Air to Water Heat Pumps
Some thoughts from another guru, on the John Manning method, bypassing top , straight through tank on bottom, would give you
Faster flow to the load, not passing across the tank
Less heat loss not keeping the tank hot on top
When flow is equal on both sides, the mass of the tank at the bottom is engaged
Eliminate any vertical movement in the tank
Could be the Heat Geeks could learn some from this side of the pond :) Explore all the optionsAn energy monitoring company is installing a number of systems of different brands, around the New England area and documenting them, similar to the Heat Geeks. It would be interesting to compare data. Especially that seasonal COP number?
With a ATWHP it is nice to design a buffer tank with a higher flow rate and smaller delta tee on the primary side than on the secondary side. With a delta tee of 10f on the HP you would want twice as much flow though the HP than you would through the secondary side if you design for a delta tee of 20.
There are different points of view. We all learn from each other. Different piping methods. The Heat Geeks talk about the Manning way bypassing the top and they have produced better results when bypassing the bottom.
I would be very much interested in that monitoring project you are talking about. Who is the company doing this? Is this something to do with Nyserda?
I am the walking Deadman
Hydronics Designer
Hydronics is the most comfortable and energy efficient HVAC system.0 -
If you have emitters that can modulate their output, so long as the heating load is above the minimum output of the heat pump you don't really need anything at all. You can just hook the emitters up to the heat pump, no buffer tank needed, and the heat pump should run continuously and modulate to adjust to variations in the load.
The buffer tank is for when the load is below the minimum output of the heat pump, and the heat pump has to cycle on and off. The buffer tank keeps the heat pump from short cycling by giving it a place to dump its output, as well as guaranteeing that a minimal level of flow is maintained if you're using zone valves and they all shut off. In addition, in heating mode many systems draw heat out of the buffer when defrosting, in order to defrost at a high COP without adversely affecting occupant comfort.
The goal in designing the plumbing is to achieve the necessary function of the buffer tank while avoiding negative impacts. So what kinds of unnecessary negative impacts should we worry about?
- Anything that conceals from the heat pump the actual load conditions. In particular, anything that causes it to run higher output than necessary and then cycle off rather than running continuously at a lower output.
- Anything that causes the water hitting the emitters to be not as hot as the water heaving the heat pump (or cold if we're cooling).
- Anything that adversely affects occupant comfort, ie, the ability to respond appropriately to changes in load, or the ability to dehumidify in cooling mode.
One other important observation:
In a three-pipe system, the buffer tank will tend to stabilize if the heating load and heat pump output are stable.
You've got two circulators, one on the heat pump and one on the emitters, it's basically like primary-secondary piping. The flows of the two circulators are independent of each other. If the heat pump (primary) circulator has more flow, the excess flow will go into the buffer, and the buffer will stabilize at the the sent water temperature.
If the emitter (secondary) circulator has more flow, it will be pulling water out of the buffer to supplement what comes from the heat pump. That water will be replaced at the bottom with return water from the emitters, and the buffer will stabilize at the return water temperature.
Once the buffer tank is stabilized, it doesn't really have any effect on the circuit, so long as the circuit is stable. If you were to replace the tank with a straight piece of pipe the circuit would work the same.
Surfing that UK forum, some of those engineers are going full in with controls. ODR, IDR, PID, solar irradiation sensors, sensors in every room, weather predictive input, wifi stats. My head hurts!
Will these third party control compliment or compete with the factory controls? Seems all the big names have their own control ideas.
It was mentioned that Dakin even has a buffer tank spec that you need to follow if you consider aftermarket buffers.
I wonder if those controls are more about the emitters than the heat pump. Specifically, if they have high-heat-capacity heated floors which have big excursions in temperature because they're unable to change their output quickly enough in response to changes in the heating load. The point of all the sensors is to try and predict changes in the load and get out in front of them.
One of the things I find kind of cool about my Chiltrix heat pump is that it knows nothing about what's going on inside the house. There's literally only one wire coming inside, and that's for the control panel. It knows how much water it's circulating, and it can see the temperature change between what it sends and what it gets back, and from that it can calculate the total load and adjust it's modulation. But it doesn't need to know anything about what's going on inside.
