Can someone explain this hydronic loop heating.

Lid431
Lid431 Member Posts: 13

Moved into a new house in NY. The heat is hydronic gas boiler. The bottom piece im assuming comes in on one side and out on the other. Why does the top do?? Doesn't seem to have a flow path.

1000009497.jpg

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,808

    I can see no purpose to that extension from the location where there should be a vent of some kind of vent to expel air from the convector. You may find it in a circa 1950s popular mechanics magazine, when there were many innovative ideas. But I can see no benefit.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Mad Dog_2
  • 109A_5
    109A_5 Member Posts: 2,548

    Is it known where the third pipe goes to ? Could the slight internal pressure change of heating the upper part modulate the water flow through the lower part ?

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,647

    I would say it was someone’s useless attempt to get more heat out of that unit.

    Retired and loving it.
    Mad Dog_2mattmia2SuperTechAlan (California Radiant) Forbes
  • Lid431
    Lid431 Member Posts: 13

    Thanks all!

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,286

    Don't even see a bleeder vent. Mad Dog

  • HVACNUT
    HVACNUT Member Posts: 6,921

    It looks like the air eliminator was eliminated.

    mattmia2Mad Dog_2EdTheHeaterMan
  • hot_rod
    hot_rod Member Posts: 25,437

    That added loop probably emits a small amount just from convection.

    Unless we don't see another piping connection, I don't see it actually circulating through?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,319

    Weird. The 3 pipes were originally put there for some reason. Is there another tapping on the right-hand side of the original convector?

  • mattmia2
    mattmia2 Member Posts: 13,742

    I don't even see where much of any water is going to get in that contraption

  • Lid431
    Lid431 Member Posts: 13
    1000009497.jpg

    Will this be the correct fix? Remove the top baseboard and add an 1/8" bleeder.

    Is the automatic bleeder reliable ? Or stick with the manual one ?

    Thanks again for all the responses.

    Mad Dog_2EdTheHeaterMan
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,319

    I would use a manual bleeder. Less likely to leak in an area where they are not visible

    mattmia2HVACNUT
  • 109A_5
    109A_5 Member Posts: 2,548

    Does this unit not heat ?

    Maybe when the tapped air in the upper part expands it adds air to the convector coil, so the heat output is self limited. I'd leave it alone if it is not leaking.

    If you need more heat from that unit you could remove upper part and and add a manual air bleeder. You may get more heat from it since you can get more air out.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Lid431
    Lid431 Member Posts: 13

    It does heat when I tested it, not sure how well. I checked out rest of the house and found all upstairs to have the same set up except that some have manual bleeders in addition to the non circulating loop, and some dont. Some have manual bleeders, some have saddle valves installed for bleeding , and some have none. Im going to remove them all and just stall manual bleeders.

    EdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 13,742

    If they have a way to bleed them, they will heat some through convection of the water but they will do little to add to the output of the convector.

  • HVACNUT
    HVACNUT Member Posts: 6,921

    There's enough room to pipe in a 3/4 ball valve, then a 3/4 x 1/8 coupling, and an 1/8" Hy-vent.

  • JUGHNE
    JUGHNE Member Posts: 11,479

    Can you see in the basement where that 3rd pipe is connected?

    What do you have for expansion tank at the boiler?

    Pictures of both would be interesting.

    EBEBRATT-Ed
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,319

    Agree with @JUGHNE

    I wouldn't do anything until you find out what the third pipe does. It seems to me there could be more to the story

  • mattmia2
    mattmia2 Member Posts: 13,742

    what 3rd pipe? i think that contraption is screwed in to the manifold of the convector.

    HVACNUT
  • hot_rod
    hot_rod Member Posts: 25,437

    For a finned tube or coil like that you need an enclosure to enable some convection currents. Colder air enters the bottom, warmed air exits the top

    What type of cover goes over that opening?

    It needs a slot along the bottom and top to enable convection currents

    A blank cover or grill or some sort will not allow good output.

    Another option to increase output is a small fan to force some convection.

