What would cause such rapid destruction of valves?

Old_Steam
Old_Steam Member Posts: 15

I looked over my baseboard system heating plant for the first time in months. I noticed severe deterioration of a valve that only happened over the last year. Can anyone advise what would cause such rapid destruction of the metal? I grabbed a screenshot of it from about 14 months ago and it looked fine. Now it’s scary. What could be going on here lately?

IMG_7936.png IMG_7911.jpeg IMG_7914.jpeg IMG_7910.jpeg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,663

    Leaking around the stem

    hot_rodmattmia2
  • JMWHVAC
    JMWHVAC Member Posts: 83

    Needs replacement. The expansion tank that its dripping on may also be compromised if the rust is too deep.

    mattmia2
  • pecmsg
    pecmsg Member Posts: 5,971

    The air vent is leaking.

    Agreed, replace the x-tank as well

  • Old_Steam
    Old_Steam Member Posts: 15

    so that Cryo-tech antifreeze that leaked out would cause that much corrosion?

  • leonz
    leonz Member Posts: 1,497
    edited April 25

    Speaking as a homeowner,

    Galvanic Corrosion, also known as bi-metallic corrosion caused this.

    If you are going to keep this plumbing as is-

    When replacing the parts you should be using bronze fittings/pipe nipples etc. all the way back to the heavy wall pipe and tees, and a bronze shut off valve and bronze pipe nipples to shut the boiler water off from the pressure regulator as you should only be filling the system ONCE and shutting the water off and leaving it off. You also need a back flow preventer piped before the water feed and pressure regulator.

    mattmia2
  • Old_Steam
    Old_Steam Member Posts: 15

    should I keep using that antifreeze if it’s that corrosive? It’s a summer house that we don’t get to much in the winter, so if the electric goes out on a very cold winter day, I don’t want the system to split open again and flood the house. This happened about ten years ago during a power outage.

  • MikeL_2
    MikeL_2 Member Posts: 530
    edited April 25

    Like most equipment in hydronic heating systems, antifreeze requires maintenance.

    Testing its concentration & acidity should be done annually. We like about a 30% concentration. And, the leaking piping, fittings, or accessories should be fixed antifreeze tight.

    The interesting thing about antifreeze is it will find an escape where air or water won't. A chemist told me it has to do with surface tension.

  • leonz
    leonz Member Posts: 1,497
    edited April 25

    I have to ask if you have a freeze prevention valve on this boiler??? A boiler protection valve like this would have opened and it would have prevented freeze damage/expansion from occurring but it would not have prevented the galvanic corrosion.

  • hot_rod
    hot_rod Member Posts: 24,966

    I would not have a fill valve on a system with glycol. Use a fill tank. Or a separate expansion tank as a fill.

    Screenshot 2025-04-25 at 8.09.02 AM.png

    Screenshot 2025-04-25 at 8.13.32 AM.png

    Air vents will spit some air and fluid from time to time, that is not unusual.

    The glycol should be checked every few years Ph mainly. A test meter or test strips is all you need.

    Screenshot 2025-04-25 at 8.11.04 AM.png Screenshot 2025-04-25 at 8.10.42 AM.png

    When the ph drops into the low 7 or below it is time to flush and replace the glycol.

    Tough call on whether you really need or want it? Do you drain down the plumbing system in winter?

    I would flush that system, run a hydronic cleaner, then refill with a 30- 35% premix glycol.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • pecmsg
    pecmsg Member Posts: 5,971

    With glycol in that system that automatic feed valve must be removed, the make up waterline disconnected to prevent any type of cross contamination of the potable water system

  • Old_Steam
    Old_Steam Member Posts: 15

    what do you think would cause all that within 14 months? I think the valve was in there over 40 years with no issue.

  • mattmia2
    mattmia2 Member Posts: 12,524

    just water dripping like that would do it, the glycol is just a bonus.

    since the leak has compromised all your old style air elimination, i'd replace all of it. i'd put in a modern microbubble separator in place of the air scoop, new expansion tank, and i'd use a caleffi prv if you are going that route but since you're running glycol the prv may not be what you want.

  • hot_rod
    hot_rod Member Posts: 24,966

    Most hydronic components are rated for 30- 50% glycol mix. I don't know that that fill valve is glycol approved?

    Some of those Watts had a little rubber flapper as a check on the discharge, but it looks like glycol was inside that fill valve.

    Hopefully there is a BFD as that glycol then could enter the homes water piping in the event of a low or no pressure condition.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 12,524

    a pretty low concentration of glycol will keep the system from bursting if the heat fails in most climates.

    ethicalpaul
  • mattmia2
    mattmia2 Member Posts: 12,524

    if the system is mostly unattended you might want to close the cap on the new automatic air vent after the initial fill and it has run for a few weeks to work the air out so it doesn't leak undetected for a couple years like the old one.