Now that I learned all this Heat Geek stuff. I have all kinds of ideas on some new piping strategies and I know how I want these different piping strategies controlled. After listening to Kaos, Hot Rod and Dc Contrarian, I have even more strategies to explore.
I think Hot Rod is coming to the same realization I am.
We need a new control company in America for all this added ATWHP knowledge we are adding to hydronic systems.
I wish we could just all get together and build our own control company. But that might be a little to ambitious.
Hydronics Designer
does yours have the ability to add an indoor sensor?
The thermal momentum of the heat distribution as well as the momentum of the structure, makes a difference in the ability to control also.
A 1200 sq ft radiant slab is around 60,000 lbs. Light, low water content panelrads with 12mm Pex tube, would be a quick responding system. Panel rads seem to be the most common heat emitters in the UK, so a much lower mass to make adjustments to. Maybe retro fits are using multiple small air handlers to offer AC options?
Gravity cast iron radiator systems compared to fin tube would be an example of the need for different control strategies over here.
I suppose that is why the one control designer wants so many inputs. Start making corrections before a weather event arrives at your door step.
I’ve been in large glass walled radiant floor homes in Colorado that run AC in the south facing rooms, heat in the north side. What a country.
The early Ecobees had predictive weather input options, I don’t hear much about that being used?
As you suggested with air source hp, you have the outdoor conditions to consider as well as well as indoor for performance and efficiency of the hp.
A great video on the three main piping methods for a ATWHP.
Direct / Open Loop
Buffer Tank / Multiple Zones
Volumizer / Adding volume to a Direct Loop System.
https://www.youtube.com/watch?v=9Ushn3MVOBw
Hydronics Designer
@John Ruhnke : "I wish we could just all get together and build our own control company. But that might be a little to ambitious."
Just to share with the other posters, I sent John a PM describing my system. Part of it is a number of custom controls. I studied electrical engineering in college and worked as a programmer for a while so I had no problem designing my own circuit boards and programming microprocessors for them.
An important thing to point out is that those modifications were 100% on the emitter side, to get my air handlers and under-floor loops to be more responsive. On the heat pump side I've done nothing, it's a stock Chiltrix heat pump, using the built-in outdoor reset and a 17-gallon three-pipe buffer tank.
@hot_rod: "I suppose that is why the one control designer wants so many inputs. Start making corrections before a weather event arrives at your door step."
I find in my house it's not so much weather events, it's the sun. When it comes out from behind a cloud the heating load drops like a rock. When the sun sets in the afternoon it goes from zero to 100% in about 15 minutes.
Maybe it's my climate, but we don't get fast-moving weather events.
The only reason that heat pump controls would have anything to do with this is if your emitters are unable to scale their output sufficiently on their own. The only variable the heat pump can control is the water temperature. If, for example, you can't get the emitters to meet the current load with the current water temperature, you need to send a signal to the heat pump to boost the water temperature. But it's simpler to manage it all with the emitters if you can.
Note that all heating systems have the issue of trying to track changes in heating load. The reason it's particularly noticeable with air-to-water is that you want to minimize temperature and maximize runtime to maximize efficiency. With air-to-water you're much better off running continuously at exactly the right water temperature than cycling on and off at a higher temperature. And all other things being equal, for the same BTU output you're better off at a lower temperature, lower delta and higher flow than at a higher temperature, higher delta and lower flow, assuming your emitters could support either.
My Tekmar controls that were installed 20 years ago are doing what Mitsubishi is talking about. ODR with Indoor Feedback.
Hydronics Designer
So in order for this to work it has to be used instead of a thermostat, because if a thermostat is doing its job indoor temperature is steady and the sensor is defeated. So you need to have either one zone for the whole building, or if you have multiple zones, one has to be designated as the "reference" zone, which doesn't have a thermostat and has the sensor instead. And you have to be sure that the reference zone truly is representative, otherwise the other zones may have trouble maintaining comfort.
My Tekmar Zone panels in my house automatically search for that reference zone by measuring each zones cycle length and operating the odr temp off of the zone with the longest cycle length. My thermostats are really all indoor sensors.
Hydronics Designer
The issue, according to the UK folks at that site is the aftermarket controls don't always match up with the factory controls so well.
My Viessmann VitoCal has ODR and indoor/ outdoor feed back via the multiple sensors. Really all I would need for a zoned system should be TRVs or ZV with a relay board.
As I've mentioned a few times in this thread, I believe that a buffer tank is only necessary when the heat pump is cycling. I'll add the observation that any method of adjusting the water temperature to meet the load will work better the less water capacity the system has. Another thing I've been thinking about doing is creating logic to figure out whether the heat pump is cycling, and use zone valves to cut out the buffer tank otherwise and run direct to load.
This fits in nicely with the idea of trying to tune the temperature setting of the heat pump, because both ideas are about assessing the load.
So let me offer this method for how the controller would work:
- Assess each zone. If there isn't at least one zone at 100% capacity, drop the water temperature until there is. If any zone can't meet the setpoint, raise the water temperature until it can.
- If the total output of all the zones isn't more than the minimum modulation of the heat pump, open the buffer tank. If it is, close it.
- If the flow through all the zones is less than the minimum flow through the heat pump, open the buffer tank.
The first one is pretty easy. The third one is straightforward. The second is a little trickier because the it's a moving target. But you'll be able to see it because the water temperature won't be steady, it will start creeping up.
For prosperity in case anybody makes it this far down into discussion. 80% of this thread was talking about tweaks and changes that make maybe a couple percentage points difference on a properly designed and set up system. Like with anything, there are also many ways of messing up the install, but it is also not that hard to get it right.
The two main configurations that will always work are the multi port buffer tank and direct to load with volumizer and differential bypass. The good news is that both of these configuration also work great with a modcon.
Air to water heat pumps are not hard or magical. They also don't need a Phd in controls to set up. A couple of rules of thumb, a bit of hand calc and a good dose of RTFM and it just works. About the only setup is getting a decent outdoor reset curve into the unit and making sure your flow rates are correct.
2 -
Hey, if it's worth doing, it's worth overdoing.
I'm with @Kaos, if you want a simple system that works, go with outdoor reset and a 3-pipe buffer. Focus on the controls of the emitters to ensure comfort. Skip the boiler backup and go with a heat pump water heater for DHW.
The point of being in the Heat Geek club is that they have done all the hard work for us. Through monitoring they know what works and what doesn't work to increase COP. They have already modified designs from what they learned. There is more work in the design phase to get things right. If you do that you can eliminate a lot of pumps and the buffer tank. The installation part is actually simpler.
When you modify the efficiency of a boiler system the gains are limited by the top efficiency of the boiler which is 100%. In a ATWHP built hydronic system the efficiency improvements made can be 8 times greater. I know Heat Geaks that have an efficiency of 800% (COP 8). This is documented by monitoring. That means any tiny improvement made to efficiency has an effect of 800% more savings of energy bills or 800% less CO2 than is possible out of a boiler system. All these tiny little improvements if made together can really add up to huge SCOP's!!!! As shown with the results that are measured in the field by monitoring equipment. Remember a graduate of the Heat Geek training has an average of 4.19 SCOP. Nothing coming out of America is even coming close to this. This is higher than anything possible on the Air side.
As far as the cost of adding huge heat emitters like the Heat Geeks do. It is cheaper than digging up the yard for geothermal. So if you are going to spend extra money spend it on Heat Emitters and leave your yard alone. The Bigger Heat Emitters are cheaper than digging up that yard.
You don't have to implement all the Heat Geek ideas. You can pick and choose and still have a great effect on raising the SCOP. This is an exciting time to be a hydronics designer because our work now has a 800% greater effect on system design with efficiency improvements than it used to have!!! We can surpass SCOPs by a big margin that is found in Air systems or Mini Splits as there is very little modification those designers can do to increase performance.
Its a great time to be a hydronics designer!!!
Hydronics Designer
this seems to be a good description of SCOP and the standard that regulates it
Just to clarify my claims on efficiency improvements after some further thoughts.
A COP of 8 is possible and maybe even beyond that. The potential to have a 800% improvement is there. But that is only at peak performance conditions. SCOP is the seasonal measurement of efficiency and at Open Energy Monitor the top SCOP is 5.5. So actually improvements in efficiency for the entire year and averaged out would be 550% or 5.5 times greater than a system with a boiler. It still makes it worth it to hire a good hydronics designer.
I didn't want to overstate in my claims.
Hydronics Designer
I'd be leery to mention that 8 SCOP number to a potential customer. They may hold you to it.
