Expansion Tank Orientation
I couldn't reach the local page on this so I've got to bother you guys about it.
It's always amused me when I walk into a boiler room and see an Extrol tank with the lettering upside down. But now I'm a little humbled because in this boiler room the Extrol tank confuses me. I have not been there and don 't intend on going there because it's in Lexington Kentucky and I'm in Colorado. But the building superintendent is a buddy and asked me about some symptoms and sent pictures.
It's a 750Kbtu boiler serving two huge fan coils that are also right there in the mechanical room. They are the only load. A very large air seperator with a B&G vent on top and a tap for a nearby (and physically higher) ASME rated Extrol tank is on the suction side of the pump. Each fan coil has its own air vent (Hoffman) on the return side of its' piping. There is no automatic feed valve.
The original complaint was that the boiler needed continual refilling and the gauge responded instantly to his doing so. I told him his expansion tank was water logged and he had a leak somewhere. He found the leak in a failed Hoffman air vent associated with one of the fan coils and replaced the air vent. During that process he checked the air charge on the tank and it was 1 psi. He charged it to 15 psi but on further examination discovered there was no water at all on the water side of the bladder. In other words, both sides of the bladder had air.
The tank is oblong but is mounted vertically near the ceiling.. The air valve is on the high end at the ceiling and the boiler connection is on the low end. There is no mounting "base" or "stand" on either end. The writing on the tank is oriented along the long axis and so one has to turn ones' head sidewise to read it. I told him the tank was mounted upside down and too high and that he needed to move it to floor level, turn it so the air valve was on the bottom and the boiler connection was on top and reconnect it to the boiler. allowing boiler fluid to enter the tank.
But then I got to thinking and told him to hold off until I talked to you guys ……
What bothers me is the lettering on the tank.
If I were in the business of fabricating tanks I would definitely put my name on it so it could be read without standing on ones head or turning ones head sidewise. BUT IF THE TANK IS OBLONG, AND THE WATER INLET IS CENTERED ON THE TANK, HOW DOES THE WATER SIDE OF THE BLADDER GET FULLY PURGED OF AIR? I mean, during the filling process air WILL be trapped above the level of the water inlet of the tank on the wrong side of the bladder!
I'll quit now and let you guys think this over. Sorry to be so wordy but I'm trying to be precise and give you an accurate picture. (And the picture below should help)
What @Jamie said.
Although the orientation may not be right the tank will work no matter where it is mounted.
Sorry, I'm still not getting it.
I. Both sides of the bladder were bone dry indicating there was a HUGE volumn of air in the tank.
2. When the operator attempted to put water in the system the gauge wanted to immediately peg, implying there was a HUGE vollumn of water in the tank. (WATER LOGGED Tank.)
3. These symptoms are contradictory.
4. If you can orient it any way you want and you orient it the way shown in the attachment, How is the water supposed to get into the tank? It's pushing against the air that is on the wrong side of the bladder, right? Where is that air going to go? The water the operator introduced to the system illustrates my point. It DID NOT go into the tank.
4. Why have a bladder at all if you're going to have air on both sides of it anyway?
5 Anyway you look at it, an upside down bladder tank will collect air on the wrong side of the bladder, defeating its intended purpose. (See picture attached.)
6. Yes! I understand that a gas compresses but this fact alone does not explain what was observed.
A bit of confusion here. You have supplied two photographs and they contain a total of THREE different tanks. Please indicate WHICH tank in the photo you are having trouble with. Three tanks: 1. gray, 2. red. 3. blue. If the tank is entirely empty of water, that is not right. The side of the tank that has the pipe connection should have water in it. Your system pressure should be relatively low. Under 20 psi. The 'other' side of the tank should be hollow—when tapped or rapped on. You can only test the air pressure with the tank isolated from the system. An expansion tank can be mounted in any orientation. The writing on the tank orientation is meaningless.
The blue tank —not an "Extrol" tank (#PFX T121), appears to be on the supply side of a domestic gas heated water heater. It is NOT on the heatring system. The tank pressure on that system will should be higher—28 or 38 psi. i.e. 2 psi. below the "cut-in" setting on the pump switch.
When you take a pressure reading on the air side there should be NO pressure on the water side influencing the the reading. This is probably why the gauge when taking said reading "pegged".
Simply put, and as an example, the tank must be charged to the system water side operating pressure. In a residential, and on many commercial settings, the setting for air is commonly 12-15 psi. The water side should also be set at the same pressure through a pressure reducing valve.
I have seen many tanks installed with many different orientations. Up, down, angled, offset etc. When the tank is properly charged with air to the corresponding systems working pressure they work correctly.
There is nothing wrong with that mounting orientation. How did he determine that the water side was dry? There is no drain or test port there to check. If it's not taking water without spiking the pressure, something is closed, the bladder is compromised, or the charge is wrong. The water side needs to be dropped to zero before fiddling with the air side. Once that water side is open (maybe disassemble the union after the valve is closed), fill the air side to whatever the desired water side pressure will be. Use two different low pressure gauges, not a regular automotive tire gauge. When that's set, reassemble the water side and fill to desired pressure. All done, unless the bladder is compromised.
