York furnace slow fan speed
Hello group. New to using fourm. Have a york 95% furnace that runs 600 cfm when in cooling mode. Heat mode ramps up normal. 2 units in house doing same thing. I thought control board at first but what are the chances of both going. Any thoughts would be greatly appreciated.
  • ratio
    ratio Member Posts: 4,234
    What's the cooling speed set to?
    It usually takes me a half-hour to figure out the DIP switch settings each time, I don't play with them often enough.
  • emerald
    emerald Member Posts: 9
    No Dip switch on this board. I am unfamiliar with york equipment and this board.
    mattmia2 Member Posts: 16,746
    did it ever work?
  • emerald
    Good question. Last year it froze up and flooded the bedroom below. I was called in the fall for no heat. After checking the motor I Determined the board was bad. Replaced board and heat was operating. This was in November so I didn't run the ac. This call I don't believe the ac worked at before I arrived. I never worked on 2nd unit in basement. While there today I went to basement and found the unit operating same manner. Cfm light is blinking 6 times calling for 600 cfm. Units are both 12 yo and in good condition otherwise.
    is y from the t-stat connected to the control board(or is it a communicating t-stat)? is it an ecm motor or is the speed set with tap connections on the control board?
    essentially rtfm
    HVACNUT
  • emerald
    Yes the condenser comes on with call. Ecm tested and runs. Fan runs properly in heat mode.
    EdTheHeaterMan Member Posts: 12,154
    edited June 2025
    Need the model number of the 95% York furnace so I can look up the necessary settings to make the fan operate at the proper speed needed for the matching condensing unit.  If you have a 1.5 ton condenser, then 600 is the correct fan speed. if you have a 3 ton condenser then you want to use 1200 cfm. or thereabouts.
    If the fan operates at a higher speed for heat, then there has to be a way to adjust the cooling fan speed based on the size of the outdoor unit.
    The York 95% furnace can be a single stage gas valve or a two stage gas valve or a variable input gas valve. Each of those furnaces has a different model number and therefore a different instruction manual and perhaps a different fan speed controller. There are also PSC motors and ECM motors that will be adjusted differently. I assume that you have the variable speed ECM fan motor by the previous statements you made, but the model number will tell all that is needed.
    that isn't what i asked. i asked if y from the t-stat was connected to the control board(or is otherwise made to do a high fan call on y or g, newer air handlers will just do low fan with g)
  • emerald
    edited June 2025
    Mdl Tm9v100c16 yes ecm motor. 4 ton unit. So I know I should be getting 1600 cfm .
  • emerald
    Yes y is connected to the control board on from thermostat.
    edited June 2025
    So you are not using the communicating thermostat ABCD. but you are using the Legacy thermostat with R W1 W2 G Y1 Y2 C terminals
    Are you using a 2 stage thermostat?
    Are you using a 2 stage condensing unit?
    You might want to set the fan based on these instructions: From page 33 of the manual.
    There are more details in this manual: TM9V C Series I believe the York and the Johnson are identical units
  • emerald
    Thank you for the information ed. No booklet left from the installer. This is very helpful and I am going back tomorrow. I will let you know how I make out. Thanks again
  • emerald
    Finally fixed. Upon arrival this morning unit was running correctly. I watched for a couple cycles and then slow fan again and no condenser. I checked voltage and only had 19 on y. Ran new thermostat wire and and problem solved. Thank you for all the information provided. Enjoy your summer
    EdTheHeaterManmattmia2
    Another happy customer!
  • ratio
    Two units, both with defective stat wires? That both failed in the same manner?
    I don't doubt you, but that's really strange. The failure mode is really strange, too. Doubly strange. Quadruply strange??
    Defective stat wire? Overly excited helper stapling up the wire?
  • emerald
    Homeowner tells me the units have never worked correctly or consistently since installed. Several freeze ups over the years.
