Balance issues in a single-pipe system
SpencerB
SpencerB Member Posts: 13
Hi,
I moved into a house with a brand new steam boiler 2 years ago and my brother promptly lent me the Lost Art of Steam Heating, which sat on a shelf until recently. In the interim, I'd been told by enough contractors that I should insulate my basement pipes, so I came to this forum and got some excellent advice. The partial insulation I did has made the basement cooler, but high usage and bad distribution are still a problem. So I dusted off the old book and was surprised to see it sending me right back here! Glad there's a close tie between all these smart people.
Anyway, I've done my best to come up to speed, but I am just a dumb homeowner so bear with me. My main complaint is that the 2nd floor rads don't put off enough heat. The thermostat is on the 1st floor, so when it gets to 70, the 2nd floor is only at 63. I'm also getting some noises when the system is running, which we don't really care about, but is probably indicative of an issue. The boiler seems to fire every 20-30 mins or so for about 4.5 mins, but obviously this varies with the outdoor temperature.
It's a single-pipe system and as best I can tell, it's been piped correctly — see pictures. There are two levels to the floor in the basement and the boiler is on the lower part. The lowest part of the main is in the other section, so to get the "A" dimension, I'm measuring from the ceiling. The waterline in the gauge glass is 55" below the ceiling and the lowest main is 13-16" below the ceiling (not sure whether to use the top, center or bottom of the pipe). The mains and risers are 2" pipe; the header is 2.5" and the returns are smaller though I haven't measured.
There are 4 rads on the first floor, 4 on the 2nd and 1 in the attic (currently off because we don't use it). They are tube-style rads with 4 tubes. They're all about 22" high from the floor and most are about 8.75" deep, with the bathroom one being about 5.5". Using some charts, I calc an EDR of about 311.
The vents on the rads are all Gorton Cs, with the exception of two on the 2nd floor that use a heat-timer vari-valve that looks like this (https://www.amazon.com/dp/B009ATMA2I?psc=1&language=en_US). These two are set to be all the way open, though there's really no difference in the heat between any of the rooms on the 2nd floor; they're all cold.
So, is there anything I can do here? What else would help diagnose the issue?
Thanks again as always to this impressive community.
  • ScottSecor
    ScottSecor Member Posts: 950
    I'm short on time right now. I'm very simple terms, reduce the size of the vents on the first floor radiators to #5, #4 for room with stat. Use #6 vents for upstairs. Make sure your steam mains are well vented. This would be where I suggest you start.
    ethicalpaulclammy
    EBEBRATT-Ed Member Posts: 17,486
    You want to vent the mains as fast as possible. Then vent the radiation based on how it heats. If you have a large vent in the room with the thermostat that could shut the boiler off before the upper floor are heated.
    But the first thing is to start with the main vents. The main vent in your last picture looks like an antique so that may be the place to start. Measure the length of your two mains and get the pipe size for each and someone can help size the main vents.
    You have 2 mains so you should have two main vents so you need to find the other one
    delcrossv
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,723
    Before looking at the venting, you must ascertain that the radiators are properly sized to the rooms.
    You don't have sufficient heat in the second floor. The heat is turned off in the attic. It's quite plausible that the second floor radiators are sized with the assumption that the third floor is heated. With an unheated attic,the second floor ceilings now face unconditioned space. So your second floor radiators may be grossly undersized (think 30%) for their current use. Try turning the radiator back on in the attic.
    A room-by-room heat loss calculation vs. radiation capacity should be done.
    Now if those second floor radiators are simply not heating, then the venting recommendations above are certainly a place to begin. In either case, good quality main vents will speed up heat distribution.
    ethicalpaul Member Posts: 7,460
    edited January 30
    ^^ this is what I would say. Your radiator vents are too big generally. The steam is going to go where it wants to go unless you force it to go where you want it to go via vent sizing.
    Additionally, you can forget about all those dimensions you listed. They don't matter at all in a 1-pipe system.
    PS: good job sizing your radiation. Just out of sick curiosity, what is the "Sq. Ft. of Steam" number printed on the boiler?
