  • Jamie Hall
    Jamie Hall Posts: 27,975

    Aren't you fussy, @hot_rod 😊 Funny, I use exactly the same definitions for efficiency you do — and Siggy did. Don't ever put yourself down!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • John Ruhnke
    John Ruhnke Posts: 1,024

    Thank you DCContrarian. I now realize that and I learned it from you. It took a little bit to sink into my skull but I get it.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
    DCContrarian
  • jesmed1
    jesmed1 Posts: 1,631
    edited January 2025

    Thank you for introducing me to that Brookhaven efficiency study and the resulting cycle efficiency curve. It's an excellent study that does measure the actual, total, useful BTU's output by the boiler according to the delta T x gpm equation, so it is indeed a "real world" study that uses actual measured, not theoretical, efficiency.

    Unfortunately the methodology of the study makes it difficult to draw direct conclusions for our cold start, cold finish boilers. The Brookhaven method was to instrument and run the boiler to maintain a fixed internal water temperature for the entire range of test time, as would be the case if the boiler were also providing DHW.

    This means that the Brookhaven boilers had significant jacket and flue losses during idle times while the burners were not running. So for example, in a test run in which the boiler had, say, a 20% duty cycle, it would run for 5 minutes on, 20 minutes off, 5 minutes on, 20 minutes off, etc. And it would be maintaining its internal water temperature during that 20 minute off period. So even though the burner was only running 20% of the time, the boiler was losing jacket and flue losses at the fixed water temperature the other 80% of the time.

    While this methodology may be accurate for a boiler supplying DHW and maintaining a fixed internal water temperature, it's not accurate for our cold start, cold finish boilers. Because with post-purge, the internal boiler temperature drops off quickly within minutes as we recover the residual heat. And then for, say, 3 hours of idle time, the boiler is cold with zero jacket and flue losses.

    As a result, I don't think the Brookhaven cycle efficiency graph applies well to our different mode of operation, because out boiler is sitting cold and losing zero heat during the "idle" times when the Brookhaven boilers were still maintaining internal water temps and suffering jacket and flue losses.

    Of course, we do suffer jacket and flue losses, but only while the boiler is running and post-purging for a few minutes thereafter.

    Nevertheless, I don't think your 60% overall efficiency conclusion is far off. I think we're probably in the high 60's or low 70's. So we're within 10% of each other's conclusions, which is probably close enough.

  • jesmed1
    jesmed1 Posts: 1,631

    I didn't mean to suggest anyone was guessing. My point was that the report describes a range of Euro boiler efficiencies, which I'm sure they obtained from good sources. But the report isn't the boiler efficiency study itself, and it gives no technical details on any specific boiler that would help me say, OK, that boiler is roughly comparable to my boiler, and now I can compare efficiencies on an apples-to-apples basis.

    I can only guess that my boiler probably falls into what they would call the "oil boiler, low temperature" class, which doesn't help me much.

  • John Ruhnke
    John Ruhnke Posts: 1,024

    @DCContrarian

    Everything so far that I learned from the Heat Geek courses so far has been online with no actual conversations with actual Heat Geeks. February 4th I have a actual online meeting set up with a Heat Geek on Verification. I have lots of questions and as the next step I plan to get involved in the network. It is stage two of my education process. I did have a conversation with Glyn Hudson the founder of Open Energy Monitor and he told me to get trained by the Heat Geeks. I took over 100 hours of the courses and graduated from that. It is a fun journey that still has a lot more steps to go through.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Jamie Hall
    Jamie Hall Posts: 27,975

    You know, all this reminds me a little bit of the bad old days, 60 or so years ago, when I was a pretty wild kind of guy and into drag racing. SuperStock. There were lots and lots of discussions — some rather heated — and theories on how to make a gofast car gofaster and stay at least vaguely street legal. Horsepower ratings. Best rear axle (both the axle itself and suspension). Carburetors. Timing curve mods. Headers. The lot. A lot of guys (and gals) did a lot of tinkering, and there were always the guys with fancy instruments who proved us wrong…

    But you know what? At the end of the day it was pretty darn simple: did my car get to the other end of the quarter mile before yours did? End of story.

