Unrecognized return vent
2»
    mattmia2 Member Posts: 13,734
    just arrange them so any condensate flows back out the inlet.
    109A_5 Member Posts: 2,538
    If you get the system air tight you probably won't need a vacuum pump. Just a means to let the air out of the system and not back in.
    I was curious about the airflow through some of my one pipe vents so I built this interface. Sorry not Hoffmans but you get the idea.
  • pacoit
    pacoit Member Posts: 94
    @Steamhead, @mattmia2 , Nice idea! However, my system doesn't have any steam traps to repurpose. Also, for the vacuum system, I envision a dry air-line return to a discharge pipe (with or without a pump); whatever I use as a valve to hold the vacuum, I don't expect it to see steam, or even more than warm air. So, I expect to use a check-valve or possibly a solenoid valve (depending on the ultimate design).
    @109A_5, Excellent! That's a good way for me to quickly setup a vacuum system for testing.
    By the way, I am in contact with @PMJ, who very kindly has offered to share his experiences.
    Steamhead Member Posts: 17,920
    @pacoit , they still make traps. For the long main you'd get a Barnes & Jones "Big Mouth".
    Consulting
  • pacoit
    edited August 10
    Thanks, @Steamhead .
    FYI, the threads on the "L" of the Breck are 1/8" NPT.
    EDIT: Also, it turns out the first Breck did not have a rusted out adjustment screw hole; it's just that the adjustment screw wasn't screwed in; once I obtained the key, I was able to screw it in without issue.—-Don't want people to think a Breck couldn't last 100+ years!
  • jumper
    jumper Member Posts: 2,468
    This thread is very interesting. Any steam heating system needs to expel air and return condensate to boiler. This system seemed to operate without radiator vents or steam traps which require maintenance.
  • pacoit
    @jumper, Actually, it had (has) a thermostatic vent at each radiator return.
    @jumper Systems expel the air via the vent(s) (one pipe or two pipe), as you probably already know.
    The boiler heats the water, the water expands into steam the air gets pushed out. When the thermostat is satisfied and the steam collapses back to water and a vacuum is formed. The trick is having the system tight enough so the air can't get back into the system (once expelled), to maintain the vacuum from cycle to cycle.
    I believe if the system integrity is maintained the benefits are faster steam propagation (less air to push), less air (oxygen) minimizing corrosion and @PMJ's observation of more even, uniform heating.
    I also believe with the faster steam propagation you may save some fuel too, since little gains add up over time. You are not burning fuel to push air (as much air) out of the system.
    The breck is a bimetal element air vent. See Dan's article that he linked.
  • pacoit
    Update: I put the Breck in 5% acetic acid (vinegar) for 3 days. It de-rusted very nicely. Lots of debris "boiled" out. I re-attempted heating it to see if it would close, but it did not. I also was unable do any further disassembly, nor see how it could be done. (I wonder if the insides were slipped in while the tube was still hot? Heat fit.)
    when iron rusts the scale is bigger than the original metal, even if you get rid of the rust it likely will be bigger than it started out. it also may have additional parts that screw in through the side ports, possibly with some sort of spanner that are holding the internal parts in. they may not have known enough about what would happen after a few years of use or they did know but didn't know how to fix it. This was one of the first steam air vents.
    If you ever want to part with one I bet the
    would accept a donation.
    Consulting
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,647
    it would live forever there.
    Retired and loving it.
    edited 1:17AM
    When ever I completely remove rust there was less of the original metal left, since it went away with the rust.
    Was the screw removed (Red arrow) ? It would not surprise me if the screw pushed the "D" shaped inner assembly (Yellow arrow) against the other side of the housing.
    is there a patent number on it?
  • pacoit
    @109A_5, I removed the screw before de-rusting. I imagined, as you, that the screw held the guts in place. However, de-rusting hasn't loosened things up… yet. Haven't knocked it around much, yet. Also, should check it is fully de-rusted—-another vinegar bath.
    I have not found patent numbers or markings of any kind…. Maybe I need to get my eyes checked…
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,911
    Hi, Might be good to use some Kroil on it https://www.kroil.com/product/kroil-original-penetrant/ I've had it work on really stubborn stuff. 🤠
    Yours, Larry
    This book mentions the ''Automatic Air Vent" and a 1868 patent which I could not find. See pages 71, 111.
    http://waterworkshistory.us/DH/1960HBSmith.pdf
