borecrazy
borecrazy Member Posts: 3

Hello-I have an older gas floor heater that quit, I believe it must be faulty control box-only because it is the only working part other than the thermostat. Everything else is sheet metal and cast iron! The control box seems to be made up of several parts put together-each has a letter and number stencil on it. Is there anywhere on your sight I could look those up?

Thank you,

Dave Pedreira (borecrazy@yahoo.com)

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,403

    Just post as much information on the thing as you can find — make, model, year. Photos… no need for you to look it up, but odds are pretty good that someone will know just what it is.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Member Posts: 14,242

    cast iron? is this an old coal floor furnace with a conversion burner? modern floor furnaces usually have steel heat exchangers. pictures will tell us. one down through the grate might help as well as of the outside.

  • borecrazy
    borecrazy Member Posts: 3

    Maybe it is steel, been a long time since I went under the house and dropped the actual burner out of the box! What I was getting at is it is just a large metal oval with holes, not an active part of the heater that could stop working! Unless it cracked or broke, it's just there to channel the gas into flame-

  • HVACNUT
    HVACNUT Member Posts: 7,016

    What control box are you talking about? Is there a spark Igniter to light the pilot?

  • 109A_5
    109A_5 Member Posts: 2,820

    Would not surprise me if the 'control box' was nothing more than a 120 VAC to 24 VAC transformer, and then there is the gas valve and a thermocouple.

    Someone probably needs to crawl under there with a meter and see what is going on. Probably not much there.

    Has the thermostat has been bypassed to eliminate that as the cause ? Probably the easiest thing to check first.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 14,242

    a lot are millivolt and just run off a thermopile. thermopiles wear out after a couple decades and don't produce enough current to open the valve and need to be replaced every once in a while.

    109A_5
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,122

    Chances are that your gas valve is powered by 750 millivolts. That power is generated by the pilot flame burning on the pilot power generator. There are several items that connect the electrical parts to make the millivolts open the gas valve.

    • First there is the power generator sometimes called a power pile.
    • Next there is a Gas Valve that uses that power
    • Then there is the thermostat that opens and closes the electric current based on the room temperature
    • Then there may be a Limit switch or even more limit switches placed in different locations around the furnace in order to keep the furnace from overheating.

    Some of these limit switches may have a manual reset. If you have a manual reset limit, that may be the reason you have no heat. Follow the wires to see if there are any limit switches. See if those switches have a tiny button between the wire connectors and press it. If you feel a slight click when you push it then it was tripped. If you do not feel a slight click then it was not tripped.

    Another reason for no heat is the power generator thermopile may be defective.

    Here is a wiring diagram that might be close to what you have in your floor furnace.

    Screenshot 2025-09-15 at 11.25.44 AM.png

    If you are not comfrotable playing with the safety controls on a gas appliance then i would suggest you call a professional for service. but pushing a reset button on a limit control is usually a DIY first step. If the limit trips again, then you need to find the cause. The safety switches are there to let you know something is wrong and needs further attention. Don't bypass them.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) ForbesPC7060
  • borecrazy
    borecrazy Member Posts: 3

    Thanks to all for the tips & ideas. My problem is "professionals" I have spoken with want answers to questions I can't answer before they will come out to look at it! This site has a Locator to find someone in my area to call-but in the whole state of California they only list one-and it is not close!

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,122
    edited September 17

    What kind of questions do the professionals ask?

    You should say "I have Gas Heat and the heater is not working". When I quote you the amount of $$$ I charge for a service call visit, and you reply " Sounds good, when can you get here?" That is all the information I need to send a technician.

    There has to be more than one professional HVAC or Plumbing/Heating company in your area. Just call another one that has less questions.

    EDIT: Who sells you the fuel you use? the gas company may have someone that knows how to fix your heater. Remember, As long as the furnace is not working, the gas company is not selling any gas. It is in their best interest to get your furnace working again.

    As far as the "Find A Contractor" link, A contractor needs to sign up to be listed. in the great state of California, I guess there are not too many contractors that look for help here at HeatingHelp.com. I know here in South Carolina, where I moved to retire, there are none.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,959

    Hi @borecrazy , What region or city in CA are you in? I keep trying to be retired, so am not looking for work, but am near Monterey and have experience with floor furnaces.

    Yours, Larry

    mattmia2Alan (California Radiant) ForbesPC7060
  • mattmia2
    mattmia2 Member Posts: 14,242

    you need to make some friends you can refer people to. a floor furnace that won't fire is in the realm of something anyone that is basically competent can figure out although they may hate you for sending them in a crawlspace.

  • HVAC contractors in my area won’t touch them. They are usually jury rigged and a liability.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,959

    Hi @mattmia2 , I'm very careful with referrals. I'm of the "go slowly and do it well, and just once" bent. Too many are of the "go fast and mess up" approach. I don't want my name attached to that. And, although I don't mind crawlspaces, just guessing I'm in the minority. 🤠

    Yours, Larry