    It was fun while it lasted, until the EPA took our toys away…

    Jan and Dean Live - Little Old Lady from Pasadena .

    Here it's much the same. Is the little old lady warm and comfortable in her house? Can she afford it? End of story.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    PC7060
  • DCContrarian
    DCContrarian Posts: 1,588

    "It was fun while it lasted, until the EPA took our toys away…"

    I would have expected "Fun, Fun, Fun" by the Beach Boys, not Jan and Dean.

  • DCContrarian
    DCContrarian Posts: 1,588

    Thanks. We're all here to learn, I've learned a lot from the people here. I learn the most from the ones who challenge my thinking.

  • hot_rod
    hot_rod Posts: 28,708

    I think those who are considering a move to a A2WHP would want more real life, actual installation run time data that is close to their application and location.

    Data from Hogwart helps some. I appreciate that group for putting together a database of installed systems over there.

    I though NYSERDA and a few others were compiling data on installed systems. I'm not sure what group would have the budget to assemble a team to seek out and confirm data from multiple sites? What about the Canadians?

    As DC alluded to, so many variables to consider with HPs.

    The weather is always a big unknown. We had twice as many triple digit days last summer as any other year. Also higher overnight temperatures. So on the cooling side the loads need to be reexamined. 15 days of AC under-performing may not set well with some.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • John Ruhnke
    John Ruhnke Posts: 1,024
    edited January 2025

    @hot_rod

    Everyday I am selling systems and training installers. I have been doing this since 2021 part time and April of 2024 full time. Nobody has bought monitoring equipment though yet. The monitoring equipment coming from Europe is designed for British threads (Running threads) and British electricity (50 HTZ vrs 60HTZ and 208V vrs 240).

    I rep HBX through Arctic Heat Pumps and can sell HBX controls. HBX has a BTU meter. There are plenty of electric metering options out there for the solar industry. I can put something together if anybody is interested.

    My longer term plans are take the Heat Geek way and bring it to America and build a team of installers. I currently have a small team of installers installing and it grows everyday. I first learned the Arctic Heat Pumps way. I know that extremely well. Arctic Heat Pumps has a very good unit. It is just about modifying installation methods and controls which I am already doing. Gradually methods will get adopted. Another challenge is installer capability. The Arctic way is easy to copy and install with out installers having a lot of hydronics knowledge and the SCOPs are pretty good. The Heat Geek way requires a lot more hydronic knowledge and training. It is harder to screw things up the Arctic Way. Some of the Heat Geek methods require advanced knowledge of hydronics that is lacking here in America.

    That is why I am here at the wall. I am trying to recruit the best and brightest in the hydronics industry.

    Heat Geeks have already done the R & D. I can improve SCOP in Arctic systems simply by learning and copying what the Heat Geeks are doing. Of course I will learn more if I monitor.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Jamie Hall
    Jamie Hall Posts: 27,975

    "Some of the Heat Geek methods require advanced knowledge of hydronics that is lacking here in America."

    Son, I hate to break this to you — but you just stepped on a LOT of toes. We may do things differently on this side of the pond, but different isn't "lacking". It's just different.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    LRCCBJTeemok
  • hot_rod
    hot_rod Posts: 28,708

    I can maybe help with BSP transitions. We have several pages of them in the catalog

    The original Alpha pumps were 230V and came with 120-230v transformers. You can buy those transformers inline

    Early Viessmann stuff was all 230v and had transformers built in for North America.

    I have a handful of test pumps that Grunfos has sent me over the years. They are 230v 50 cycle. I run them on 240v 60 cycle without any issues. For my own use. I we’re would not sell or install them on a customers house without UL

    So for your own testing purposes, you should be able too use anything from the UK market

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • John Ruhnke
    John Ruhnke Posts: 1,024
    edited January 2025

    Thanks Hot Rod,

    I forgot to mention. I rep and have sold caleffi products through Arctic Heat Pumps as well. Good stuff.

    The question is Do they read right? In our electricity.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • John Ruhnke
    John Ruhnke Posts: 1,024
    edited January 2025

    I will train anybody. Teach anybody. You can't teach advanced hydronics unless they learn lesser skills first. I have homeowners telling me they can't find anybody willing to install ATWHPs. There is nothing I can do if installers refuse to even consider it. I have plenty of Leeds coming at me every day from Homeowners. I need more installers.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Spot on! RE: older post about trouble getting ATWHP in Virginia. Finally found a small side-gig startup contractor (works for a large mechanical contractor); he's the only one who didn't run the other way when asked about ATWHP. He is learning along with me as I challenge him to think differently about HVAC using hydronics in residential work. It's a slow and iterative process. Took a while but he's finally getting some real support from LG corporate folks so it looks like we will use their HP.

  • DCContrarian
    DCContrarian Posts: 1,588

    Glad to hear you were able to find someone to work with you. LG has some interesting products.

  • hot_rod
    hot_rod Posts: 28,708

    Not all the A2WHP manufacturers, or their team, are hydronic savvy. Some, many, are air side, air to air, maybe ground source, heat pump brands trying to branch into A2W. Which means THEY first need the hydronic side training.

    Is residential hydronics even a thing in China?

    Specifically how to apply A2WHP to lowest SWT requirement systems. Else they may have some unhappy customers trying to replace a high temperature only, boiler with a HP.

    Fortunately a handful of manufacturers reach out to folks like Siggy for some hydronic side design guidelines.

    Many will recognize the A2WHP manuals that have Siggys fingerprints on them.

    I for one appreciate Siggys ability to think outside the box and look for ways to assure the system will perform and be as efficient as possible. He also practices what he preaches with 3 of his own A2WHP systems at his home and his kids.

    I appreciate also that he colors outside the line from time to time, challanges installers to look at "off the wall" options, not just cookie cutter systems. That probably frightens some designers, installers, and arm chair A2WHP experts. Plenty of those haters online these days, if you surf the many online chat rooms.

    Obviously as equipment changes becomes more versatile so do installation options. His first system did not have or offer variable speed compressor and vapor injection.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Posts: 1,588

    I love Seigenthaler, I've learned a lot from his writings and I consider him influential in my learning. However, having seen a few videos and read a few articles by him on air-to-water, I have to disagree with some of his design choices.

    First, he often includes DHW and a backup boiler in his designs, as I noted above I believe that's just a bad idea.

    When it comes to cooling, he often advocates installing a three-ton air handler with ductwork and a hydronic cooling coil. That's basically giving away all the advantages of hydronics. You're left with no advantage over conventional AC and a bill of materials that's two to three times as high.

    He often says, "with the right controls, hydronic panels can be used for cooling." I feel this is a dangerous over-simplification.

    I don't know if he's still advocating this, but in the past I've seen designs from him where he puts the temperature sensor in the buffer tank. One of the keys to understanding air-to-water is that the heat pump wants to adjust its output to meet the load, and you want to do as little as possible to obscure from the heat pump what the load is. This sensor placement has the effect of obscuring from the actual load, and can lead to unnecessary short cycling.

    We're all still learning.

    lkstdl
  • John Ruhnke
    John Ruhnke Posts: 1,024
    edited January 2025

    I took a lot of classes on radiant heating and hydronics from Ziggy. I have a couple of his books. I also have his software. I bought Hydronic Design Studio over 15 years ago and it still runs on my Windows 11 laptop. I use it to size pumps and systems still today. It is my most favorite software design tool.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Kaos
    Kaos Posts: 1,003
    edited January 2025

    There is also way too much focus on hydraulic separation and not enough on what actually matters. This is getting enough flow through the AWHP under all conditions and never mixing down supply water. Hydraulic separation fixes the first but very easy to screw up the 2nd.

    I'm also with @DCContrarian if you add up the BOM cost off all the non AWHP bits in any of those diagrams you are probably talking at 3x the cost of the heat pump. Except for very high end builds, that simply does not work.

    I'm coming around the same conclusion as well. If you want air to water for floor heat, best option for cooling and supplement is a ducted heat pump. Regular HPWH for hot water. It is still expensive but now not out there. The bad news is you will not get that blinged out wall of copper pipes and valves.