The precharge needs to be checked once a year or so, the schrader usually leaks a little and i'm not sure the bladder is completely non-permeable to gasses, it leaks out over time.
Any air in the water side of the tank should get removed by your air elimination if you have good air elimination. Water flows in and out as the system heats and cools and when the system is cold, if the precharge is correct, the bladder should be almost completely collapsed toward the water side. If the air elimination is correct then this flow of water in and out should scavenge any remaining air.
I think the way it is installed it will collect air in the system over time similar to a compression tank. The issue is that since the bladder won't let this air rise to the top, each the system system cools down and the pressure drops, this air is pushed back into the heating loop. I guess over time the air eliminator will remove it but will take many cycles.
Yikes!
I always get down in the dumps when I fail to explain a situation succinctly. Paragraph 3 of my original post was my best effort at describing the piping and I was sure the photo cinched it. The red tank is the expansion tank, the gray tank is the air separator and I wish I'd never mentioned the blue tank because it just created a distraction. I just thought it was a good example of how air could get on the wrong side of a bladder. Oh well.
I do appreciate all the input but frankly I don't find any of it really speaks to the issue. I'll just put my tail between my legs and walk off stage here but will offer one final question. If it doesn't matter if air is on the wrong side of the bladder then why do you all suppose anyone ever invented a bladder tank? My understanding has always been that it was because someone thought it would be a good thing to keep the water and the air from coming into contact with each other. What I get from you all is that you don't agree and, hot rod, that the manufacturers don't seem to agree either. Go figure.
As for me, I'm going to keep on piping bladder tanks so that air is not encouraged to enter the water side.
ccstelmo
Whether air or water is on the water side of the x-tank is of no issue. The important thing is the air side that allows the water in the system to expand and contract when properly charged.
I've seen x-tank instructions that say that they should only be mounted vertically and I've called manufacturers that have said that this is for support considerations only. When properly supported, vertical mounting is considered fine.
Two btu per sq ft for degree difference for a slab1 -
the air in the tank is compressible, so as the water expands, pressure increases, it will push into the space regardless of the position of the tank.
The manufacturer doesn’t know which position it will be mounted when affixing the labelNo reason the tank needs to be above the boiler, base mount styles are usually on the floor next to the boiler.
There have been instances where a new tank has the diaphragm stuck against the nipple and will not accept water. Increase the fill pressure until you hear it pop, or some suggest pushing a wooden dowel against the epfm.
Living the hydronic dream1 -
If you're concerned about being succinct, perhaps answering the questions you've been asked would be a step in the right direction. We're all trying to help you, but that's impossible when you don't provide the necessary information which is requested of you. Again, how did he determine that the water side was dry? Was the described pressure adjustment process followed?
2 -
Yikes Again!
I believe that all three of the installation images provided by Alan Forbes are 3/4 filled with air and 1/4 filled with water. I can't imagine any other scenario. I also believe this tank installation scenario defeats the holy grail sought by those who believe the correct way to handle air in a closed loop system is to expel it from the system by mechanical means.
Speaking to Ground Up, I acknowledge being annoyed that my original statement about the tank being completely empty of water was not taken at face value and apologize for not giving your question more attention. To answer your question though, it was determined that the tank had no water in it when the union just upstream of the tank was broken and no water came out. That having been determined, the operator decided that tank filling protocol was irrelevant until the cause of the empty tank and the pegging pressure gauge was determined. That's when he called me. Prompted by your message here, however, I have advised the operator to disconnect the union again, crack the valve next to it to see if boiler fluid is available there, and to run a rod or something into the tank to rule out the tank inlet being filled with crud (and perhaps discover that there is in fact water in the tank). The manner in which it is piped would promote rust, crud, and corruption at that location. This scenario would explain all the symptoms described by the operator because the air cushion would in fact be isolated from the system in general due to a blockage at the inlet to the tank.
When I was in the business I never used bladder tanks because they did not fit into my Air Control piping technique. I used plain steel tanks, placing them directly above the boiler and piped from a tap on the top of the boiler. I viewed the boiler as a "wide spot in the road" where air WANTED to come out of solution. I modified the supply nipple (also on top of the boiler) with a "dip tube" so that the supply fluid was drawn from just below the top of the boiler casting. This left a small cavity at the top of the casting where air would collect and eventually find the inlet to the air tank. I always put a drip leg at the inlet to the tank to catch the crud that invariably collects in that kind of a tank. My thinking was that oxygen, not air, was bad and that once the oxygen-containing air (21%) was captured in the plain steel tank it, the oxygen, reacted with the steel, and was converted into iron oxide, (a solid) leaving only inert, harmless nitrogen (79%) in the system.
I owe this technique to Dan Holohan who, at one of his seminars when I was comin' up, told us to "think like an air bubble".
Ground Up, I just cannot tell you how satisfying it is to stand next to a newly-fired-up boiler and listen to all that air in the system going Bloop - Bloop - Bloop into the tank. 🙂 Yes!
