Venting a low return in the spaghetti factory.

Gateacre
Gateacre Member Posts: 47

Hey everyone. Up front, 1890s commercial property, 2 pipe steam. 2 condensate return tanks remote from the boiler room, 1 in the boiler room and a boiler feed tank. There are 2 boilers. One is abandoned in place and sits in a pit about 3 feet below the floor of the current boiler. For a time, it was maintained as a backup meaning condensate could be routed to either. This resulted in some unorthodox return plumbing that I refer to as the spaghetti factory and this sets the stage for my current situation.

There are a handful of rads on the boiler level of the building. They are served by two 3/4" returns that disappear into the concrete floor and emerge in the boiler room as a single 3/4" copper pipe (I know). It's the ability of this return to effectively vent air that I'm concerned with.

Visual aids incoming.

20250209_180946.jpg 20250209_181522.jpg 20250209_152408.jpg

So as we can see, anything (liquid or gas) needing to exit that copper pipe must pass through a permanent water seal. Will this prevent or seriously slow the venting of the rads that use this return? Being a former coal burner with no mains venting, this whole system is already slow to heat.

If I were to simply sweat in a Tee (in place of that compression coupling perhaps) and extend a few feet of pipe up, left open to the air, would it make much of a difference? I'd turn down the top of the pipe to keep anything from falling in.

Thoughts?