Checklist for cold radiator?

Friend's house.

All rads warm except one Cold radiator 2nd floor.

I removed vent and was able to blow through it.

What next? Common culprits?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • neilc
    neilc Member Posts: 3,024

    the closed valve at the other end of the rad,

    the sagged pipe in the floor /basement holding a pool of condensate that steam can't push thru,

    the abandoned, disconnected riser / lateral,

    all the other rads having too large / fast a vent on them not leaving any steam left for this rad,

    aliens,

    is this rad furthest from the boiler?

    known to beat dead horses
  • 109A_5
    109A_5 Member Posts: 2,403

    What does it do with the vent removed ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpauldelcrossv
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,415
    edited January 31

    @neilc has got most of the causes listed…. knowing the source of this questions I'm inclined to think it is ALIENS!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    delcrossv