Draft
captainco
captainco Member Posts: 853
What does a draft test tell us?
  1. The flue is sized properly or
  2. The flue s undersized or restricted
  3. There is adequate combustion air in the room
  4. If there is combustion air interference
However. draft does not tell us if the equipment is venting properly or if there is adequate combustion air at the burner
GGrossMad Dog_2
    EdTheHeaterMan Member Posts: 12,155
    That is what the analyzer is for
  • HydronicMike
    HydronicMike Member Posts: 343
    Knowing Jim, it’s either 'All of the above', or more likely' None of the above'.
    Mad Dog_2
    EBEBRATT-Ed Member Posts: 20,165
    I don't think it tells you anything by itself. It's how your interpret the readings and what other tests youdo and what you observe
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,546
    Jim Davis....My Man!!! Mad Dog
  • retiredguy
    retiredguy Member Posts: 1,090
    edited May 2025
    This may not be what you are discussing about draft but a lot of the very old gas burners relied strictly on a good draft to provide the needed air for proper combustion. There were no fans or blowers to provide the correct amount of combustion air, just a good draft.
    Mad Dog_2
  • Mad Dog_2
    Yes, buildings were looser and equipment more forgiving. Mad Dog
  • captainco
    Why do instructions state to use a match or smoke at the draft hood
    to verify venting?
    Draft hoods disconnect equipment from flues and minimizes draft through equipment not increase it.
    Mad Dog_2
    I use a Marlboro at the draft hood. All that proves is the chimney is taking what the boiler puts out….or not.
    PC7060
    Chesterfield is a much better smoke. @EBEBRATT-Ed
    A friend said so.
    PC7060Mad Dog_2
  • GW
    GW Member Posts: 5,184
    'sup Jim
    1. The flue is sized properly or »»»all is good, numbers are steady
    2. The flue s undersized or restricted »»» CO will climb
    3. There is adequate combustion air in the room»» all is good, numbers are steady
    4. If there is combustion air interference »»CO will climb
    How did i do?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    "Why do instructions state to use a match or smoke at the draft hood to verify venting?"
    »»verifies the chimney works, doesn't verify the appliance is venting
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    Mad Dog_2
  • captainco
    Excellent Gary!! You realize only 5 or 6 techs on here know that.
    Up until 1999 the National Fuel Gas Code recommended a cigarette for this test, but l believe it was Lucky Strikes.
    GWGGross
    Jamie Hall Member Posts: 27,359
    Phillip Morris Commanders… or Lucky Strike. Players when I could get them. Those were the days…
    My old man was Chesterfield non filters and my grandmother was Pall Malls, my uncle was Lucky's, Grandpa smoked a pipe.
    " Do you have Prince Albert in a can?"
    "Well let him out"
    When I was about 6 or 7 the old man would give me a quarter to go get a pack of butts. One day the guy at the store told me they are $.28 now. The old man had a fit.
    Mad Dog_2
    HVACNUT Member Posts: 7,436
    L.S./M.F.T.
  • Mad Dog_2
    Grandpa Norb was 3 packs of Chesterfields a Day...lit one match in the morning...typing his articles...didn't get The Cancer...go figure Mad Dog
  • GW
    I will never forget the “constipation” theory
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    Mad Dog_2
    @Mad Dog_2
    My mothers uncle "George" rolled his own lived into his 90s. And he didn't roll any funny stuff.
    Mad Dog_2
    edited May 2025
    Juvenile Delinquent and graffiti on the walls… what an awesome analogy   Spoken like a true teacher!
    That will draw a picture in your minds eye!
    Bob Harpermattmia2