    PPS: replace this ancient main vent:
    delcrossv
  • SpencerB
    edited January 30
    Thanks to all, as always, for the rapid and insightful feedback. I'm away from home for the day, but tonight I'll measure the mains and try to find the second main vent if there is one. I will look into replacing that old main vent and post the sqft of steam number, too. Long Beach Ed - the 2nd floor rads are heating, just not enough. The one in the attic is small, ancient, and isolated to the front of the house, so I'm not sure how much of an impact it has, even when turned on. I'll give it a try though.
    Overall, it sounds like my best approach is to start with the main vents, then move onto re-sizing the ones on the rads if needed. Right?
    Yes. Resizing the ones on the rads is going to be needed IMO. You have a bunch of wide open holes on your radiators, the steam is going where it wants.
  • SpencerB
    A quick follow-up as I start to think ahead towards replacing some vents. Does a variable vent like the Hoffman 1A make any sense? Otherwise, are there brands I should favor or avoid? supplyhouse.com seems to have decent prices on a wide selection
    Yes supplyhouse is good. I don't really care for Hoffman, they are expensive and the adjuster is pretty jank. I like Gorton just fine, but for figuring out your venting, nothing can beat the low cost of Maid O Mist which allow you to swap their sizing orifices without tools so you can get the sizes on the radiators that work for you.
    After that, if you hate them for whatever reason you can get the correct size Gortons to replace them.
  • SpencerB
    Ok, so apologies, I didn't check my vents closely enough! Some aren't even Gortons, let alone all Cs. Below is a full chart of what I'm dealing with. A couple other questions and notes:
    • I confirmed that the other main has the same type of old vent. I'm happy to replace both, but is it a safe DIY job? I mean I'll be sure to have the system fully off, but I'm a little leery of just wrenching these things in considering the pressure they need to withstand. Also, any recommendations on a model?
    • Looking at the chart, it does appear as though someone did try to size this out, just with what they had on hand. Regardless, it does still sound like I want a 4 for the living room and 5s for the other first floor rooms, right?
    • The nursery vent being damaged concerns me, but with all these new spare vents, I'm sure I can swap it out with no problem. But could that be part of the reason it's the coldest room?
    • To work on the question of whether or not the radiators were sized correctly, I added each room's square footage and its ratio to EDR. Can I draw any meaningful conclusions from that? I'm not very likely to swap out any radiators but maybe a skewed ratio informs a vent adjustment?
    Thanks again as always!
    Floor
    Main
    Room
    Room sqft
    Typical Temp
    Note
    Vent Type
    Radiator Type
    EDR
    EDR to Sqft ratio
    1
    Right
    Kitchen
    90
    69.4
    Fine
    Gorton 6
    Tubular - Four Tube
    30
    0.333
    1
    Right
    DR
    162.5
    67.3
    Fine
    Gorton D
    Tubular - Four Tube
    39
    0.240
    1
    Left
    LR
    186
    69.6
    Fine
    Gorton 6
    Tubular - Four Tube
    48
    0.258
    1
    Left
    Plant Room
    71.5
    63.9
    Very cold - hollow floor
    Maid-o-Mist C
    Tubular - Four Tube
    42
    0.587
    2
    Left
    Bath
    70.125
    63.5
    Cold
    Gorton C
    Tubular - Four Tube
    32
    0.456
    2
    Left
    Master BR
    196
    64.4
    Cold
    Vari-valve open
    Tubular - Four Tube
    45
    0.230
    2
    Right
    Nursery
    90
    62.3
    Very cold
    Gorton C - damaged
    Tubular - Four Tube
    30
    0.333
    2
    Right
    Guest BR
    127.5
    65.2
    Cold
    Vari-valve open
    Tubular - Four Tube
    33
    0.259
    3
    Right
    Attic
    huge
    Who cares
    Gorton D
    Gurney Columnar 3-column
    15
    314
  • LRCCBJ
    LRCCBJ Member Posts: 973
    Put Gorton 4's on the kitchen, dining room, and living room. See what you get. Post the chart again after install.
    And be sure both mains have at least a Gorton 2 main vent.
  • delcrossv
    delcrossv Member Posts: 2,059
    Agree with @ScottSecor and @ethicalpaul . You really need to reduce your 1st floor venting.
