heating oil tank manufacturer's warranty voided by transfer of oil from the old tank?
mrblint
mrblint Member Posts: 44
edited May 17 in THE MAIN WALL
I am getting quotes for a new indoor heating oil tank. All three quotes indicate that oil in our old tank will be moved to a temporary tank and the usable oil will be pumped back into the new tank.
I was reading the manufacturer's installation instructions to certified installers and they state that the installer or their delegate should be present during the first full filling of the tank. None of the quotes had mentioned that this step would occur, so I contacted the manufacturer and asked what the purpose of this instruction was. Was it that they needed documentation of some kind that the tank had been filled all the way and that everything was working properly? I thought it could be stress testing.
I got an email from the manufacturer's customer service saying that it was to prove that no oil had been transferred from another tank, because doing so would void the warranty.
Did the customer service agent not understand the company's requirement? Or are these tank companies not following the instructions "to the letter" and invalidating the warranty for the customer? Is it that the oil cannot be transferred directly from the old tank without being visually inspected so that only usable oil is pumped into the new tank, on the assumption that any sludge or water will have settled to the bottom of the (clear, see-through) temporary holding tank?
    HVACNUT Member Posts: 6,868
    Transfer the oil to the temporary tank and connect to the existing oil line to get the burner(s) running.
    Install new oil tank with new oil line, filter, OSV, etc. to the burner. Plug the end of the oil line at the burner, and close valves.
    Fill the new tank while someone is inside at the tank to observe there are no leaks during delivery.
    When the temporary tank runs dry, call the service provider and they'll come to connect to the new tank. Replace the nozzle and strainer. Prime and start. Combustion test. Done.
    SuperTechRobert_25EdTheHeaterManjringel
  • mrblint
    The temporary tank is not left with us as part of the install. The way the quotes are written, it's a one-day operation, and we never see the installers again.
    EBEBRATT-Ed Member Posts: 18,240
    edited May 17
    This is always an issue. Customers would prefer to not throw away oil they paid for.
    @HVACNUT has the correct answer.
    The other alternative is to burn the old tank down to just below 1/4 of a tank and then install the new tank.
    On the other hand, how will the tank MFG find out what went in the tank if no one tells them?
    The tank MFG are doing a CYA.
    kcoppIntplm.
    Are they filtering the transfer into the temporary tank? Are they filtering again pumping into the new tank? Even if the pickup tube is 5 inches from the bottom on the pump out (you DO NOT pump out the whole tank. There should be up to 50 gallons of waste oil.), so you think you're not picking up sludge and water. Has everything completely settled to the bottom? No.
  • mrblint
    We have only 1/4 tank (of 275) left now and this wouldn't take place until June. The various guys who came to scope out the basement said the old tank's contents would be emptied into a holding tank, and one of them did say something about the pump tube being placed a few inches from the bottom, I don't remember anyone saying 5 inches. One of them said the holding tank was clear so that they could see the oil, and that they would put only the "usable" oil into the new tank. Nobody said anything about filtering the oil. But the nuances of the process are beside the point if any transfer voids the manufacturer's warranty. Since two of the companies also sell oil, I don't see why they couldn't arrange to have a truck arrive to fill the tank, since we're paying a pretty penny for this and they'd also acquire us as a new oil customer.
  • mrblint
    edited May 17
    I'd rather have a 30-year warranty than 60 gallons of sludgy oil from the bottom of a tank that is probably around 60 years old. If the manufacturer is worried about transfer of water from the bottom of the old tank, that seems a reasonable concern to me. What worries me more than the manufacturer's CYA motivation is that none of the quotes even mentions that the manufacturer requires them to be present for the first full filling, and yet they're promising a 30-year manufacturer's warranty. Do they not know of the requirement? Do they not care about the requirement? They have plenty of language in their own sales agreements saying that in no way are they liable for any sort of remediation costs if there's a failure, even it is the result of improper installation.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,575
    mrblint
  • HydronicMike
    HydronicMike Member Posts: 81
    Don’t pump it over. Its waste oil now. It’s right in the instructions. If your contractor wants to ignore it, you need a new contractor.
