I have a PTAC unit in a rental unit I need to replace. There's a loud sound coming when the A/C is running. I grabbed the fans motor shaft and I could feel up/down side to side play. The fan's blades are hitting the motor housing. I tried pulling the sheet metal housing away from the motor using a screw and a locking pliers, but that fix was temporary and the noise returned shortly thereafter.
Based on a Prior thread I started, I know the fan's motor could potentially be replaced. It could also be worn motor mounts. B/c it's in a rental unit and in the tenant's master bedroom, I cannot setup shop and learn how to replace the motor.
There are a total of 4 of these PTAC units in the rental unit. I'm pretty sure they are all identical. My thinking is to replace this noisy unit with a new one, and fix the noisy unit offsite. This will leave me with a good working unit in case another one breaks. And also all the spare parts I need to repair one of the other 3 units. These units are 40 years old.
Based on one sticker I found on the old unit, I think it's a Singer. This seems to be a wiring diagram.
Islandaire makes a slide in replacement units. Can I just measure the existing unit (45 x 16 1/4 x 9 1/2) and order a replacement? Or are there other things I need to take into account. My unit is front return, top discharge.
Here's the link to IslandAire's replacement guide.
This seems to be the model I'd need to replace it with:
Singer® Type EA,ES and RS | 16 3/8 | 44 7/8 | EZ Series ED |
---|
Picture of the non-functioning unit, wiring diagram sticker and the dimension diagram of the replacement attached:
Comments
-
-
I've looked all over the unit. No model or serial#.
0 -
that 28000204 looks like a model number. i'm sure they can tell you how to get the information they need to match it up.
0 -
-
look into inverter PTAC’s
https://www.totalhomesupply.com/p/friedrich-pvh09k3fc-9000-btu-class-freshaire-series-with-inverter-technology-12-1-eer-ptac-air-conditioner-with-heat-pump-20-amp-230-volt-r32-refrigerant?gad_source=1&gad_campaignid=21772542403&gbraid=0AAAAAD1XDHyefuqVVLU_CP1vIRyj8dF1d&gclid=EAIaIQobChMIxaeTzZe4jwMVPTcIBR2GmjiBEAAYAyAAEgI5ffD_BwE
1 -
-
This ended up being the solution. I was talking to the Islandaire rep and gave him all the numbers on the wiring diagram. He said no dice. He asked me for my address and right away he knew which unit I needed. He's done work in my building before. I just needed to give him the room size to determine how many BTU were required.
I thought about inverters but the building provides heat with hydronic pipes that run just above the ptac unit. The PTAC's blows air onto the copper pipes and circulates heat throughout the room. I'm already paying for that heat via common charges.
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.6K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 47 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements