Burnham ALP 105 Hard Lockout 25

VinAms
VinAms Member Posts: 2

Hi. Have an Burnham ALP 105 which showed a Hard Lockout 25 around two week ago. A simple reset from LCD screen then a normal power reset restored operation. Thought Sage controller might have failed. But my heating system been working fine since I reset it. All setting are fine on unit. Can this remain ok? Or should I order a Sage controller or High Limit Switch?

I normally wouldnt expect that to be intermittant. Or could the High temp limit sensor have overshot creating the error. Wanted your opinion or thoughts on this. Any advice appreciated. I do have full documentation on my burner. And all setting are perfect (within tolerances) as per service manual. In past only replace parts have been: Flame sensor, igniter Sensor, flue temp sensor. And of course basic cleanings. Any thought appreciated. TY.

Vinny Frittitta

Comments

  • Ironman
    Ironman Member Posts: 7,696

    Why do you wanna replace a control or safety for doing its job?

    Find out what made the safety trip. It’s most likely due to lack of flow through the heat exchanger which could be from air binding or a circulator problem.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • 109A_5
    109A_5 Member Posts: 2,291

    Not sure how the High Limit Switch switch fits into this scenario. I would think they are referring to the electronics hardware within the Sage unit, but it is kind of vague. Hopefully it was just a glitch.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    VinAms
  • VinAms
    VinAms Member Posts: 2

    My ALP 105 is now a month since I cleared the hard reset and did power reset. Unit running normal since. I realize Sage controller can be indicated. Hoping just a glitch as you indicated.