    PC7060DCContrarianlkstdl
  • John Ruhnke
    John Ruhnke Posts: 1,024
    edited January 2025

    I am not new to designing systems with ATWHPs. It is the only thing I do all day long. I have been doing it for over three years now. I have gotten pretty good at it. I have specialized in hydronics for 35 years so I might know a thing or two. When I took the Heat Geek training I learned a lot of different piping methods. The heat geeks love simple systems with less zones. They love to size the pump to handle both the heat pump and the load. In new construction with a smaller simpler house, with out hydronic cooling it makes sense. That is mostly what they do in the U.K. I say great, pipe it with out a low loss header or buffer tank. The radiation, and pump need to be sized right for a low delta tee and higher flow rate. With Ziggy's Hydronic System Pro I can easily design for this. The software is great and with it I can account for delta tee, flow rates, velocity and pump head. I can easily build that system. Yes you will get the best possible Efficiencies from optimizing this kind of a system designing for long run times, constant circulation and the lowest possible supply water temps. They use panel radiators and trv's. The trv's never fully turn off. You just dial them up or down. The problem is you need to maintain a delta tee of 8-10 running through that Heat Pump. That's a much smaller delta tee than most installers are used to. Things can easily go wrong very fast if you don't get this type of a design right. When it goes wrong expect a high rate of short cycling, error codes with the HP, bad efficiencies and a HP that needs to be replaced often. Same thing happens if you install but undersize the buffer tank. Much of my competition is recommending smaller buffer tanks. Most likely one reason they aren't as successful.

    One problem you run into is an existing house where you don't want to rip out the existing radiation, piping or pumps on the secondary side. I also learned the proper way to pipe up a buffer tank so you don't get the short cycles and you get good efficiency. I was taught this in the Heat Geeks mastery class. You can also use outdoor reset and run very low water temps.

    In my house I have radiant heating though out the entire house. It is warm and comfortable. It is the best heating around and I wouldn't trade it for anything else in the world. I have furniture and area rugs in places on the floor. This does change the balance of the system. Trying to balance a system by adjusting the delta tee in each loop is one way to dial it in. It takes a lot of work to do this and you have to wait a day to see the results and then make further adjustments. Many trips back before a client is happy. I have lots of zones in my house and I don't need to worry about this. I never had any balance issues. All my kids get control over there own room temperature. I also have a open well geothermal radiant cooling system in it. My system is 20 years old. When I add a Heat Pump to my house I will most likely use a buffer tank.

    If you want to pipe up a house using existing American hydronic methods than a properly sized buffer tank with a higher flow rate on the primary side and lower flow rate on the secondary side is the way to go. You won't get short cycling. You can design things on the secondary side similar to what you are used to. You can design this with good efficiencies. Some of the systems with multiple HP's and multiple AHU's Fan Coils, radiant and panels radiators in these bigger houses or commercial buildings it makes a lot of sense to use a buffer tank.

    If you decide to build a system without a buffer tank than you have to learn and do the math for a proper design!! Ziggy's software Hydronic System Pro would be the tool to buy. I find it essential to get everything right.

    P.S. Another trick is to use that buffer tank as a volumizer. This can solve a lot of the short cycle lengths and aid in the defrost cycle. It also increases the efficiencies. A topic for another day.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • DCContrarian
    DCContrarian Posts: 1,588

    There are two things that are fundamentally different with heat pumps. One I've already talked about, which is that the heat pump control circuitry has to be able to sense the actual load. The second @Kaos alludes to, which is you want your emitters to be receiving water at the temperature it's coming off of the heat pump.

    Unlike a boiler, where a BTU is basically a BTU, a heat pump cares a great deal about how that BTU is produced. If, for example, you need water at 110F, you don't want to be producing it at 140F and mixing it down, you want to be producing it at the temperature you need it. And the heat pump will run a lot better running continuously at 25% load rather than running at 100% load on a 25% duty cycle.

    These two principles together can be summarized as: If you're mixing, you're doing it wrong.

