Converting from oil to gas Eastern PA
We recently moved into an old 1890's farm house, and the house is currently heated by an old Mclain oil boiler with hot water radiators. I would say like 40 years old. We had oil at our last house, but I've never been a fan, we just had to fill up and it costed us $1000 to fill and we now know we blow through oil in this house with using it to heat our water as well with an indirect tank.
Which is why we want to switch to NG, there is a gas main right out front so our utility company will bring a line for free and we just need to pay for the boiler replacement. We have gotten a few quotes and are trying to decide on which kind of unit is best. This will be our forever home and want it to last. One quote said to install a Combi boiler Bradford white BFTCF199NA3XN 20-199KBTU 95% Efficient boiler or a standard efficiency New Yorker CG50F 117,000 btu natural gas boiler.
I've heard mixed reviews on Combi boilers and I'm trying to weigh our options, any input would be appreciated!
Our house is 2600 sqft, and right now in the winter we keep our thermostat between 64-66 and our second floor gets around 70 degrees with the heat rising. I do believe the radiators are not balanced, which I plan on slowly fixing the shutoff valves that are seized and repack them to get them working again.
Comments
-
The very first thing you should do is to get someone (possibly us) to do is a heat loss calculation to size your new boiler properly. If you can tell us:
1. the date of your recent $1000 oil fill
2. How many gallons it was
3. The date of the previous fill (so we know how long it took to burn that quantity of oil)
4. Nearest city (so we can look up climate data)
Knowing that, we can calculate how many BTU/hr your new boiler will need to supply on a "design day," which represents the 99% coldest day of the year in your area.
Having said that, your current boiler is probably in the right ballpark for an 1890's farmhouse which is likely poorly insulated with leaky windows. But if the house envelope has been insulated and air sealed, with improved windows, then it's possible your existing boiler is oversized.
But if your $1000 oil delivery was, say, 285 gallons @ $3.50/gallon, and that was roughly one month's worth of heat/hot water, I'm guessing your house is fairly leaky and poorly insulated, which could mean your existing boiler may be in the right ballpark size-wise.
Also, given your current setup in which the boiler is heating domestic hot water through a tankless coil, that is typically a very inefficient setup in which drastic efficiency gains are possible, particularly by installing a highly efficient boiler like one made by Energy Kinetics (EK). Energy Kinetics boilers are extremely well engineered and extremely efficient. They're also pricey, but if you can afford one, I would highly recommend it in your situation. Depending on how inefficient your current boiler is, it's entirely possible you may cut your energy use by 35% or more (on a total BTU basis).
Here's the Energy Kinetics website. Their president @Roger occasionally posts on this forum and can direct you to a local rep who can answer questions and perhaps recommend a local installer who's familiar with EK boilers.
I am not a heating pro, just a homeowner/mechanical engineer with two oil boilers that I maintain for our 4-unit condo building. I have no agenda, just trying to help homeowners like myself. But if I were in your situation, looking to stay in a "forever home" and looking for a very efficient, reliable, long lasting boiler, an Energy Kinetics boiler would be number one on my wish list.
So if you can start by answering the questions I posted up top, we can help you get an idea of what size boiler you'd need.
0 -
Can't you just replace the burner instead of the whole boiler?
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Wow that's awesome, I appreciate this. I'll look into the EK systems. Here's the info you asked for!
1. the date of your recent $1000 oil fill- 2/21 was our last fill
2. How many gallons it was - 261 gallons (which i think they either over filled our 275 gallon tank or their meter was off which i'm not happy about)
3. The date of the previous fill (so we know how long it took to burn that quantity of oil) 1/15 they put in 180 gallons
4. Nearest city (so we can look up climate data) Schwenksville, PA
There are approx 40 windows in the house, and 16 windows have been replaced (soon to be 25 total).
The kitchen is very leaky, I need to try and take a look at how to fix this. Also I need to figure out how to insulate an older home better with plaster walls.
0 -
A couple of thoughts on tightening the envelope — which will be the biggest bang for your buck.
First, windows. Unless you are getting absolutely top of the line replacement windows, and the folks putting them are very good craftsmen, you are — bluntly — wasting your money. I have found that, in general, tightening up existing double hung windows and installing quality storm windows (either interior or exterior) well be as effective, if not more so, than good quality replacement windows — and will last about 5 times as long.
On insulation. 1890s construction is likely to be balloon framed, and that is not that hard to blow dense pack cellulose insulation into. That is much preferable to any type of foam (conscientious contractors will not try to put foam into plaster walls anyway) and much MUCH cheaper than taking the plaster apart, even if you replaced it with drywall, which would be a tragedy.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Get a blower door test done. Then you will know where the leaks are and can deal with them.
