Shoulder Season Issues (Increased Pressure, Rattling Radiator)
NY2024
NY2024 Member Posts: 21
Hi everyone,
During this year’s heating season (January & February 2025), I got the one-pipe steam system working pretty well on our newly purchased house in New York's suburbs (with a lot of help from the members here). The system was operating at pretty low pressure (generally just a few ounces of pressure to 1 PSI max) and heating the house relatively evenly. During Jan/Feb, I insulated all of the near-boiler piping and the 40 ft. main in the basement with 1 inch fiberglass insulation. I replaced all the valves on the radiators with new Maid-o-Mist valves and adjusted them using extra orifices I bought till the system was relatively balanced. I also swapped out the very small Gorton No. 4 which was on the main when we bought the house for a much, much larger Gorton No. 2.
This shoulder season (and particularly very recently), the system hasn’t been working as well. Although it doesn’t cut out on pressure (set at 1.5 PSI) the system operates at a near constant 1.25 - 1.4 PSI. I can tell that the radiators/boiler don't like this. One radiator in particular, on the 1st floor, sounds kind of like a dishwasher when it's running, with condensate swishing around in there. It rattles and bangs too. During the heating season I had a #6 orifice on this one. I just swapped it for a #4. This has helped slightly, slowing the steam uptake on that radiator and I believe helping to redistribute some of the steam more evenly up to other radiators along a nearby riser. However, I can still hear the condensate swishing around, the radiator rattling and the radiator valve hissing too much (though the banging stopped).
The valves on certain other radiators are hissing and whooshing much louder too, whereas when the system was operating at lower pressure it was a very pleasant, steady venting sound coming from them.
The boiler itself is definitely oversized for the EDR of the house. Is it possible that this is showing itself more now during the shoulder season than during the prime heating season?
The EDR of the 10 radiators in the house is 302 sq. ft. (i.e., 72,480 BTU/HR). The Burnham steam boiler (model number SIN6LNC-LE2) has a net EDR of 450 sq. ft. (i.e., 108,000 BTU/HR). So, the boiler is appx. 49% oversized by my estimation.
Any ideas about how to solve this so that the system operates at lower pressure again for the shoulder season and can get rid of the whooshing, hissing valves and rattling in that one particular radiator.
Should I decrease the orifice sizes of the radiators closest to the boiler and increase the orifice sizes in the radiators higher up in the house to draw more steam to the higher floors quicker to relieve pressure on those radiators closest to the boiler (which are the ones hissing and rattling)? Is this likely related to the boiler being oversized? Perhaps having insulated all the near boiler piping and the full main (as well as the exposed portions of all the risers) in the basement has made the oversized boiler even more prominent an issue.
Please let me know your thoughts. Thank you very much!!
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    How much temperature swing is your thermostat allowing? Try setting it to the minimum possible and see if things improve.
  • dabrakeman
    dabrakeman Member Posts: 906
    edited April 2025
    The only real difference between the colder months and shoulder season is that likely cycles are spaced out significantly farther apart so piping would be generally completely cold at start of cycle as opposed to warm. This requires more steam and thus more condensate production to get steam out to the radiators. Given your described symptoms you obviously want to make sure your new Gorton #2 is still functioning but more likely the higher amount of condensate is causing problem. It would seem it would only cause problems if the condensate is building up in the supply piping somewhere restricting steam flow so I would reexamine your mains and takeoffs for problems with pitch or sags. I too live with a similarly oversized boiler. First cycle of my recovery is the only time I ever really hear any occasional light hammer so probably for the same reason. Others here will probably be able to provide more insight.
    ethicalpaul Member Posts: 8,385
    edited April 2025
    If you hear sloshing in a radiator, regardless of the main vent, regardless of the radiator vent, then either your boiler is surging, or there is a sag in the supply pipe to some radiator that is collecting water. Is the sound only at a single radiator? What happens to your water level during a call for heat?
    Respectfully, I don't see the relevance of the thermostat here.
    Respectfully, this is mistaken thinking. The boiler produces X amount of steam, and Y amount of condensate regardless of whether it's the shoulder season, and regardless of the size of the main vent.
    ^^^^ this I can get behind
  • dabrakeman
    @ethicalpaul perhaps you misread my point as I think you know a cold system does indeed run longer to get x amount of heat to the radiators than a warm one even after producing steam and thus it does indeed produce more condensate. This is just due to the delta T of the piping.
    Jamie Hall Member Posts: 27,014
    @ethicalpaul and @dabrakeman — you're both right. Starting from cold will produce more condensate — in the mains and runouts — than starting from warm. Not, however, in the radiators (usually — although very long off periods will result in the radiators being cold, too). After all that, the difference isn't that much — but it's enough that you may get pooling or even slight water hammer on a cold start which you wouldn't get on a warm start.
  • Hap_Hazzard
    I think @dabrakeman and I are looking at the same issue. In the spring and fall, the off cycles are longer; thus, issues relating to temperature swing become more apparent. The greater the swing, the longer the off cycles, and the pipes and radiators don't retain much heat between cycles. It's perfectly easy to test this hypothesis. Adjusting the swing doesn't cost you anything.
  • NY2024
    Thank you guys. By adjusting the swing, do you mean changing the 'heating cycle rate' on my White & Rodgers Series 80 Thermostat from SL (Slow) (which I currently have it set to) to FA (Fast)? See excerpt from the thermostat manual below:
    "Select FA or SL (Fast or Slow) Heating Cycle Rate - The FA setting is frequently used for gas, oil or electric heat. The SL setting produces a longer heating cycle which is normally for hot water or steam (hydronic) systems. Both settings produce very accurate temperature control and can be set to your personal preference. FA cycles the system just under 1°F and the SL setting cycles at approximately 1.5°F."
    In response to some of your other questions: (i) Yes, the Gorton # 2 on the main is still working; and (ii) I believe the condensate is building up somewhere in the system as generally at the start of the cycle now, the boiler cuts off on low water one time (which wasn't happening during the prime heating season). I think the condensate is getting stuck out in the system during the early part of the cycle.
  • Hap_Hazzard
    @NY2024 Yes. Set it as fast as possible. I've found this works best for steam. If it doesn't help you can always change it back.
  • delcrossv
    delcrossv Member Posts: 2,189
    Yes. If your stat had cycles per hour, I'd recommend going from 1 cph to 2.
    in your case, I'd try switching from slow to fast . You'll get more firings but things won't cool down as much.
    FWIW, one of the one pipe systems I service is happiest at 2 cph.
    Hap_Hazzard
    I think if changing the swing affects anything during the shoulder seasons (if), that's not really a solution of anything
  • delcrossv
    Depends on what your solving. This is "treating symptoms ", where a major repitching job would be "treating causes".
    A running all winter coal fire was a lot more forgiving of dubious piping than gas or oil is.
  • NY2024
    Thank you! I'll let you know how things turn out after I adjust the swing later this afternoon. My guess is that it will help some. Right now, in the shoulder season, if I set the temp at 68, the thermostat often overshoots 2 degrees to 70. Hopefully adjusting the swing will run the system for less time, avoiding some of the pressure build towards the end of the cycle and the temp overshoot.
    Also, to be clear, this was not an issue at all during the heating season. This is purely something that cropped up just recently. I'm hesitant to believe that there is a major pitch issue, as this problem wasn't occurring during the heating season.
    Will keep you posted!
  • dennis53
    dennis53 Member Posts: 68
    On the problem radiator, could the valve disc have fallen off the stem, allowing steam in but trapping water?
    Any new piping installed lately? A good skim might reduce your higher-than-normal pressure.
    Good luck,
    Dennis
    Dennis
    I hear you but I reiterate that if you are hearing sloshing in a radiator, SOMETHING is wrong other than it being Spring.
    delcrossv
    Steamhead Member Posts: 18,324
    I'll bet the valve disc came off- this is not uncommon. If you disconnect the radiator you should be able to see this- if the disc is lying on the seat, replace the valve.
    Consulting
    delcrossv
  • Hap_Hazzard
    I'll take that bet. What are we playing for? 😉
    mattmia2 Member Posts: 16,043
  • NY2024
    Just wanted to thank everyone for their help on this. I drained a good amount of water from the boiler and it solved the issue. The boiler went back immediately to operating at low pressure (maybe under 10 ounces of pressure) and the swishing / rattling inside the radiator at the end of the main ceased. It was good for several days like this.
    Now, unfortunately, about 10-12 minutes into the boiler cycle, it starts again (pressure building to 1.25 PSI, rattling/swishing inside radiator at end of main, most radiator air vents making more noise than they should). This is better than before, where the pressure started building to 1.25 PSI as soon as the steam hit the end of the main (maybe 4 minutes into the boiler cycle). I don't know if at some point the automatic water feed added additional water to the boiler. Maybe I need to install one of the automatic feeders that has a meter on it so that it can be measured.