    John Ruhnke
  • John Ruhnke
    John Ruhnke Posts: 1,024

    There are Air Handlers that have coils designed specifically to work with ATWHPs. I have sold and trained installers on this. You can use your ATWH AHU to reduce the number of HPs on the job. Also why worry about having to change refrigerants in the future. Hydronics will always be around so a hydronic AHU makes sense. That refrigerant in that AHU may not be around 10 years from now.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • hot_rod
    hot_rod Posts: 28,708

    do the “right controls” even exist? Even the hp manufacturers have not come up with the control to do everything on ever application. Currently it seems you need a blend of OEM and off the shelf components to pull it all together.

    We’ve been through this when hydronics blends with solar thermal, wood, or HVAC systems. Coming up with Rube control packages the only the installer understands. Maybe!

    Heck it is a challenge to just get some brands of thermostats combined to a simple hydronic or Hvac system, ie Nest.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Posts: 28,708

    You mentioned your system have adequate mass or volume to defrost without needing to kick in resistance strips? I don’t think that would be common with the millions of zoned fin tube systems out there. The will need some buffer, until the compressor can modulate down to a very low level. The buffer piping and size options have been reduced greatly from the earlier single speed compressors.

    Connecting into a two temperature system as many larger radiant homes are, will include some mixing. Multiple heat sources may require hydraulic separation.so the “ideal” application that you may have will not be the norm in retrofits.

    The key for retrofits is understanding the application and piping options. A2Whp will not be for everyone. The designer/ installer needs to know when to not participate in a job that doesn’t make sense for a hp. Regardless of the consumers pocket book.

    Same for radiant floors in high load homes. Orin tiny load homes. Just say no!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Posts: 1,588
    edited January 2025

    To be clear, I'm not opposed to air handlers. I'm a big fan of small ones in the 3000-10,000 BTU/hr range, with variable speed fans. Put one of those in each room with an independent thermostat and you get unsurpassed comfort, incredible temperature stability. They're a good complement to under-floor heat because they're able to ramp up and down much more quickly, and of course in the summer they provide cooling. And the BOM isn't too awful, you might be able to get away for less than $1000 per room which is pretty good when you're looking at each room having its own thermostat. That's what I have in my own home*.

    The issue I have is with big three-ton air handlers with ductwork. They get installed just like conventional AC and they offer no benefits. But since everything in the hydronics world is niche, they end up costing two to three times as much as conventional AC. And this gets to a general theme in my thinking when it comes to air-to-water, which is that the question is never whether something is possible, it's whether it's practical. Ideas that drive up the cost of installation without delivering value just aren't practical.

    *(I will say that I am disappointed with the product offerings available in the US right now when it comes to small air handlers. I have seven air handlers in my house, a couple of them I imported direct from overseas and all of them had to be modified and customized extensively to make them work satisfactorily. Nothing wrong with the technology, just the implementation. I couldn't in good faith recommend any of them as they come out of the box.)

    lkstdl
  • John Ruhnke
    John Ruhnke Posts: 1,024

    @DCContrarian,

    Options, That is what it is about. Options. Radiators, radiant heat or cooling, Fan coils Which is what you are describing with the thermostats and AHU's with low or high velocity ducts. Its nice to be able to design a system tailored to any options.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • John Ruhnke
    John Ruhnke Posts: 1,024

    @DCContrarian,

    I am very interested in learning more about how your system design works. It sounds like you have a great system and its dialed in!

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Kaos
    Kaos Posts: 1,003

    I don't think any recent AWHP needs a buffer for defrost, I don't run one and has never been an issue. Defrost happens mostly around near freezing temps and most likely there is a zone calling for heat at the same time which the heat pump can steal heat from.

    As @DCContrarian buffers tend to hide the system load from the AWHP which means they will not modulate properly. I've seen some of the Artic diagrams where they are essentially running the heat pump with a digital on/off signal. Running full tilt like this is bad for efficiency, you want the unit to modulate and run at constant power during the heating season. Buffers tanks are not free and external reset controls are defiantly spendy.

    I run two different temp zones without issues simply by cascading them. The return from the high temp zones is warm enough for the floor heat, so there is no mixing.