    Replacing your main vents is straightforward. Penetraiting oil and a large wrench is indicated.
    You mean 2 psi?
    PeteA
  • SpencerB
    edited February 4
    @ethicalpaul All I know is that I don't want any steam blasting out because I'm a dunce. But yeah, penetrating oil and the right wrench. Also, sorry, I wasn't able to find a "sqft of steam" figure on the boiler or its literature.
    So I was building my cart and disappointed to see that the Gorton #2s are $150/ea. Look, I know you'll all hate me for being cheap, but $300 is a real outlay here, plus they're sold out. I don't plan to be in this house long enough to see a real ROI. I can see from the 'Balancing Steam Systems' capacity chart that the current Hoffman #16s are woefully undersized, but could I get away with at least one Gorton #1? One main is 11 ft and the other is 31ft.
    My plan is to buy four Maid-o-Mist vents (two 4s and two 5s) for the downstairs as advised, then one Gorton #1 for the 11ft main and one B&J Big Mouth for the 31 footer.
    Decent plan?
    I would just try a Gorton #1 in each location. Or Maid O Mist #1 for more savings.
    They can vent a lot of air and the benefit from a #2 might be measured in seconds of burn time.
    There’s no loss of heat or efficiency. Worst case is Steam might heading to some radiators a little sooner than others.
    Vent replacement is the first level of steam home ownership. You got this
    Long Beach Ed
  • SpencerB
    Good enough for me! $100 saved. Thanks for the vote of confidence. Forward with wrench in hand!
    ethicalpaulLong Beach Ed
    edited February 4
    Send us a picture of your boiler rating plate, we should be able to tell how large it is if you're interested.
    If you do find that the longer main is filling noticeably slower than the short one, you can always get a #2 when you are able to for it.
  • SpencerB
    Took me a while to get the one main vent on the longer right main replaced with the Gorton 1 — stickiness meant that PB blaster and a new bushing was required. Boiler is 130 MBH or 542 sqft and below is the latest temp table. This one's a bit optimistic as it was taken in the late morning with the sun coming in, but in general results have been better! I'll still try to get the vent on the shorter left main replaced, it's just in an awkward spot behind the washing machine. My only real complaint now is some increased leaking from the supply valves on a couple of the rads. Any ideas here? It's not the worst to empty a deli container every couple days but still…
    Floor
    Main
    Room
    Room sqft
    Old Temp
    New Temp
    Note
    Old Vent
    New Vent
    EDR
    EDR to Sqft ratio
    1
    Right
    Kitchen
    90
    69.4
    69.6
    Fine
    Gorton 6
    Maid-o-Mist 5
    30
    0.333
    1
    Right
    DR
    162.5
    67.3
    67.6
    Fine
    Gorton D
    Maid-o-Mist 4
    39
    0.240
    1
    Left
    LR
    186
    69.6
    68.9
    Fine
    Gorton 6
    Maid-o-Mist 4
    48
    0.258
    1
    Left
    Plant Room
    71.5
    63.9
    71
    Very cold - hollow floor - but sunny!!
    Maid-o-Mist C
    Maid-o-Mist 5
    42
    0.587
    2
    Left
    Bath
    70.125
    63.5
    66.2
    Cold
    Gorton C
    Gorton C
    32
    0.456
    2
    Left
    Master BR
    196
    64.4
    67.3
    Cold
    Vari-valve open
    Vari-valve open
    45
    0.230
    2
    Right
    Nursery
    90
    62.3
    65.5
    Very cold
    Gorton C - damaged
    Gorton C - damaged
    30
    0.333
    2
    Right
    Guest BR
    127.5
    65.2
    68.2
    Cold
    Vari-valve open
    Vari-valve open
    33
    0.259
    3
    Right
    Attic
    huge
    Who cares
    Gorton D
    Gorton D
    15
    314
  • SteamingatMohawk
    SteamingatMohawk Member Posts: 1,047
    Shouldn't the Varivalves be slowed down?
  • delcrossv
    edited February 18
    @SpencerB
    With boiler OFF:
    Remove handle knob, remove packing nut (smaller nut round valve stem), using a pick, remove old packing, wrap new packing (available at hardware store) around valve stem and push down into groove where old packing was, gently tighten packing nut, replace knob.