Everything I find on line from engineering groups indicate 3-4.0 as a good SCOP number
The open energy monitor site is a really good resource but I would advise a bit of caution when seeing a SCOP of 5.5 Have at look a the detailed data. Sometimes its a holiday home and is only being kept at low temperature when unoccupied!
What does confuse me is that there are a lot of Vaillant Arotherm+ systems up with quite high SCOP numbers. Lots of renewable suplies places stock them in the UK so that might be the reason. But these systems all use R290 refridgerant. Looking at some detailed Mitsubishi Ecodan data and the units that use R32 seem to have much better peformance than the R290 units of the same output. The R290 units can modulate over a greater range and get to much higher temperatures.
Confused John
@John Ruhnke : "Remember a graduate of the Heat Geek training has an average of 4.19 SCOP. Nothing coming out of America is even coming close to this."
I've never seen SCOP calculations from an American system so I don't know how you can say that.
At the risk of rehashing an earlier discussion, there is zero predictive power to a SCOP number. It's useful for comparing two competing installations, the one with the better SCOP is going to use less energy. But you can't take a SCOP number and say that my house in my climate is going to achieve an average COP of X based on the SCOP.
SCOP numbers are a useful comparator but they are really dependent on the temperature profile of the location. Comparing SCOP numbers from the UK with the USA or even other parts of Europe is impossible.
I said a COP of 8 not SCOP of 8. There is a big difference between the two.
Hydronics Designer
That's exactly backwards. SCOP is adjusted for climate. They're designed to make it possible to compare performance across different climates.
@DCContrarian I don't understand how calculating (Heat Output) / ( Electrical Input) over the year has a component that considers climate.
It doesn't. But that's not what SCOP does. SCOP does that calculation and then adjusts for climate. We discussed this back on page 2 of this thread.
Because the SCOP number is way better than any version of any number coming out of America. The biggest thing to remember is that these Heat Geeks are monitoring in real time and able to adjust the equipment for better performance in real time. They make improvements on the next job based off of this measured performance. They compare results with other installers. This is why there SCOP keeps getting better over time. It is a revolutionary educational method. I did something similar while building race cars when I was in my twenties. I modified my car based off measured performance and my car and I kept getting faster and faster as the years went on until I finally won an Amateur racing championship in 1988.
I know how well this works. It produces unbelievably successful results that are documented. I worked for a Measurement and Verification Engineering Company here in America. They aren't even close to the progression these Heat Geeks have made in the U.K. We might have a few monitoring projects in America but the results posted don't really go over the actual individual improvements made in a detail such as what the Heat Geeks are doing. There is a night and day difference between the two.
Hydronics Designer
COP of 8 is stretching it. You are the point where installed cost of extra area makes the ROI pretty much never. As nice as to think of ways of improving systems you can quickly hit the law of diminishing returns.
The beauty of modern AWHP units is you don't need fancy controls. Nothing aftermarket will work as well as what is built in plus you are now adding cost, complexity and a heck of a lot more commissioning time.
When I'm looking at these systems, my first priority is how I can eliminate a part or controls. Simplifying the setup means cheaper install and much easier setup.
For example with a recent modification, I eliminate a relay module. Removed a couple of actuators for bathroom floor heat and adjusted the rest to allow some flow even when off. Set the manifold deltaP pump to run 24/7 as there was no need to control it from the thermostat. Bonus is the floor heat is much toastier (and happier management) and there is overall more circulation water through the emitters, thus lower RWT to the heat pump.
As an instantaneous COP 8.0 is not outlandish, my Chiltrix claims 8.5 with an 8C (14.4F) difference between outdoor air and water temperature, at 25% output.
I just don't know how useful instantaneous COP is as a measure.
Instantaneous COP is useful when adjusting delta tee, flow rates or controls. You can watch the COP go up or down thus seeing if the adjustment you just made is better or worse.
Instantaneous COP is kind of useless though when comparing efficiencies from average cop of the whole day, week, month or year.
Hydronics Designer
Watching Adams You Tube on the 800-% efficiency claim, it seems some PV and optimization interface is in the mix. I see his thought on bigger, lower temperature buffers also.
Good for him taking this technology to these extremes. He claims combi boilers are the most common heat/ dhw source in his area. So the push to carbon free needs to go through the HP.
- 110 Chimneys & Flues