    What is the average system BOM cost VS AWHP ratio for these installs? If you are in the 2x to 3x range, it will not fly for anything but expensive custom. For these systems to have any chance of success in the market, the installed price needs to improve.

    I have done detailed BOM of all AWHP with FCU for cooling and it simply does not pencil out. A smaller AWHP for heat and a ducted heat pump is the fraction of the cost and similar install effort. The kicker is that is uses less energy as well. I would like to be proven otherwise but cooling with AWHP is dead.

  • hot_rod
    hot_rod Posts: 28,708

    if you defrost with the water from the buffer you defrost with heat generated with 2 COP or higher. So if the goal is to squeeze every ounce of efficiency this makes sense

    I don’t believe you can buy the Viessmann system without the buffer, it comes in the package. The dhw tank is an option.

    The US boiler and maybe a few others are packaged with a buffer, that is how the manufacturers wants them piped.

    i sit right next to my my system and hear and watch the pump and compressor modulate all day long to maintain 20 gallons of buffer. The pump runs as low as 3.2 gpm, up to about 6.8.

    This water goes directly from tank to radiant slab. I still haven’t dialed in the ODR to modulate the buffer temperature I can go down to probably 95 on milder days

    Single digits this past week here, on sunny days my PV has been cranking out around 4800w so the HP load is covered

    My cooling will be chilled water to the slab I think in this dry climate it can work well enough for my shop anyways


    If so there are a lot of radiant slabs in my area that could use the slab as part or all of the cooling load

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Hot_water_fan
  • DCContrarian
    DCContrarian Posts: 1,588

    I asked Seigenthaler about the "right controls" in one of his webinars, and what he meant by that is a temperature/humidity sensor that calculates the dew point and adjusts the setpoint on the heat pump to keep the water temperature above the dew point so condensation can't happen.

    That works, in the sense that it does what it is intended to do, but it's not going to provide appropriate cooling. What if the amount of cooling you need is greater than the amount your emitter can provide at that water temperature?

    Worse, it ignores the role that dehumidification plays. What's often suggested is to add a few air handlers to provide dehumidification and supplement the passive devices when they can't keep up with the cooling load. The problem is that there's no methodology for designing such a system, a la Manual J and Manual D. To be safe what you'd have to do is size the system according to Manual J. But then you end up with a completely redundant system, plus the challenge of controlling it by dewpoint if you wanted to somehow prioritize the hydronic loops. I'm not aware of any product commercially available that does that prioritization.

    ScottSecor
  • DCContrarian
    DCContrarian Posts: 1,588

    @Kaos : "I have done detailed BOM of all AWHP with FCU for cooling and it simply does not pencil out. A smaller AWHP for heat and a ducted heat pump is the fraction of the cost and similar install effort. The kicker is that is uses less energy as well. I would like to be proven otherwise but cooling with AWHP is dead."

    I have seven air handlers on my system, they range from 3,000 BTU/hr to 10,000 BTU/hr, total of 41,000 BTU/hr. Each one has a four-speed fan, at the lowest fan setting they put out about 10% of nominal capacity. They can cycle on and off without ill effect, so you can get arbitrarily low levels of output from them. Which means you can put a fan unit in each bedroom, say, each with its own thermostat, and have them provide as much or as little cooling as needed to that room without impacting the other rooms. That's basically the appeal of hydronic heating, but with ATWHP and air handlers you can get it for cooling as well.

    I know of no other way of getting that level of granularity of output from air conditioning. The value proposition is comfort, not cost.

  • DCContrarian
    DCContrarian Posts: 1,588

    BTW:

    In some posts above I've talked about how for variable speed compressors COP is higher at partial loads, but that while most air-to-air manufacturers provide part-load figures, air-to-water units tend not to have them. Well, I was just poking around on the Chiltrix website and I found they have output and COP numbers for 100%, 75%, 50% and 25% of capacity — at least for cooling. It's at:

    https://www.chiltrix.com/documents/Chiltrix-Inc-ACCL-Catalog-V2.420240224.pdf

  • Kaos
    Kaos Posts: 1,003

    We have to look at what most people are fine with. That tends to be a single air handler for the whole house for cooling. Bigger house, maybe 2 zones (either as extra air handlers or duct zoning).

