Cast Iron baseboard leak on strange fitting
I have an older home with cast iron baseboard. I found a leak on a strange looking fitting. Can I replace this fitting with a normal peice of 3/4 copper? What is the point of this fitting?
  • Grallert
    Grallert Member Posts: 1,026
    edited February 1
    Looks like an expansion coupling. Looks like a bad idea. Should be a simple repair with a couple of couplings and a length of pipe.
    Long Beach Ed
    hot_rod Member Posts: 26,563
    A # 75 SlantFin expansion coupling, I'll bet. They come across E bay from time to time.
    EBEBRATT-Ed Member Posts: 19,491
    Expansion joint. How long is the pipe run? I doubt they installed it for no reason
  • castiron1790
    castiron1790 Member Posts: 6
    edited February 1
    there are two of these joints both are leaking, both at the beginning of the run. The water comes up from the basement then splits at a tee fitting on the second floor, About two feet from the t fitting are these joints. Each run goes around the perimeter of separate bedrooms then back down to the basement.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,806
    How long is the pipe it's on?
  • castiron1790
    edited February 1
    Coming off the tee, The pipe is about 3 foot long before it goes into the cast iron baseboard.
    You should be able to see how much the tube is moving by the scale around the outside.
    an expansion loop can be built with 4 ells also.
    PC7060mattmia2
  • castiron1790
    so these should not be eliminated with straight pipe but replaced with new expansion fittings?
    it depends on the overall length of that section. The piping and baseboard combined.
    Without an expansion joint you may get noise, creaking, snap, crackle pop type noises as the metals heat and expand and try to grow in length.
    Long copper fin tube sections will arc up off their supports if you don’t accommodate the expansion movement.
    There are other types of expansion joints like a corrugated section. Viessmann use to have a short corrugated coupling that went between their solar hot water panels. I think it was a metric size however
    I wonder what the temperature rating is on these water heater connectors? I think it would offer enough flexibility.
  • delcrossv
    delcrossv Member Posts: 2,189
    edited February 2
    Bellows type is still available.
    Much better than a slider joint.
    https://www.flexicraft.com/Metal_Expansion_Joints/Copper_Piping_Expansion_Compensator_S/
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,002
    Hi, What temperatures is this seeing? Perhaps a loop of PEX would do the job.
    Yours, Larry
    EBEBRATT-EdIntplm.
    Larrys pex solution is probably the simple best solution if the temp is ok for the pex
    Intplm.
  • delcrossv
    edited February 2
    With more connectors? What's wrong with a compensator? 2 sweat joints and you're done.
  • Intplm.
    Intplm. Member Posts: 2,818
    A lot of good ideas. Fostapex has a top temp rating of around 200Deg. f. . If it was me I would replace the expansion joints with a length of that.
    delcrossv
    pecmsg Member Posts: 6,765
    edited February 2
    https://www.supplyhouse.com/Parker-Hannifin-475447-VAB7SS-7-8-ODF-Vibration-Absorber?utm_source=google_ad&utm_medium=Shopping_HVAC&utm_campaign=Shopping_X_HVAC_X_SSC_ClassB/C&utm_campaignid=21633352527&utm_adgroupid=164986448125&utm_targetid=aud-386072062457:pla-2352433400835&utm_product_id=475447&utm_matchtype=&utm_keyword=&utm_adtype=pla&utm_category=HVAC&gad_source=1&gbraid=0AAAAAD_WAytSArjNTgjqdKLzFSkR2w6t_&gclid=CjwKCAiAzPy8BhBoEiwAbnM9OwC63tVi6cAUJjR5aAP3f6-fq9NLqu2BfKqW4gFK59T3h3oA8o1TahoCEyMQAvD_BwE
  • delcrossv
    It will handle 180°F water.
    McMaster Carr lists it at -300 - 1200°F
    delcrossv
  • castiron1790
    thanks for the help fellas, put in a small expansion loop, no leaks and no popping sounds like before.
    mattmia2delcrossvIntplm.hot_rod
