Mitsubishi MUZ-FH12NAH evaporator doesn't get cold
sixplex
sixplex Posts: 159
edited August 2025 in THE MAIN WALL
So installed a MUZ-FH12NAH mini split.
It cools/heats slightly above ambient (ambient 25C, AC produces 20C in cooling, 30C in heating).
No leak or contamination 100%. Pressure tested to 250psi vacuumed down to 30 microns, holds the pressure and under 500 microns overnight.
The liquid line gets frosty (charge is 100% correct, 2.5lbs) , the evaporator doesn't get cold.
What can I do to diagnose this?
  • GGross
    GGross Posts: 2,062
    how long is your lineset and have you triple checked your wiring is accurate?
  • ratio
    ratio Posts: 4,316
    Check the valve on the mixed-phase ("liquid") line. It shouldn't be frosty, just wet with condensation when it's working. Something's restricted, the valve is the simplest answer.
    After that, check the EEV. Make sure the coil is snapped down tight & plugged in. Maybe check the coil windings for continuity. Mitsubishi makes a magnet that'll drop over the EEV & allow you to manually stroke it. Once I found one that was sticking, I managed to free it up with the magnet.
    GGross
  • sixplex
    sixplex Posts: 159
    The liquid (thinner) valve is definitely fully open, counterclockwise to the left until it stopped. That line is frosty all the way to the evaporator.
    Is the EEV inside the condenser? Is that the same thing as LEV?
    Apparently there is one inside the evaporator too.
    One thing i did wrong was breaking the vacuum with 100psi, that could have damaged something, you're supposed to use ~2-5psi to break vacuum.
  • sixplex
    sixplex Posts: 159
    edited August 2025
  • sixplex
    sixplex Posts: 159
    pecmsg Posts: 7,551
    Ice like that is charge or EEV issue.
    is this a new install?
    Contact tech support and get it filed.
  • sixplex
    sixplex Posts: 159
    New install, condenser (open box), evaporator (brand new).
    Original r410a recovered, well vacuumed, new charge added by weight.
    pecmsg Posts: 7,551
    you still need to recover and weigh the charge.
  • sixplex
    sixplex Posts: 159
    not sure what you mean, as i said that was done already, exact charge is inside, no leaks to contaminants in the system.
    pecmsg Posts: 7,551
    tech support will want to know how much charge is in there.
  • sixplex
    sixplex Posts: 159
    2lbs 9oz as per the label, line set is short, no need for more.
    pecmsg Posts: 7,551
    when you contact Tech Support they’re gonna ask you did you pull and weigh the charge.
    pecmsg Posts: 7,551
    where did you purchase this?
    Who installed it?
  • sixplex
    sixplex Posts: 159
    It did but it was low. All refrigerant was removed, exact amount was added, since there is no way to just top up and be 100% sure the correct amount is in there and to also rule out contamination.
    pecmsg Posts: 7,551
    you weren’t concerned when the indoor unit was low from the factory?
  • sixplex
    sixplex Posts: 159
    sure, i couldn't return in.
  • ratio
    ratio Posts: 4,316
    Yeah sorry, LEV == EEV, I misremembered the nomenclature.
    Open box, were there signs that it had been installed once? Could be a return because it didn't work. IDK where you got it from, but the (please don't be offended) big box stores around here are well know to reshelve returns until the returnee marks all over the box with a sharpie "BAD DON'T BUY".
    That mixed phase line is definitely waaaay too cold. The LEV stuck closed is the next simplest answer along with the LEV not opening due to mechanical or electrical issues.
  • sixplex
    sixplex Posts: 159
    Could be anything, you're right, but it looked new, and the matching evaporator was completely new/sealed.
    I'm reading the actual magnetic coil on the LEV sometimes gets unsnapped, i drove this this for 2 hours without the original box. A long shot but worth checking.
  • sixplex
    sixplex Posts: 159
    Nothing wrong with the AC, EEV coil popped off during transport. They should zip tie them or something. Ice cold now. Thanks for the help guys!
    GGross
  • ratio
    ratio Posts: 4,316
    The coil on the LEV might not be seated correctly, the coil might be bad (winding shorted or open), the harness might not be seated correctly, the outputs on the board might be blown (there's a thread here somewhere where that happened, but it was due to a failed coil IIRC), the computer might have lost its mind & is not energizing the windings in the right sequence (exceedingly remote possibility).
    Could be something else entirely, too. You said this is a heat pump, perhaps the reversing valve is sticking, but IIRC you said it does heat and cool, so it must be mostly shifting.
    Take the side off & look at the frost. You should be able to follow that all the way back to the restriction. If it just stops in the middle of a pipe, or at a joint between two pipes, there's something stuck there. If it leads to a valve, whap it gently to see if it'll free it up.
  • sixplex
    sixplex Posts: 159
    edited August 2025
    The AC works now!
    The black part hanging is the coil, it's supposed to sit on the shiny cylinder with the metal clip snapped into the copper pipe. It got bumped off during transport i imagine. As soon as i snapped it back in place the AC began working as it should.
  • ratio
    ratio Posts: 4,316
    Awesome, glad you got it working!
    pecmsg Posts: 7,551
    sorry but the start up sequence is
    EEV Command closed. Feed back is sent to the computer verifying this has happened.
  • sixplex
    sixplex Posts: 159
    edited August 2025
    For anyone who might be having a similar issue here is an excerpt from the service manual, indicating they know the EEV can come off. It happened to me because I transported the condenser without the original box which i guess dampens vibrations when you're going over bumpy roads with the condenser in the back of the vehicle.
    Symptoms are very similar to low refrigerant. Inexperienced techs might add refrigerant overcharging the system which isn't cheap to fix if you're going to do it properly by recovering the entire charge and weighing in the right amount.
    GGross