    No amount of filtering will make that oil ok. Only a fuel polishing machine would work.
    It’s only about 60 gallons, let them take it to someone who has a waste oil heater. Or like the others said, use it in the existing tank until it gets down to about an 1/8.
    Robert O'BrienSuperTechmrblintEdTheHeaterMan
    pecmsg Member Posts: 6,291
    if the installers do this
    If the into that
    if My wife say yes
    There is no way of the manufacture know.
    run the tank down and sell the used oil
    Your tank is low now you might make it until June only using it for hot water the heating season is over. If the tank gets low before they change it you can dump some diesel fuel in form a gas station.
    Then start off with new oil in the tank.
    I seriously doubt any tank MFG ever checks the install or the oil fill process or quality.
    EdTheHeaterMan Member Posts: 10,777
    NEVER PUT OIL FROM AN OLD TANK INTO A NEW TANK
    yellowdoghot_rodjringel
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,897
    Hi @EdTheHeaterMan , Are you really sure? 🤣
    Yours, Larry
    That is as loud as I can type Larry.
    But I did type it as slow as I could because I know that you have trouble reading
    Larry WeingartenPC7060JoannieGGross
    This is one of those things like "you must always install a drop header" or "you must use all boiler supply tapings on a steam boiler" or "don't use Teflon tape on oil lines".
    All oil tanks collect water from condensation because basements are usually cooler that the outdoor temp in the summer.
    A lot of people transfer oil from old to new tanks. Is it a problem? Who knows.
    The MFGs stich their orr in the water to CTA. Just like they do with Teflon tape. We used Teflon for years before that rule changed with no issue.
    Something happens down the road with a tank and the MFg anit gonn pay no matter what they are long gone. We all know that. they don't pay when boilers crack either. They can always find an excuse.
    ethicalpaulLRCCBJ
  • mrblint
    Is it reasonable to ask the installer, if the company also sells oil, to not transfer any oil from the old tank but to coordinate an oil delivery the afternoon of the install, especially if the tank customer agrees to become an oil customer?
    edited May 20
    mrblint said:Is it reasonable to ask the installer, if the company also sells oil, to not transfer any oil from the old tank but to coordinate an oil delivery the afternoon of the install, especially if the tank customer agrees to become an oil customer?
    I believe that is the best way to go about it. The fuel dealer also makes a profit on the fuel and the installer can do that first delivery inspection that is recommended.
    I personally did not own an oil company but worked for several fuel dealers that did not employ their own service personnel.  I would often replace a fuel oil tank and wait for the driver to show up for the first delivery.  Only one time did I have a problem where a fitting has a pinhole.  Stopped the delivery and had to remove the defective fitting.  The driver returned after delivering to another customer while I replaced that bad fitting, and we completed the delivery that day.  Always a good practice to have 2 people on hand for the first delivery to a basement tank.
    I also included a provision to leave a temporary tank or barrel to use up the oil from the old than that was removed.  That way there was no need to throw away any old oil.  Once a customer owns the oil in their tank, they either have to pay to get rid of hazardous waste or burn it.  When oil was close to $5.00 per gallon, no one wanted to pay to have it removed.
    I was associated with a tank removal company that would charge you to remove your old oil and donate it to a church.  The Church would give him an address of someone that needed help with their fuel costs and pump that old oil into their tank.  There were occasions where those deliveries of “Free” oil would cause a clogged filter or nozzle… so much for  “Free” oil after paying for a service call to fix the heater.
    mrblint
    Let me know how you make out
  • mrblint
    A "pump-over" doesn't void the warranty of the the tanks made by one of the major players in the sector, so I'm switching manufacturers, even though they don't offer one in the perfect size for our space. Scheduled for install early next week, barring anything unexpected.
  • SuperTech
    SuperTech Member Posts: 2,614
    Sounds like you are going with a box shaped tank with a plastic liner. The only thing I don't like about them is that you can only connect the oil supply line to the top of the tank. I've always preferred single pipe setups connected to the bottom of the oil tank. Just as long as your installer knows what he's doing you won't have any problems. But there's definitely more potential for issues with a tank that has the oil line coming out of the top
    EBEBRATT-Ed
  • mrblint
    Yes, box-shaped with plastic liner with top supply line. Our old tank had the line coming out the top of the tank, then immediately down to the floor, then following the exterior wall and taking a 90-degree turn and then going up about 3' to a TigerLoop / Riello F4 burner. Maybe 25' total run. Until we had the TigerLoop installed, we did have some pump-pull issues.
    Installer of new tank wants to run the supply line up to the floor joists (about 7') and then follow that same exterior wall path, up at ceiling height. The line would have to take a small dip to go under some 1 inch copper piping for a sump pump that discharges outdoors in the front yard. I've read that dips in the supply line can trap air, so I'd like the installers to follow the same path along the floor that the old line took.
    Yup. The infamous TL.
    Everyone insists you can run single pipe overhead
    But the you end up with a TL more times than not.
    LRCCBJ
  • mrblint
    If we have the TigerLoop already (and it has been working fine for some years now with the single supply line running along the floor), would there be a potential issue if they run the line up at the ceiling (attached to bottom of the floor joists) and the line has to take a dip of ~1.5 inches to go under a 1" inch copper pipe that runs along the bottom edge of one of the floor joists?
    I don't like overhead lines period unless hooked up two pipe. Others will say it is fine. JMHO.
    With a tiger loop you should be fine IF the installer knows how to make the connections tight and can flare tubing properly
    mrblint
    edited May 31
    I don't recommend placing any oil from any steel tank into any new tank. That is a result of experience.
    1. Do you know for sure that there are no TBD Tank Bottom Deposits (contaminants/sludge) in the oil that is in the old tank? I can guarantee you that there are. They are also black and smell awful
    2. Can you be absolutely sure that those TBDs will not get into your new tank? I can guarantee you that they will.
    3. Will those contaminants be stopped from entering the oil pump and/or nozzle during the subsequent winter operating season?
    4. Do you like it when you have a burner failure when it is very cold?
    If you can answer YES to all these questions then by all means put the old oil in the new tank
    Regarding the slight up and down you will get in a new fuel line regardless of the reason, that will not be a problem. Especially when using the Tiger Loop.
    EDIT:
    Case History: This actually happened to me. As a result of the previous fuel dealer's poor tank maintenance policy for years, there were a number of homes in Ocean City NJ that had a problem with clogged nozzles. This one homeowner that suffered from this problem was told by the city that they needed to replace the buried sewer pipe that connected their home and the neighbors home. Since the fuel oil tank was over the buried pipe, they needed to remove the tank and could replace the tank after the work was completed. due to the age of the tank, the city would also purchase the new replacement tank.
    I provided the estimate for the needed work and included putting a temporary fuel supply in place so the home would not be without heat and hot water as a separate line item from the replacement tank quote. I also added an option to keep the three 55 gallon drums as a temporary tank until the old oil was used up. This would ensure that no old oil would be introduced to the new tank. The city declined to pay for that option and the homeowner wanted to save $$$ and elected to just pump the old oil back into the new tank. Against my strongest recommendation to use up or throw the oil. Away, the customer (who is always right)  instructed me to put that old oil from the three 55 gallon drums back in their new tank. That winter there were 3 service visits to replace a clogged nozzle that also included a new filter and pump strainer service.
    This customer wanted an explanation as to how this dirt crud and sludge could have possibly got into the new tank?   I explained that the former fuel oil dealer was not using any additives in the oil they have been delivering for the last 30 years since the son took over the business from the father.  This saved him $$$ but as time went on all the tanks that were served by that company were accumulating copious amounts of tank bottom deposits (TBD).  I kept a sample of what we pulled out of the old tank before the scrap man removed that tank from the property the previous year.  I also showed him the 2 oil filters and nozzles that were covered with those TBDs. I left them in a plastic container in the boiler room because I had a suspicion that I might need them in the future.
