Cutler-Hammer 9201 .80amp What to replace it with.....

I believe this is a thermal overload relay… When i Jump out the two terminals that have wires going to them the pump and blower for the modine come on. I do know that the coil that used to be there has completely disintegrated ( i have a picture of a new one here with
different ratings but what should be there).. If i just eliminate this control and wire nut the wires together will that be fine?? or what would work as a replacement. Thank you in advance
Comments
-
-
mattmia2 Like ratings ? (the pump they had in the past 10+years was a 1/6p which pulls up to 1.8 amps on high speed) I have the cover plate ratings which are
0 -
in the first picture the rating for the coil was stamped .80 which you can see the coil is no longer "whole"
0 -
Sorry the first picture didn't load here it is
0 -
the picture of the burned coil is not in this post, just a whole one that says 2.1 a.
do the motors say something like "thermally protected" or "impedance protected"? What voltage are they running off of? If the motors don't have built in protection then you need external protection in the motor starter.
0 -
The motors are running off of 120v.
The pump has impedance protection I just looked that up, as for the fan motor. I cant really get to it in any easy fashion.. not as in high in the air as in practically sealed off with ducts coming off of it to diffusers…
Thank you for your time bud, I appreciate the insight
0 -
-
How would go about getting a new heater? Also, So jump out the fan then check for amperage and then… how to size the new heater?
0 -
The heater that was there is discontinued
0 -
-
how can u tell if it has a thermal overload built in? im going to attempt to get to the unit, and get the nameplate off of the unit and the blower and see if i can look up the motor.
0 -
-
Look up a Square D 2510FG1 manual motor starting switch. They have overload protection but you have to buy the correct size overload heater separately.
Other brands make these as well like Siemens and Eaton.
If you can run the motor underload and amp it out multiply the amps you get x 1.15 to select the overload heater. But be careful with some brands heaters you select by motor amps and the 15% is already added in
2 -
-
EBEBRATT-Ed
Got to say i love this group of gentleman. Thank you for the advice, that is exactly what I'll do.
I couldnt agree with you more. Everything is rusted to oblivion. He's going to have to go with the new set up, I just didn't know how to go about it. Thank you
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 45 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements