Boiler with Hydro Air vs New Multi-Head Mini Split
I’m still working hard to find the best setup for a client with an existing propane-fired boiler and electric resistance baseboard heating (no central cooling).
CZ6. Building heat load of roughly 35K BTU/hr at 1F. 2-story house with single-story addition.
Viessmann Vitodens boiler in the basement (connected to Vitocell indirect WH) currently serves the entire 1st story and addition via a mix of underfloor and under-the-subfloor radiant. Second story is heated via electric resistance baseboard.
So, we’re down to the following options for heating the 2nd story:
A) Add a hydronic air handler to the attic, fed by the existing boiler. Future plan would be to add a cased evap coil to the hydronic air handler for cooling.
B) Install a Mitsu ductless multi-head mini split heat pump.
I’m inclined to go with option A, but I know that option B has its merits.
Option A would include new ductwork and some drywall patching (to accommodate the new piping to the attic). The drawback (as I see it) is that the ducts will be in an unconditioned attic, and I will have to build a “room” in the attic to house the air handler.
Thoughts?
Swinging hammers and fitting pipe…bringing the dream to life
Let’s say that $ is an important consideration…which way would you go then?
+1 For ducted. If you are in a place that needs cooling, hydro air makes no sense as you still need to buy an AC unit.
Wall mount mini splits seem like a good idea on paper but have issues. Each head needs periodic cleaning as the filters are useless. The drains occasionally plug up and cause flooding. Multi splits are near impossible to size to feed bedrooms without significant oversizing which creates comfort and efficiency issues. When my multi split dies, it is getting replaced with a ducted unit.
2