Why not use fast vents on all radiators?
Other than the loud air sounds, are there any other downsides for not using fast vents on all radiators?
  • Intplm.
    Intplm. Member Posts: 3,005
    A fast vent in the room that has a thermostat might satisfy the heat in that room before the rest of the house is heated shutting off the boiler too soon.
    DerheatmeisterRTW
    Jamie Hall Member Posts: 27,323
    No two rooms will have the same heat requirement. There are two ways to adjust the heat provided by a radiator: with the size of the radiator itself, and with the vent. Not much one can do, easily, about the radiator size. That tends to be sort of fixed. But the vent? Ah yes. So to adjust the heating in a room to the use and taste of the occupants, one changes the vent size. Too hot? Try a slower vent. Too cool? Try a faster vent — but only after making sure that the rest of the venting in the building is more or less on.
    Or, in short, if you make all the vents the same size and all fast, you will be guaranteed uneven heat.
    RTW
  • CoachBoilermaker
    CoachBoilermaker Member Posts: 457
    I've also wondered this. Vents are relative to each other. So, using all Gorton D should give the same results as using all Gorton 4? I have Gorton D's on my 2 primary rads and slower vents on others. The vents are used to balance radiators.
  • Tezak
    Tezak Member Posts: 44
    I started off venting everything very slowly using all vent-rite #1s on my 15 radiators. They heated painfully slow. I swapped most of the vent-rites out for Maid-O-Mist adjustable vents and slowly increased the speed so that now nearly half of my radiators are using the D orifice. The rest being C or 6 and the bedrooms and bathrooms still have the vent-rites so I can turn them “off” when I want to.
    I did notice some noise when I started venting faster. I thought it was hammer but it turned out to be expansion pings. This was completely solved by putting little pieces of milk jug under the radiator feet. Now the system is basically silent.
    Just relaying my experience. I was afraid to vent fast because folks mostly discourage it but after trying it out it’s working really well for me.
    ethicalpaul Member Posts: 8,746
    I have a friend with all size D vents on every radiator. It works for her. But for most homes that would result in the steam just going wherever it wanted to, and not where you want it to, and would result in some overheated rooms and some cold rooms.
  • ChrisJ
    ChrisJ Member Posts: 17,353
    This is the fastest I could go on each radiator without causing one issue or another.
    The Macon Trvs came with a vent that seems similar to a Gorton 5.
    Tezak
  • Jells
    Jells Member Posts: 649
    I colored outside the box in trying to get my system working. I added a MoM with no orifice installed on the valve side of the rads on the top ends of the runs, essentially acting as an accessory main vent. Steam will get to the near side of the rad ASAP, then after that vent closes, fill at the rate of the regular vent. I'd have done it by adding a tee to the spud pipe as I did to one, but on the others that would shove the rads obviously out of their positions below the windows.
    delcrossvLong Beach EdTezak
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,833
    edited February 2025
    Jells, you can drill and tap the vent boss on the inlet end of the radiator and put your additional vent there, if that's not what you did… It will serve to vent the runout to the radiator.