    Vacuum and brush the fins to increase output also

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Lid431
    Lid431 Member Posts: 13
    edited August 12

    The third pipe is connectconnected to the convector, meant for bleeding im sure. The boiler is about 10 years old, Williamson 105k. Its a typical setup , expansion tank , hy vent , coming off the boiler. Pretty sure someone, definitely not an expert, at one point attempted to get more heat out of convectors. Out of the 10 units , 2 have saddle valves piecered in the pipe for venting , 3 have coin bleeders , and the rewt dont have a way to bleed at all.

    The the cover is slotted at the bottom and the top to allow for air movement.

    I Ordered the fittings and manual bleeders , so arrive tomorrow.

    HVACNUT
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,319

    @mattmia2

    The OP confirmed the 3rd pipe is the vent. How many times do you see a vent that big? All it needs is an 1/8" coin vent.

  • mattmia2
    mattmia2 Member Posts: 13,742

    I think that convector element has tapings to feed it from the top or bottom or connect in a loop or feed as 1 or 2 pipe steam so it has several taping that can be used different ways for feed or reduced for a bleeder or steam vent.

  • 109A_5
    109A_5 Member Posts: 2,548

    Since the unique tapping is only at one end and on top and the supply and return is from underneath I still think it is a self metering method. It seems deliberately made that way.

    It's not like trapped air that needs bleeding like with a typical vertical CI radiator.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HVACNUT
    HVACNUT Member Posts: 6,921

    There are thousands of homes on Long Island with that type of convector on mono flo systems that have a 3/4 tap for bleeding. I don't remember who made the original bleeders, but they looked like brass rockets. About 4 or 5 inches tall.

    I have to admit, I never saw one where the tap was on a vertical, so it is deceiving. A pic from another angle would show it better.

    mattmia2
  • HVACNUT
    HVACNUT Member Posts: 6,921

    @Lid431, saddle valves? For real? Complete with 1/4" tubing for easy bleeding? 🤪

    EBEBRATT-Ed
  • Lid431
    Lid431 Member Posts: 13
    1000009531.jpg

    Yes, saddle valve located at that exact location for air bleeding.

  • 109A_5
    109A_5 Member Posts: 2,548

    Ummm " Yes, saddle valve located at that exact location for air bleeding. "

    A bleed valve here seems like knucklehead maneuver.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 13,742

    maybe it was to drain it

  • 109A_5
    109A_5 Member Posts: 2,548

    Yes, that would make more sense to drain water out of an assembly that should be air bound, not for bleeding air out.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 13,742

    water will get in to that bottom part over time and it will freeze if you have the house shut down for some reason.

  • 109A_5
    109A_5 Member Posts: 2,548

    As I alluded to before, I believe it was an attempt to reduce or limit the heat output, not enhance the heat output. Did the home have gravity or coal fired heat at one time ?

    As illustrated below when the upper air chamber is cold the convector has full flow, when heated up the air expands entering the convector coil, thus reducing the volume of water that could pass through the convector coil, limiting the heat. Whether this worked well or not, I have no idea, apparently the concept never gained any traction.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    mattmia2
  • 109A_5
    109A_5 Member Posts: 2,548

    If it actually works as I illustrated I would have built it so it could not trap water like it would now. The Copper pipe over the aluminum finned air bound section.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 13,742

    the water will absorb some air when it cools and some of that water with more dissolved air will find its way back to the boiler where it will be heated and the air will come out of solution then that water will circulate as hot water to the convector and cool and absorb more air. over time at least some of that loop will fill with water.

  • Lid431
    Lid431 Member Posts: 13
    1000009577.jpg 1000009576.jpg 1000009575.jpg

    All 11 convector heaters had their top section removed and replaced with just an 1/8 coin bleeder. I was able to bleed air from all of them and they all heated up nicely.

    Again , out of the 11 of them. Some had coin bleeders on the top loop, some had saddle valves installed, and some had neither. Very very strange.

    mattmia2HVACNUT
  • mattmia2
    mattmia2 Member Posts: 13,742

    Might want to seal up those holes in the floor so it pulls air from the room instead of from under the floor. Use foam or something around the pipes so they can move.