Water to Water Geothermal heat pump replacement with lp boiler
Comments
-
a clamp on probe will get you the temps. the pressure is less important, the temps in different places will tell you a lot about the flow. I'd pull one of the circulators with the isolation valves and see if there is a flow check in the circulator. If there is and it is undamaged and you are getting ghost flow you have problems with the way the circulator for the zones and the circulator for the heat pump are connected together.
0 -
It’s hard to beat eyes on the ground. Hopefully you have a knowledgable hp expert on the way.
You have a good list of questions here to get answers for.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Please report back if he figures it out. Inquiring minds want to know!
0 -
That is outside my wheelhouse but I will look around and see if I could find someone I would contact Water Furnace and ask their input and suggestions for a technician. Here is a link to their dealers close by. Water Furnace
Ray Wohlfarth
Boiler Lessons0 -
-
Hopefully he recommended someone good. I think WF is pretty good stuff.
Let us know how you make out.
0 -
Were you able to calculate gallons per minute at 8 dt? you can see how much heat you were extracting.
0 -
Supposed to be meeting next week. Will update once they assess the current system.
0 -
How close are the drilled grouted wells to each other?????????????????????????????????????????????????????
When you said three 180 foot deep wells piped in series that struck me as very odd. These drilled wells were apparently drilled and had a looped drop pipe system installed with the "so called "geothermally enhanced" clay grout that acts as an insulator rather than an open loop system.
You may have one problem which could simply be the 3 wells are too close together and cannot shed the heat or reclaim enough cold from the surrounding ground-go figure-due too shallow a depth.
The driller that did this did you no favors as a 600 foot deep open loop cased well with a six inch pipe cap on the first pipe joint with a marine concrete plug in the last 10 feet of the casing would have given you almost 590 feet of water column for heat exchange with a single drop pipe set in 200 feet of water column.
0 -
I just looked at the drilling information from the driller. Cores were 180' deep all shale and limestone and a little coal. He sealed with benseal. 3/4" pipe. All wells are 17' apart. He laid them out in a triangle.
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 45 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements