House heats up but thermostat is turned off AND thermostat's battery is dead
2»
    109A_5 Posts: 4,363
    If all wires are disconnected from the two T - T terminals, when the system is powered up if the relay still activates the L8124C is defective, that was mentioned before.
    Are you sure this black wire is not pushing on the armature of the relay (the black plastic part) ??? It is way too close for my comfort.
    If it helps you any the relay's coil is visible from the side.
    109A_5 Posts: 4,363
    " Yet the circulators are running to heat the house with TT open "
    How many circulator(s) are there ???
    109A_5 Posts: 4,363
    Left - Relay de-energized, contacts open.
    Right - Relay energized contacts closed. Pressure from an ill placed wire could push the armature (the black plastic part) and erroneously close a contact.
    HVACNUTEdTheHeaterMan
    Jamie Hall Posts: 27,738
    First, get rid of ChatGPT. It hallucinates. So do some of us, but at least we know when we're doing it.
    Then start by looking at @EdTheHeaterMan 's comments. He really does know what he is doing.
    Also, the circulator CANNOT run unless it is getting 120 VAC power from somewhere. If it keeps running when T-T is open and either the relay in the box is stuck closed — it happens — or there is another 120 volt feed to the circulator which, if I'm reading your comments correctly, seems to be what is happening (circulator running with T-T open and presumably your test showed the relay really is open — although that is not clear.
    Now I have to admit that I'm a little concerned, as it almost seems that you are poking about at energized wiring without really knowing what's happening. The problem with that is that connecting yourself to an energized wire can ruin your whole day. You were fortunate with your "insulated" needle nose pliers — that's a 24 VAC circuit and you got away with it.
    109A_5 Posts: 4,363
    " Last fall the boiler system was in perfect working order, never a drip, no corrosion. Now there's a puddle on the floor in front of the boiler. How am I going to fix this? Is it fixable? "
    DIY or Plumber. Replace what is leaking, may need the tankless coil assembly. Seems like a lot of rust and corrosion for only a few months of leaking.
    HVACNUT Posts: 7,656
    Is the relay pulled in while the circulator is running without call for heat? Like @109A_5 showed, you can manually press the clapper to see if the contacts disengage. Or you can pull slightly on the clapper to engage the contacts. This thread should be dead by now.
  • WilliamJ
    WilliamJ Posts: 29
    edited May 2025
    @HVACNUT I will test the thermostat wires with my multimeter. I have no reason to believe they are energized, see pic. https://photos.app.goo.gl/rDvFuvSbQ1SK8nhG6 How do I use a multimeter to test for a short in the t-stat wires? Answer: search youtube.
    @109A_5 previously I only disconnected one of the two T-T wires as I understood that was sufficient to open the circuit for testing. This time I'll disconnect both T-T wires.
    Anyway. I'm going back to the house today. I will check the relay to see if it's stuck. I still have the old aquastat. I could reinstall it, now that it's dried out.
    EdTheHeaterMan Posts: 12,691
    edited May 2025
    That CK61 is an older version of the one I showed in the diagram above This is the manual for the Field CK-61. The wiring is similar
    I have updated the wiring diagram for you to print and place with the heating equipment for future reference.
    @109A_5 has a very good illustration of the 1K2 contact inside the L8124C 1K relay I referenced above.
    Untitled Image
    If that contact is welded together or there is a wire pushing on that armature, then the contacts will always make the circulator operate whenever power is applied to the L1 contact on the L8124C control. That contact in that photo must be open to stop the circulator from operating. If you find that the contact is being manually closed by an obstruction, then removing that obstruction will solve your problem. If the contact is welded together, then you need to replace the control.
    Also @HVACNUT indicates that you can manually move (with your finger) the weight on that armature to open or close that 1K relay to see if the contacts are opening and closing. This will power the C1 terminal and disconnect power to the C1 terminal on the L8124C as you change the position of the armature manually. Once you actually move that part with your finger and see that the C1 terminal stays powered (Defective) or opens and closes (Operating properly) you can determine if you need to replace that control, or not.
    Pushing the weight should stop the circulator and the burner, pulling should start the circulator and the burner.
  • WilliamJ
    WilliamJ Posts: 29
    @EdTheHeaterMan Thanks Ed. And everyone.
    After looking closely at this statement
    Later I did some testing with ChatGPTs directions. For one of the tests I connected C1 and I disconnected one of the TT wires then jumped T T with an insulated needle nose pliers. The relay engaged immediately. I also did a couple of other tests. One for Voltage at B1and B2 both when TT is open and again for when it is closed (jumped); I got 120V when TT was jumped. Same results at C1 and C2. Those results were normal, if I'm following correctly. Yet the circulators are running to heat the house with TT open (one wire disconnected) which is not normal and not even explicable.
    I can see that your test may tell me that the L8124C may be operating properly.
    When you say you "Jumped T T with an insulated needle nose pliers" and you saw the relay engage and when you removed the jumper the relay disengaged. This is what is supposed to happen.
    You further stated that B1 to B2 was powered when the T T was jumped and that B1 to  B2 had no power when not jumped.  This is also proper operation.
    You further stated that the same happened with C1 and C2.  This is also the correct operation of the control.
    I do not understand how the circulator is operating when there is no power to C1 if the only wires from the circulator are connected to C1 and C2.   There must be another wire connected to the circulator for it to get power when there is no power from C1. That other wire will provide power to the circulator and provide power to C1 at the same time. In other words, the power is not coming from the C1 on the L8124C.  The power is coming from somewhere else and powering the circulator that also happens to be connected to C1
    Here is a wiring diagram with the photo of the control. I have labeled the components from the diagram on the photo in order to better understand the way that control works. I saw that you may have a question about what is the 1K relay in an earlier message. This can be confusing to many. It took me years to figure out how the diagrams work.
    Bottom line is we need to determine why the circulator is operating when it is not supposed to. With a little more info We can do that for you. I sent a Private Message (PM) with more info.
    After a closer look at your post I am wondering if there is more to look at here. This is what I'm talking about:
    "Yet the circulators are running to heat the house with TT open (one wire disconnected) which is not normal and not even explicable."
    Is "circulators" a typo, or do you have more than one circulator? If you have more than one circulator, then how many thermostats do you have. There are several ways to connect a circulator based on using multiple thermostats. That multiple thermostat thing can be part of your problem and may have nothing to do with the L8124C control.
    109A_5 Posts: 4,363
    edited May 2025
    " previously I only disconnected one of the two T-T wires as I understood that was sufficient to open the circuit for testing. "
    Yes normally disconnecting only one wire is enough to disable a simple circuit. However since you don't seem to be able to identify, isolate, understand, troubleshoot the circuit to the needed level to understand what is causing the problem (and the whole AI thing seems at best confusing the issue), then when I see wiring like this (see picture and comments below), I have know idea what is going on. So then when you seem to be doing random, non logical things, I would try to get to a known useful state, which in part is to disconnect everything from the two T - T terminals and move that wire that is way too close to the relay's armature away from it.
    White wire only at one end.
    Green wire not a consistent color.
    A Green thermostat wire Grounded ???
    edited May 2025
    So we did some "real time" testing over the phone and have determined that the thermostat is defective. The thermostat wire with the thermostat off the wall, does not complete the circuit from T to T on the L8124C1003. The C1 is not powered when the thermostat wire is connected to the L8124C and the thermostat is off the wall.
    When you connect the red and green wire at the room thermostat location the, 1K relay pulls in and the C1 terminal gets power. This is the way it is supposed to operate. The thermostat wire and the L8124C are doing the job as designed.  The thermostat must be defective since the only time the system overheats with the thermostat turned off, and when the thermostat is connected on the wall. Remove the thermostat and everything is operating properly.
    Here is the wiring diagram for your system with the Boiler, Burner with Electronic primary control, L8124C Aquastat, the Field Controls SWG with the CK-61 control kit and a simple T87K thermostat.
    You should print this diagram and have it close to the heating system for future reference.
    This is some thermostats you may want to use for the replacement Honeywell CT87K or the Honeywell CT31A do not require battery replacement.
    You can also purchase other thermostats with more features but the tenant will most likely not benefit from them.
  • WilliamJ
    WilliamJ Posts: 29
    edited May 2025
  • WilliamJ
    WilliamJ Posts: 29
    Ed, Thanks again for all of your help and everyone else who contributed to this thread. Here's a little video I stumbled across today by Steven Lavimoniere. The problem described looks like mine, house heating up past t-stat set point: Low batteries in the thermostat.
    THERMOSTATS IN HOUSE KEEP CALLING FOR HEAT VERY HOT IN HOUSE - YouTube
    Looking at that Steve L. video from 2018 from start to finish.  I did not see that the problem was solved.  He tried to see if the zone valve was open when there was no call for heat.  He indicated that the valves were in fact closed as they should be.  How he determined the valve was closed is by using the Manual open lever on the valve motor.  There will be tension on the lever if the valve is closed and no tension on the lever if the valve is open.  The problem with that test is that he did not check (feel) the water temperature of the pipe on the discharge side of the zone valve.  If the water temperature is cool to the touch on the discharge side and warmer on the inlet side then you know the valve is closed.   By testing the valve by trying to see if the lever is tight or loose, you will end up letting warmer water from the inlet side of the valve move to the discharge side of the valve and you will not be able to tell the difference between an open or a closed valve by feeling the temperature.
    Once he verified that the zone valve motors were in fact closed he went to the thermostats and found dead batteries.  Once the batteries were  replaced, he could see that the thermostats were in a 73°+ temperature room and the set point was lower than 60°. That condition would indicate that the thermostat is not calling for heat and the zone valves should be closed.  This is what Steve L discovered upon arrival and the batteries did not validate the customer's concern because that is how the system should operate.  Adding batteries to a thermostat that is not calling for heat and discovering it is still not calling for heat after replacing the batteries, does not prove anything.
    Raising the thermostat setpoint above the room temperature and finding that the zone valves open and also operate the burner and circulator will prove that the thermostats are now working and the zone valves are working.   It will not prove that the boiler when it is operating for domestic hot water DHW does or does not cause heat to get to the radiators.  That test was not shown on the video, and therefore I don't think any such test was completed at that time.
    Also one thing that was not talked about was the fact that lowering a heating only thermostat will not lower the room temperature, especially if the weather outside is warm and the sun is overheating the attic causing the rooms below the attitude to warm up from solar gain.   The heating only thermostat can not make the room temperature go down.  It can only stop the burner from operating and the circulator pump from operating so the radiators do not make the rooms hotter.    It sounded like the customer wanted the heating only thermostat to make the first floor colder.  That thermostat does not have that ability.  The only thermostat that has that capability is the second floor thermostat. But that thermostat must be set to operate the air conditioner.   If the customer doesn't want to turn on the air conditioner, then the same holds true for the second floor.  Setting the thermostat for heat and turning the temperature lower will not make the room get colder…  It will only allow the room to get colder.
  • neilc
    neilc Posts: 3,201
    so ya think he had a Leakha, or not?
    known to beat dead horses
