Remodeled House. Now Radiators Are Way Too Large

We installed this boiler and radiator system in 2017 when the owners purchased this house. Nothing had been done to the building since it was built; single glazed windows, no insulation.
I sized the radiators for 130F water temperature as I wanted the boiler to condense and they turned out very large. My supplier says I order larger radiators than anyone else. I suppose that’s a compliment.
Recently remodeled, the radiators are now way oversized and I can drop the heating curve even lower. It’s now set to 1.1 with zero offset and the radiators will only get warm, not hot. Safe for their new children and more savings on their utility bills.

IMG_3401.jpeg IMG_3399.jpeg IMG_3397.jpeg
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
GGrossmattmia2delcrossvPC7060KaosIronman

Comments

  • bjohnhy
    bjohnhy Member Posts: 110

    Nice. Is the reason for the reduced heat lost because of their new insulation, windows, and air tightening? I suppose you do not have a new design water temp yet? But now much lower than 130F?

  • Big Ed_4
    Big Ed_4 Member Posts: 3,223

    Flat curve comfort too..

    There was an error rendering this rich post.

    bjohnhy
  • GGross
    GGross Member Posts: 1,518

    and a sweet little Mesa combo amp in there too, you didn't use that as your table during the project did you?😁

    Alan (California Radiant) Forbes
  • hot_rod
    hot_rod Member Posts: 25,153

    what sort if delta do you design for? With a 30 delta you have some cool return temperature

    You were “future-proofing “ before it was in the news!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream