White plume of smoke
joe143
joe143 Member Posts: 25
Hi - Just changed the oil pump on beckett burner and now everything it's on I'm getting a lot white smoke or steam from chimney. Had a very slow stream and it just stopped pumping so I replaced it.
    Jamie Hall Member Posts: 26,847
    Is this a steam system? Or hot water? Either way — a nice puffy plume of white smoke from the chimney is not a good sign.
    Do you also need to add water to the boiler?
    joe143
    EBEBRATT-Ed Member Posts: 19,621
    White smoke from an oil burner usually means a fire that is way too lean….too much air in relation to the oil. Did you disturb the air adjustment while changing the pump?
    Also the replacement pump may not be set to the correct oil pressure.
    In either case you need a tech with a combustion test kit to adjust.
    SuperTechbburd
    EdTheHeaterMan Member Posts: 11,586
    If your boiler is Catholic, you may have just elected a new Pope
    CLambIntplm.delcrossvtechforlife
    ethicalpaul Member Posts: 8,176
    Too soon Ed!!
    Intplm.delcrossvjoe143