    My neighbor (with whom I share one wall) has a problem where he drains water every 2-3 days from his boiler (I haven't gotten the details). However, certain of his risers are inside the wall between our houses, and I can hear the banging and condensate waterfall sounds in the risers coming through our wall when it gets bad. It seems like it's a more severe version of the problem I'm having.
    Has the water level in the boiler increased? You didn't mention the water level since the issues have started again.
  • NY2024
    Thanks, Paul. I didn't notice the water level in the boiler increasing and I didn't think that water level was an issue initially.
    However, I was able to drain maybe a gallon+ of water before the boiler cut out on the low water cutoff. While I was draining the water from the boiler, the water in the sight glass moved downwards, but not all that much (maybe from the middle of the sight glass down by an inch or two). When the boiler cut off on low water, there was still 2+ inches of water in the sight glass.
    The automatic water feeder came on and fed some water into the boiler afterwards, but I can't imagine it fed anywhere near what I drained from the boiler (based on how long it came on for).
    After this, the boiler went back to working the way it was during the heating season (quite well) for several days. However, the problem returned (although it isn't as bad as it was before I drained the boiler - it happens 10-12 minutes into the cycle rather than as soon as the steam hits the end of the main).
    I think there might be something wrong with the sight glass, where it is not accurately reflecting the amount of water that is actually in the boiler.
    Either the feeder isn't shutting the water off completely, or the bypass valve around the feeder isn't shutting off completely. If the feeder is a Hydrolevel VXT, the valve can be rebuilt and you won't need a completely new feeder. Also, excessively high water service pressure can cause feeders to leak.
    I bet your neighbor is having the same problem as you.
    Consulting
    I'm getting a little lost in the details but based on your descriptions of what you're seeing, I would suspect that the boiler is throwing water into the steam mains. This is quite common so I have to be careful to suspect it when it's not the issue.
    What I saw you say is that you think that draining water from the boiler helped…that may be, and I was trying to know if, since you saw the return of your issues, that the water was high again.
    From your last message it didn't seem high at all so I don't really have a next step for you.
    I have clues from your descriptions of things that you might have some incorrect ideas about how your boiler operates which is not at all unusual, nor any kind of judgment.
    if you are in southern NY I could have a look and share some knowledge…my mother lives in the New Paltz area and I work in NYC. You can find my contact info by following the links in my signature below.
    where is the level on the sight glass before and after you drain water? lowering the level below normal level may be compensating for water quality or near boiler piping issues(or even system piping issues).
  • NY2024
    Thank you all! Paul, I will likely get in touch with you. Thank you very much for the offer to help!
    Here's three photos. The first is the level before starting to drain. The second is the level after draining (and after the boiler cut out on low water, although there appears to be more than sufficient water still in the sight glass). The third is how much water I drained.
    edited April 2025
    You want the level at the 1/2 to 2/3 point on the gauge glass…I like mine even higher but I know my water is very clean and not carrying over.
    Even though there is still water in the glass, the LWCO is doing the right thing in your case by stopping the boiler there, and the auto-feeder is doing the right thing by putting more in.
    The oily scum on the gauge glass above your water line adds evidence that your water quality is poor and may be causing surging/carryover (which could definitely lead to all the sloshing sounds you are hearing). This would likely be accompanied by a significant (more than 2") drop in the water level during steam production.
    That oily sign on the glass can't really be cleared by draining, only by skimming. It also might be so old that it's not playing into this. It can be confusing!
  • NY2024
    Thanks, Paul. My guess is that there are water quality issues. Although we bought the house less than one year ago, the boiler is 20 years old. I doubt the boiler has ever been skimmed, as there is no skim port. Additionally, before we moved in, some of the steam pipes were moved and a riser runout from the main was re-piped (due to renovating the kitchen). This could have introduced oil into the system (which also was not skimmed). Furthermore, as you wrote above, the water definitely drops more than two inches during steam production. Oftentimes, it ends up staying consistently close to the very bottom of the sight glass throughout the steam producing cycle. It looks like water is running down from the top of the sight glass down to the bottom of the sight glass during steam production as well (if you look closely).
    This is certainly something I intend to cover at an upcoming boiler maintenance once the heating season is fully over.
    edited April 2025
    OK these are the key pieces of information, I now have no doubt your water is surging. You need to skim. If there really truly is no way to access the skim port there is a product called Squick that can be added via the pressure relief valve. It can work in a pinch.
    Here is my video about Squick:
    what does the near boiler piping look like? if that is sufficiently wrong, no amount of skimming is going to fix the problem of the water leaving the boiler.