3 -
Pockets of air in the water side of a tank are inevitable. Regardless of its angle of install. A reason why the orientation of the tank is not critical as mentioned numerous times here, is because a properly sized tank with a air separator (preferably a Micro Bubble air separator ) will remove said air/micro bubbles as it is absorbed by the water.
@ccstelmo Clever use of the steel tanks.
The reason folks install there tanks as shown above is an example of good workmanship. Horizontal or vertical.
@Alan (California Radiant) Forbes Some beautiful pictures. Always like to see your work. Thanks for sharing.
2 -
I assume @Alan (California Radiant) Forbes has a seismic code to meet that we don't have to in Michigan that keeps you from just hanging it from a supported pipe.
I have had diaphragm tanks that were run with near zero air them for years. They would not take any air at all. Over 100 psi and nothing. My theory is that the stretched diaphragm covers the port and sticks “welds” there not letting air in or the port corrodes closed or something like that. Next one I find I’ll cut open.
To the horizontal tank point. I have lots of diaphragm tanks that are in the horizontal working great for over 15+ years.
There are tanks that have full acceptance bags in instead of diaphragms and they are vertical only, hanging best.
Teaching or figuring out the differences in tanks is harder than making a rule new guys can just follow. They can then confidently tell people tanks are wrong when they don’t really understand why. A huge number of vehement opinions on tanks can’t test or fill them properly. Poor or no maintenance leads to many early tank deaths. Open systems with closed system tanks is a thing too.
3 -
Here is the installation instructions from Zilmet. They show hydronic and potable tanks in any mounting position.
I would say there are two problems with the way the expansion tank in the first photo is installed, and the second of these applies to every tank illustrated: 1. it makes getting to the Schrader valve — where pressure needs to be checked at every maintenance — a royal pain, and 2. even though if everything is working to plan the air on the water side of a diaphragm will eventually dissolve, re-emerge and exit via the air vent valve, wouldn't it be better to have the tank water connection upward so that every time you refill the system you can easily purge all the air and regulate the pressure without the variable of air that is going to escape in its own sweet time sooner or later? Most of my work is with glycol systems that do not have automatic pressure regulating make-ups, so you can see why I want to know the air is gone from the get-go. If the expansion tank is mounted in any other orientation, we have to get the air out of it by repeatedly over-pressurizing, then dropping it as you listen for the fluid in and out of the tank until you hear the air is no longer trapped in there. Again, an unnecessary pain and not always even possible. (Note Zilmet's default position is water connection upward.)
That said, I agree with ccstelmo that, you want a drip leg to trap crud and, likewise, I do not mount the expansion tank straight into the bottom of an air eliminator because that is an excellent place to gather stuff that you do not want falling onto the bladder. I do not put faith in the manufacturers saying they don't care which way the tank is oriented. It may not be a problem for their piece of equipment, but that does not mean it is not a problem for the system.
I also have run into expansion tanks with the bladder stuck either to the water end or the air end. In some cases 100psi of air with the other end open would not unstick it. In your case it does sound like it is stuck to the water end, but I am not sure that is possible on so cylindrical a tank. And as you describe the symptoms, I suspect you are on the right path by checking to make sure the passages are open all the way to the bladder.
Sol Brother0 -
I think the tank in the original post may be a partial acceptance or full acceptance style.
So it has a bag inside. The bag or bladder can be top or bottom connected on the tank, depending on if it is a partial or full acceptance tank.
The selling features are a longer lasting tank, the fluid is in the butyl rubber "bag" and much smaller size than a compression or even diaphragm style tank.
Pics from Taco Tuesday episode.
This topic has certainly been interesting to drop in on once in a while. There is a huge variety of collective experience in our trade on the subject and I'm newly edified and impressed.
To add to the discussion a bit more, though, recently I was in search of a top-fed (fluid), base-mounted compression tank. I suspect the one that I installed there 40 years ago will soon self-destruct and want to plan ahead for that event. It turns out that Amtrol no longer makes such a tank. Imagine then, the piping arrangement I'll have to make when the time comes. I'll have to come off the boiler piping, pipe to the floor, then connect to the bottom of the tank. To those who have followed my original post on this matter, you can imagine how much I'm going to HATE that! How will the air trapped on the wrong side of the bladder in that tank EVER be expelled?
I feel like I have to apologize to some of you for not being persuaded that air doesn't linger long on the wrong side of the bladder. Forgive me, I'm an old dog and all that.
ccstelmo
what is the tank you actually have there? is it a diaphragm? full acceptance bladder? partial acceptance bladder? was the tank designed for a specific mounting orientation (might say vertical or horizontal) I've looked through the amtrol install manuals for all 3 styles the diaphragm ASME manual does not say that you can't mount it this way, but they also have specific vertical and horizontal models, the ASME bladder tanks of both variety say you must mount vertically, and not on a dead end pipe (due to air collection!), the drawings all show the tank mounted upright on these models. the residential have the following written in the install manual
"Mount tank vertically in downward position only. Ensure the piping can support the entire weight of the tank when full of water." *Locally we are required to support these anyway*
"Do not install the EXTROL on a dead-end pipe or wherever air can collect. This can cause corrosion and possible leakage."
- 167 Indoor-Air Quality