Tightening the envelope has the greatest return on investment. Now you can go with a smaller boiler and burn less money.
Did that boiler run 24/7 in cold weather or cycle on / off?
It's the end of the season, concentrate on improvements 1st.
0 -
Looks like a 60kbtu heat loss, so you're decently oversized. If you switch to gas, I'd keep the indirect OR go with a standalone gas tank. I wouldn't let DHW be handled with a boiler without any storage, you have the space!
Be extremely careful with insulation and air sealing improvements, they can sometimes be good investments but quickly can become terrible investments. There are STEEP diminishing returns and you can easily be paying 10x market prices for heat using insulation.
0 -
Energy costs like those you are dealing with really put a damper on living in an old house. (I own a 1700s farmhouse with 1800s addition…I get it).
The replacement windows will be helpful. The rest is part of the journey to bring the energy bills down to a far less painful point.
Would you post a picture of the exterior of the house (to better see what you’re dealing with)?
Swinging hammers and fitting pipe…bringing the dream to life
0 -
Using HDD data from nearby Allentown, PA I get HDD65=1419 for the span 1/16 to 2/21.
During that time, you used 261 gallons of oil at most, some of which went to hot water. But for worst case envelope heat loss, let's assume all of it went into heating and none into hot water.
261 gal x 140,000 BTU/gal x 0.8 efficiency = 29,232,000 BTU
(You boiler is running less than 80% efficiency, but using 80% will give us a best-case heat output, which tells us your maximum possible envelope heat loss).
29,232,000 BTU / 1419 HDD = 20,600 BTU/HDD
20,600 BTU/HDD / 24 hrs/day = 858 BTU/hr/heating degree
Design temp for Allentown is 11 degrees. Let's say desired room temp is 70. So delta is 70 - 11 = 59 F.
858 BTU/hr/degree x 59 deg = 50,622 BTU/hr heat loss at design temp (at most)
This assumes (1) no BTU's went to hot water production, and (2) that your boiler operated at high efficiency (which it's not), meaning this is the theoretical maximum heat loss for a design day (excluding wind). So your actual envelope heat loss is going to be lower than this upper limit. If, say, 20% of your oil went to hot water production, then your envelope heat loss for a design day is closer to 40,000 BTU/hr.
ASHRAE recommends sizing boilers to 1.4 x design heat loss, so 1.4 x 40,000 BTU/hr = 56,000 BTU/hr net output for new boiler sizing.
So a new boiler rated at, say, 75,000 BTU/hr input and about 56,000 BTU/hr output would be in the right ballpark. And further envelope improvements will reduce your heat loss.
2 -
It would turn on/off, I'll see if i have any local contractors that will do a blow door test.
0 -
We just moved in about a month ago, so we are trying to figure everything out still! Here are some exterior photos. There have been a few additions, but I believe they all are still plaster walls.
0 -
There's not much you can do about the lack of insulation in your walls without spending a lot of money and often not getting the results you hoped for, but fixing drafts can do a lot to lower heating costs and improving comfort. But, to fix 'em, first you gotta find 'em. I have a low-cost, low-tech method for doing this.
Close all your windows and outside doors, get some insense sticks, light one and walk around the house trying to detect air currents. You don't need to do this in the winter. You can wait until it's warm enough to do whatever work you might need to do on the outside. For best results, do it when no one else it walking around the house disturbing the air. Patience is key. If you try to hurry, it's easy to get frustrated and confused.
When you detect moving air, keep moving towards the source where the air is either coming into the house or exiting, so be aware of which way the wind is blowing outside. Since it's usually easier to find where air is leaking into the house, you may need to repeat the processs over several days where the prevailing wind direction is different.
When you locate the source, you just need to figure out how to address it. Sometimes it's just a matter of some caulking; sometimes you need to replace or install some weather stripping; sometimes you need a new window or door. Do the easy/cheap stuff first, then prioritize what's left.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-242 -
Those pics explain a lot, because the stucco exterior helps reduce air infiltration. So the combination of exterior stucco and some new windows help account for a heat loss that isn't bad for an 1890 house in your area. You're already under 19 BTU/sq ft, which is good, and will get even better with replacement windows properly installed, of course.
1 -
Please… before you spend close to a grand on each "new modern window" (if you're spending less that that, you aren't getting a product as good as what's there), listen to @Hap_Hazzard and make sure you are fixing a problem. Those double hungs, with a small amount of work, can be made quite tight, and replacing the outside storm sashes (I think that's what I'm seeing?) (which, I agree, are a first class pain) with quality interior storm windows (I use this outfit:
Interior Storm Windows For Older Homes, Churches & Buildings
but there are others) will do the job — and last.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I'll definitely try this! I also can borrow a FLIR thermal camera that might help a bit too.
0 -
Speaking of new windows, one of my neighbors discovered that it is possible to purchase Pella windows without going through an installer. I'm not sure who he had to talk to (but it definitely wasn't the installer) or if it's possible to get Andersen or other brands this way, but if you end up needing new windows, and you're capable of doing the work yourself, look into it.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
That's awesome, I appreciate that! So the boilers the first company quote gave me were oversized looking at the BTU?
0 -
We had our 100-year-old double-hung windows professionally weatherstripped with spring bronze seals on the sides of the sashes, and silicone rubber bulb seals at the top, bottom, and middle parting rail. With new sash ropes, the windows are better than new, and with conventional storm windows they seal just as well as new replacement windows.
So I am also an advocate for restoring and air sealing old windows. I can prove they seal just as well as replacement windows, because we live in a 4-unit building with two heating systems. One boiler heats the half of the house with the original, weatherstripped windows with storms. The other boiler heats the other half of the house where the owners replaced their old windows with new vinyl replacement windows. I track fuel usage of both boilers with ecobee smart thermostats, and both sides of the house use almost exactly the same amount of oil.
1 -
Thermal imaging has to be done when it's cold outside, unless I'm mistaken, and it's better at detecting radiant losses than air leaks.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Yes, and that's common, because the boiler installers don't want to take the time to do the calculations, and they don't want to be blamed for insufficient heat. So they commonly oversize by a factor of 2, even 3.
The New Yorker CG50F has a DOE output of 117,000 BTU/hr, which is about 2x what you need.
The Bradford White combi at 199,000 BTU/hr is about 3x what you need, but it can modulate, so the oversizing isn't as bad. I'm not a boiler expert, so don't take my word for it, but I think most pros here will advise against installing a combi boiler.
One other factor to be aware of. Boiler sizing is typically done for a 99% low temperature condition, meaning 99% of the time, the temperature will be higher than what you're sizing for. But 1% of the time, the weather will be colder. And in extraordinary conditions, like a polar vortex day with high winds, the high winds can add 40% to your heat loss. We had a brutal polar vortex 3-day event here in Boston in Feb 2023 (?) during which I monitored our boiler run times. Normally our building has a design heat loss of about 100,000 BTU/hr at zero degrees outside air temp. During that polar vortex, with near-zero temps and high winds, we lost almost 140,000 BTU/hr. That was a one-in-50-year record cold.
So, you need to be aware that, 99% of the time, sizing your boiler per my math above will match or exceed your house's loss at design temps, which is 11 degrees F for your area. But there will be some rare extraordinary cold events which will temporarily exceed the demands on a boiler sized per the above method.
0 -
I'll look into this, the whole first floor has all original windows and if we can keep them we would love that!
0 -
Check the Philly area for old window restoration specialists. We have three or four such specialists in the Boston area. Make sure to ask if they use spring bronze air seals. If they don't, don't bother with them. The pros who do it right use spring bronze; the pretenders don't even know what spring bronze is.
This is expensive, possibly as expensive as cheap replacement windows, but after you do this, your original windows will last another 100 years, while cheap vinyl replacement windows will fail in 20 years.
Here's a video from one of the pros who does it right with spring bronze side seals and silicone rubber bulb seals at top, middle and bottom. You want someone who uses these materials, installed properly like this guy.
https://www.youtube.com/watch?v=TYAYnp4M_lM
0 -
are those aluminum storm windows on there?
0 -
Back on boiler sizing, I would look at the Weil-McLain CGa-3 or CGa-4.
https://www.weil-mclain.com/products/cga-gas-boiler-series-3
The CGa-3 is rated at 67,000 BTU/hr input, 48,000 BTU/hr net output. That would probably cover you for 99+% of the time, but on a rare design day with high winds, it will struggle to keep up.
The CGa-4 is rated at 100,000 BTU/hr input, 73,000 BTU/hr net output. 99.95% of the time that will be overkill, but on the once-in-50-years polar vortex with high winds, it will have the extra margin for that.
So a CGa-4 with an indirect hot water tank might be a good setup for you, or a CGa-3 if you don't mind the rare day when the house loses a few degrees because the boiler can't keep up with the high winds at single-digit temps.
0 -
I know this is a thing, but i'm not sure with my boiler being so old if this would be an option.
0 -
Yes they are aluminum storm windows
0 -
then replacing the old windows probably won’t have a return on investment.
search Blower Door Test in your area.