    Visual aid:
  • jesmed1
    jesmed1 Member Posts: 1,225
    Another thing you can do to help balance your heat is to upgrade to an ecobee smart thermostat with a remote wireless sensor. I have two heating systems in a 4-unit condo building in the Boston area. Each heating system serves two units, one upstairs and one downstairs.
    We used to have just one thermostat per heating system, each in the first floor unit. And the upstairs units had no temperature controls/sensors. This was not good for the upstairs unit owners.
    So last year I upgraded to ecobee 3 lite thermostats in the first floor units, with a remote sensor in each upstairs unit. The thermostat averages the sense temperatures in the first and second floor units, and this does a much better job of maintaining comfortable temps for both residents.
    I don't have any experience with steam (our boilers are hot water), but a number of steam users here have said that their ecobees work well on their steam systems. You do need to make sure you configure the thermostat appropriately for correct differential (swing) setting, etc.
    Also be aware that you may need a separate 24V power source. I have our ecobees wired to a dedicated 24V transformer in the basement, with power going to the ecobees through separate 2-conductor wires.
  • SpencerB
    @SteamingatMohawk - yes, I could, I'll play with them. Thanks!
    @delcrossv - Awesome! Had no idea it could be so straightforward. Thank you.
    @jesmed1 - This sounds like a great idea, too. We may have some electrical work coming up so I'll check into this then to see what would be involved. Thanks.
  • SteamingatMohawk
    If there is a temperature difference between multiple averaging thermostats, how does that cause the system to heat all areas to the same temperature. If the difference is 2F that's a 1F difference from the average, which is not all that much. If there is a 5F difference,its 2.5F which is "feel-able" for lack of a better word.
    Jamie Hall Member Posts: 25,835
    It doesn't. Much too sensible a comment, @SteamingatMohawk .
    Got a temperature imbalance? don't shoot the messenger. Fix it.
    If you truly don't care about your attic, then turn the vent upside down or tape over the vent hole and disable that radiator.
    If your rooms are cold with a vari valve open or a C on it, then there is something else going on. Steam isn't getting where it should. There could be a sagging supply pipe that has water trapped that is blocking the steam.
  • SteamingatMohawk
    Thanks Jamie, but I was hoping for an explanation of how the radiators/vents in the two rooms would manage the available steam to equalize the temperatures. Apparently as you said, it won't….so then why would anyone try to average?
    When I bought my rental in 1989 I had 3 thermostats in parallel. The fourth apparently was too difficult to run the wiring to, so some previous owner didn't bother. When any one thermostat called for heat the whole house got it.
    When I replaced the boiler, the heating guy said I couldn't continue to do it, so we picked one room and learned the hard way how to manage the heat. My other posts talk about how I eventually did that with lots of help from the guys at HH. I am forever grateful.
    Personally, I didn't see any problem with parallel thermostats, because the coldest one would call for heat and the others would not, so I didn't think there was any kind of electrical issue. No current would flow with all open and only one would call, so what's the difference?
    Electrically there's no problem with thermostats in parallel. From a control standpoint… maybe. If the various spaces heat up or cool off at different rates, you could potentially get a situation where one space calls for heat and starts to warm up nicely, but another is much slower. The first place gets nice and toasty and the thermostat says stop, but the other space is still chilly and the system keeps on going until that space gets nice and toasty. By which time the first space is a sauna…
    Or the two space cool differently, and the first space gets chilly, system fires up, place warms up some, system shuts off — and about that time the other space decides its gotten chilly or somesuch, and it fires the system up…
  • SteamingatMohawk
    Nobody ever complained, but that's not a guaranteed way of knowing.
    Possibly as long as the coldest room was getting comfy the others which are already warmer didn't want to complain about being too hot or something other "phenomenon".
  • SpencerB
    @ethicalpaul I should have updated the notes and not just the temps. For the most part, we're happy w/the way things are now, I just wanted to post the updated stats for those that might have the same issue and want to see the results. Sometimes folks ask things here, get an answer and don't come back to say how it went. I didn't want to be one of those people. Anyway, thanks again to all!
    ethicalpaultechforlife