Reduced Hot Water Supply from Steam Boiler Domestic Coil
Water temp. at the faucet initially is very hot and soon turns luke warm and doesn't recover. A Honeywell triple function L6081A aquastat controller is used as a high and low limit . There is an adjustable mixing valve . The complaint is lack of hot water after a short initial supply of very hot water. Is this a mixing valve problem ?
Comments
-
Much more likely a scaled up coil in the boiler problem.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
You can ultrasonically clean the scale out of the coil with good success. One company offering this service is some areas is called "Hot Water Plus".
0 -
Compare their rates to the cost of a standalone water heater
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0