Steam Boiler keeps overfilling

lhamwey
lhamwey Member Posts: 1

We have a steam heating system in our home with radiators throughout the house. When we turned it on this winter everything was normal, then after a few days we got really bad water hammering. To the point where it was shaking the walls and so loud we could not sleep. We called out a plumber who said that our boiler (Burnham Independence) was overflowing and there was just too much-standing water in the pipes. He showed me what level the water should be should be in the sight glass and told me to drain it it out to that point. I did and it worked for a few days before I noticed once again the boiler was overfilling again and the water hammering returned.

I drained the whole thing and let the Programmable water feeder fill up the boiler to the proper level. I also noted the reading on how many gallons it filled so I can see if that was where the water was coming from. A few days go buy and once again it is overfilled. I checked the water feeder reading and it was the exact same as when I last filled it, so I assume the additional water is not coming through there.

My question is, where could the water be coming from and is there is a troubleshoot/solve this I could try on my own before calling out another plumber? Right now when it gets bad every few days I just drain it some, but that seems like a inefficient band-aid rather than a solution.

Comments

  • 109A_5
    109A_5 Member Posts: 2,349

    Hello lhamwey,

    Assuming you have a VXT auto water feeder, it is just a timer (when it is actually active) with the water going through a calibrated orifice, it does not measure water flow like a utility type meter does. So the feeder's valve could be leaking with no record of the added water or a bypass valve could be leaking too. Is there a valve that shuts off the water to the whole system, if so I'd try that to see if it stops overfilling the system. If so keep an eye on the level so it does not get too low until it gets repaired correctly. Do you have a DHW coil ? If so that could be leaking into the boiler. Pictures of your system help us help you.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,602

    Either the manual feed valve or the auto feeder is leaking by. You probably don't have a tankless heater on that boiler

  • tcassano87
    tcassano87 Member Posts: 87

    i assume you don't, but I do you have an indirect HW tank off the bottom of your boiler? The relief valve would most likely be blowing off as well but if you it's possible the coil is cracked inside the indirect tank. Otherwise it's like others said, your automatic feed is no good, the bypass valve is passing or, a long shot you're low water cutoff isn't telling the feeder that its filled and turning it off

  • Silkey
    Silkey Member Posts: 24

    If the manual water shutoff is a quarter turn valve, I guessing its most likely fine.....???

    Is there maintenance I can do on the Autofiller to stop the leak? (Change a washer or similar).

    Will add photos and brand of both later today. Same system I posted about years ago, not has overfilled 3 times.

  • mattmia2
    mattmia2 Member Posts: 12,447
    edited March 26

    well let's ask instead of assuming…

    Does the boiler make domestic hot water, either through a tankless or an indirect water heater or some other scheme?

  • Silkey
    Silkey Member Posts: 24

    No.

    https://forum.heatinghelp.com/discussion/155727/should-new-traps-get-new-cage-units#latest

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,745
    edited March 26

    The VXT feeders have an electric fill valve that should be serviced regularly. There is a strainer on them and a valve rebuild kit available. Any feeder should be installed with unions that can be opened to easily determine if it is passing water inappropriately. It is made for simple repair by a qualified individual.

    The bypass valve should also be installed with unions to check that it is not passing water when closed.

    One of those valves is leaking water when it is closed.

    Hap_HazzardMad Dog_2SuperTech
  • delcrossv
    delcrossv Member Posts: 2,114

    Water doesn't come from nowhere.

    So it's:

    1.Autofeeder leaking

    2.Bypass valve leaking

    3.Slow returns make autofeeder overfill boiler.

    No change in reading, so it's either 1 or 2.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2pecmsg
  • Steamhead
    Steamhead Member Posts: 17,734

    @Silkey , where are you located? We might know someone who can help.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delcrossvMad Dog_2Long Beach Ed
  • Silkey
    Silkey Member Posts: 24
    edited March 28
    20250327_214341.jpg 20250327_222843.jpg 20250327_213925.jpg

    Just cleaned the Wye filter in the Autofiller, hit the manual feed button a few times, and opened and closed the manual ball valve a few times. Hopefully this cleared any debris.

    Opened the Union after the Autofeeder and that seems to be the source. The manual shutoff doesn't have any unions.

    Does the whole unit need to be replaced? First glance is $300.

  • Steamhead
    Steamhead Member Posts: 17,734

    The valve assembly on that feeder can be rebuilt. If you tell us where you're located, we might know someone who can do this.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2delcrossv
  • Silkey
    Silkey Member Posts: 24

    Kenmore, NY 14217.

    I'll ask the the plumbing supply store for the correct rebuild supplies.

    Thanks!

  • Intplm.
    Intplm. Member Posts: 2,599

    Im not sure but does that unit have a 'Dwell time" selector on it? Doesn't it have some dip switches that could be selected and possibly correct what's happening?

  • Steamhead
    Steamhead Member Posts: 17,734

    Kenmore is just north of Buffalo- who's out there?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,745

    If the valve isn't closing tight, a rebuild kit should solve your problem.

    delcrossvmattmia2
  • mattmia2
    mattmia2 Member Posts: 12,447

    Looks like a slide switch but if it isn't calling in the first place that won't help.