I recommend getting at least 2 done for comparison.0 -
The boiler cycling when at design conditions says oversized. The on time off time can give you a good idea by how much.
0 -
Thank you again! Huge help and everyone on this forum. I've gotten so much feedback. I'll look into these units, since they aren't high efficiency, I'll have to get a stainless-steel chimney liner installed unfortunately.
0 -
You can certainly go the high-efficiency modulating-condensing route. But you should be aware of the tradeoffs. You will get somewhat higher efficiency, but only if your mod-con is piped and programmed correctly with outdoor reset to run as low water temps as possible in order for the boiler to condense. And mod-cons are less reliable, fail more often, and will probably need replacing sooner than a plain cast iron boiler.
You can read hundreds of threads here about the potential pitfalls of mod-con boilers here and decide for yourself whether they're worth the additional cost and headache of maybe 10-20% better efficiency, assuming they're set up correctly, which they often are not.
After reading all the tales of mod-con woe from homeowners, my own personal conclusion is that I'd rather lose the maybe 15% efficiency gain in exchange for a plain, dumb cast iron boiler that will last maybe 30-40 years with minimal maintenance.
Or an Energy Kinetics non-condensing which will be higher efficiency than a conventional cast iron boiler, but doesn't have the headaches that come with condensing.
That's just my 2 cents. You'll have to make your own judgment on the tradeoffs. Just keep in mind that with your envelope upgrades, most of the time your heat loss will be under 40,000 BTU/hr, so you're not going to be using a lot of gas anyway, and the less you need, the less you save from higher efficiency, so you get diminishing returns.
0 -
-
Yes, gas should be cheap in PA, so you won't save much on a 10% efficiency gain.
0 -
My boiler is 42 years old and still going strong. They don't make 'em like they used to.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Oil boiler? Mine has to be close to 40 years old. It looks pretty rough at the bottom.
0 -
0
-
No, mine's natural gas. At least have someone take a look at it. I thought my boiler was on its last legs the first time I blew down the LWCO and saw all the rust and junk that came out. That was 25 years ago.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
OK, great, now figure 10-20% savings at most from a mod-con, so $130-$260/year from a mod-con, assuming it's plumber and programmed correctly, which often they aren't.
No worth the hassle, IMO.
0 -
Based on what you have said so far, it looks like:
- you have your forever house;
- you’re leaning towards natural gas (over the existing fuel oil);
- you are committed to significantly reducing the energy load of your house;
- your existing boiler is keeping you comfortable, but the cost of operating the boiler with fuel oil is what is causing the pain;
- you have concerns about the existing boiler’s longevity.
I strongly suggest that you consider moving forward with scheduling the energy audit, as well as establishing a relationship with an HVAC contractor whom you can trust and work with over the years.
I have learned (as a tradesman & as a homeowner) that the relationship with and the quality of the installing contractor is second in importance only to having clear goals to communicate to your contractor. This is especially true with the goals that relate to the HVAC system(s) for your forever house.
The energy audit should be a powerful tool for both you and your HVAC contractor. Choose the auditor well, leave plenty of time for him\her to perform the audit, and be sure to tell them what it is that you want to get from the audit.Swinging hammers and fitting pipe…bringing the dream to life
0 -
Regarding NG, check the cost of NG in your town including all costs. I have oil at home and only pay for the oil I use - at my commercial building I have NG and I pay $800 a year for "delivery" charges I have to pay even though I shut the boiler down from April through September… That $800 deliver charge alone is more than 1/3 my home oil usage (2800sq) for heat and hot water for the year.
I won't compare heating costs because even though the building is smaller than my home, it's comparing apples to bricks construction-wise.
0 -
@Ghynes440 Watch the fine print on that calculator - those are July prices conveniently, which are misleading. Obviously Peco built the calculator and know what they charge, so they consciously picked a summer month with outdated delivery costs instead of keeping it updated. Current peco rates are, at least from an online search is:
$15.70/month
+ $.68/ccf delivery
+$.59/ccf commodity cost.
+ whatever other fees they tack on. So they’ve misstated the savings by several hundred.
The issue with a gas utility (and I have a gas connection, no oil) is that they keep raising the delivery costs. You can have dirt cheap gas molecules but they’ll get ya with the shipping and handling. So conversion might look like a ten year payback, but as those flat fees are tacked in future years on it becomes a trap.
1 -
maybe have the chimney inspected also, before you decide on the type of boiler.
A PP sleeve could easily drop down that chimney, for a mod con. If it is no longer suitable or safe for venting.
Take a look here for programs that may help.
https://programs.dsireusa.org/system/program/pa
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 953 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements