Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Burnham V904 make up water

SC
Member Posts: 37
I have a new Burnham V904 Steam boiler with a domestic hot water coil.
How much "make up" water should be used in a month (VXT120 Water feed).
No leaks in return or at air valves
0
Comments
-
It varies, and you will get differing opinions and experiences. More than a gallon a week and I'd be real worried. A gallon a month seems reasonable. Some — like the one I tend to — use a gallon per year, exclusive of necessary LWCO blowdowns.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
What would cause excessive water make up
0 -
-
According to Burnham, any more than 22 gallons per month added to a V904 is cause for concern.
This should be called out around Page 50 of the Installation Manual.
0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements