Burnham V904 make up water

SC
Member Posts: 37
I have a new Burnham V904 Steam boiler with a domestic hot water coil.
How much "make up" water should be used in a month (VXT120 Water feed).
No leaks in return or at air valves
0
Comments
-
It varies, and you will get differing opinions and experiences. More than a gallon a week and I'd be real worried. A gallon a month seems reasonable. Some — like the one I tend to — use a gallon per year, exclusive of necessary LWCO blowdowns.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
What would cause excessive water make up
0 -
-
According to Burnham, any more than 22 gallons per month added to a V904 is cause for concern.
This should be called out around Page 50 of the Installation Manual.
0