    Now the customer understood why I strongly recommended paying a little extra for the temporary fuel drums to use up the oil.  When the customer asked what can be cone about this problem. I gave him a more expensive option that would include running the fuel oil tank to near empty.  I would then set up a containment system in his backyard so I could lay the new contaminated fuel tank on its side and take 20 gallons of new oil, clean oil and pump it through a hose with a spray nozzle on the end of the hose. This was in order to use the clean oil like you might use a garden hose to wash down your driveway or sidewalk.  The pressurized oil would force the TBSs off the bottom of the 1 year old tank and allow another pump to suck out the contaminated oil with all of the TBDs that were  suspended in that oil.   After 4 rinses  (5 gallons at a time) all the contaminants were virtually gone.  Then I reinstalled the tank and had a delivery of fresh oil delivered with an extra tank cleaning additive to be added to each delivery.
    The following winter there were no plugged nozzles reported by this customer.  Since you will be using oil from your old tank, I can not tell you that you will have that same problem, however I can tell you that this customer’s attempt to save $$$ by not throwing that old oil, cost them much more than they had planned.  But at least the toilets were flushing properly now.
    bburdmrblint9326yssh
  • mrblint
    edited May 31
    Thanks. I won't object then if they want to run the line across the floor joists above.
    I am going to try to talk them into bringing 50 gallons of clean new diesel oil to test the system with, and offer to pay extra for their effort and of course for the oil.
    The easiest way to get this done is to:
    1. Remove any old oil and either discard the oil or put it in a temporary storage Drum or Tank on site.
    2. Connect a temporary fuel line from the temporary tank to the burner.
    3. Remove the old tank to make room for the new tank
    4. Install the new tank
    5. Have fuel delivered to the new tank by the fuel delivery company. Best to have the delivery scheduled the same day as the new tank installation so the installer can see his work in action.
      1. When the driver is delivering the first tank of oil, have someone on the inside to see that there is no problem.
      2. Make sure the inside man can communicate with the delivery driver in the event of a fuel leak to stop the delivery
    6. Once the new fuel is in the new tank The job is almost finished. Pay for 90% the job if it is successful to that point.
    7. Then let the old temporary storage stay on site until all the old oil is used up.
    8. When you have no old oil left, call the installer to connect the new tank with the new fuel line and new oil filter to the burner.
    9. Change the pump strained and oil burner nozzle.
    10. Remove the temporary storage and fuel lines from the site.
    11. Do the combustion test and adjust the burner as needed.
    Any more logistical thinking is just a waste of time.  I have done this many times and it is the best way to ensure you don't put problems from the old tank into your new tank.
    I include enough labor in my tank price to allow for that return trip after you run out of old oil. I also charge additional rent for the customer to use my temporary storage drums or tank if it takes more than 60 days to use up the old oil. But I usually calculate the job with the old fuel that is int the tank to be at a minimum, so i rarely need to charge extra. Only remember one guy that ties up 3 of my 55 Gallon Drums the entire summer so he didn't have to pay the hazardous waste fee to get rid of that oil.
  • Robert O'Brien
    " Tank location should be chosen in accordance with the following requirements: ▪ The tank should be placed in an area where it is unlikely to be adversely affected by normal household activities; ▪ The tank should be placed in an area where it can be visually inspected from all sides; ▪ Under new NFPA guidelines, any outdoor steel tank fitted with a side outlet or installed in a top-draw configuration must be a double-bottom or a double wall tank. ▪ The tank label must be visible; ▪ If possible, tanks should not be located directly under house eaves where they may be subject to falling snow and ice or dripping water. Protection should be provided if there are no other placement alternatives; ▪ Tanks should not be placed in intimate contact with walls or structures since leaves and other organic matter can accumulate and cause external corrosion of the tank; and ▪ Tank location shall respect the local code for distance to property lines, to other energy sources or to other storage systems."
    HydronicMike
