 'C' option with each circulator being its own sub zone (I believe they are separate rooms), since that will most likely provide the best comfort control. If for @inaun that is not doable i'm just providing other ideas / options. As I stated early on in this thread the OP's original idea may have issues as far as comfort control.

    Messing around with louvers throughout the heating season sounds very irritating to me, I'd rather automate the process.

    I also kind of like @mattmia2 heat exchanger isolation idea. However that requires more plumbing hardware than just a heat exchanger. So the cost may be higher, but the OP would not have to buy and install new baseboards.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,129

    @109A_5 said: "I also kind of like @mattmia2 heat exchanger isolation idea. However that requires more plumbing hardware than just a heat exchanger. So the cost may be higher, but the OP would not have to buy and install new baseboards."

    Why would a heat exchanger be needed. If the non barrier tubing worked on the existing system I would bet that there are more than just the one 4 loop zone has non barrier poly tubing in the other zones. The system is already operating without a HX. Perhaps I'm reading the issue incorrectly. but I understand that this is one of several secondary zones piped as a secondary loop. @inaun has indicated that the system is older, before oxy barrier tubing became popular. This is very much like the huge mistake (learning experience) i made when one of these non barrier systems needed th have the boiler replaced. That polybutylene tubing in a thin pour concrete slab over a crawlspace worked for over 20 years with all that oxygen because the original boiler was stainless steel.

    So adding a HX to @inaun system seems like @mattmia2 has assumed that the existing poly tubing is the problem and not the fact that it needs to be replaced for reasons not exactly articulated in the original comment, ( I think it has a unrepairable blockage or too many pinhole leaks to easily resolve) but is not easily accessed. The balance of the non barrier poly tubing in all the other zones are not a problem that require a HX so why would a HX help here?

    I certainly wish that @inaun might come back and better explain the rest of the system and perhaps offer the type of heating source there is for that particular secondary loop. The fact the they said "However, there does not seem to be a "textbook" way of providing separate temperatures without two pumps" indicates that they have done some research and understand that no one has successfully done what they want to do and published the results. I think that's because it won't work.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?