    Now to implement that with AWHP you need those expensive 3 ton FCUs plus all the ducting. So $$$ plus efficiency will still not be that great as there is extra heat transfer stage (outside→refrigerant→water→air), no way around that physics problem. The AWHP and emitters would have to be sized for full house load as well. You could use an FCU for extra heat but they need high temp water, so again, efficiency suffers. Running an FCU with low temp water is a no go for comfort as nobody wants lukewarm air blowing in the house.

    Lets look at smaller AWHP for base radiant load and ASHP for cooling/supplement. Lower BOM cost, heating and cooling is more efficient and similar install cost. You also have redundancy for free without having to plumb in a boiler. For a new build, it is hard to argue with that math.

    Biggest bonus is that it is viable strategy for retrofit. You no longer need a big air to water unit and install extra emitters to get the SWT down as the existing ones can provide most of that baseload heat. In an existing house with rads and no cooling, this is the only thing that makes sense.

    Of course there are cases when you do want better control and I can't really argue with the flexibility of hydronic with smaller FCU but be ready to spend real dollars for it.

    @hot_rod Small buffer tanks are fine and if they are free with the unit, why not. They quickly settle to either SWT or RWT depending on how they are plumed, so generally won't effect operation much. A small buffer tank can improve cycling in the shoulder season, don't know how much it would actually effect seasonal efficiency as most of your energy cost are in weather colder than that.

    Improperly plumbed big buffer tanks is where you run into issue.

    There is also the real risk of mixing with certain buffer tank configurations, not something I have seen mentions in literature out there.

  • DCContrarian
    DCContrarian Posts: 1,588

    @Kaos : "Small buffer tanks are fine and if they are free with the unit, why not. They quickly settle to either SWT or RWT depending on how they are plumed, so generally won't effect operation much."

    I agree with this, and it's an important observation. It's why putting a temperature sensor in the buffer tank is not a good idea because it doesn't convey any information about operating conditions.

  • DCContrarian
    DCContrarian Posts: 1,588

    @Kaos : "I've seen some of the Artic diagrams where they are essentially running the heat pump with a digital on/off signal."

    I think I've seen the same diagrams. My immediate thought was, "guy who thinks a heat pump is just like a boiler, only noisier."

  • JDHW
    JDHW Posts: 107

    @DCContrarian

    Have a look at the following:

    http://www.mitsubishitech.co.uk/Data/Ecodan/Controls/PAR-WT50R-E_FTC5/FTC5_Databook.pdf

    Lots of detailed data on ecodan heatpumps.

    John

  • John Ruhnke
    John Ruhnke Posts: 1,024

    The bigger the buffer tank the better. The buffer tank acts as the load for the HP. It isolates the system piping from the primary piping. It provides energy for the defrost cycle. With a proper sized buffer it is hard to screw things up. The bigger the tank the longer the minimum cycle length will be. You can pipe the secondary side practically anyway you want without problems. Just don't over pump the secondary side. Over pumping the secondary side is hard to do because of the smaller delta tees on the primary side you have a bigger flow rate on the primary side vrs the secondary side. Arctic has lots of designs with multiple heat pumps. To do staging and make all that work properly piping to a buffer tank works great.

    You can combine most any form of hydronic design after the buffer tank and it works great.

    Small buffer tanks are a bad idea. They will promote shorter cycles. Kill your COP.

    Arctic systems have been out now for decades. They have experience and they know what they are doing. ATWHP systems without problems since 2015. A long track record of success here in North America.

    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
    bjohnhy
  • hot_rod
    hot_rod Posts: 28,708

    Actually there is a movement to smaller buffers, this Caleffi model from our UK website. A small wall hung buffer would have been ideal under my Vitocal.

    The small VitoCal 100 comes with a 20 gallon tank. It actually mounts on the indirect, if you chose to use the DHW function.

    Wall hung tanks keep them it off the shop floor. I found 4 manufacturers of small wall hung buffers for variable, modulating HPs.

    And there are specific buffers for just chilled water use, with a baffle or layered baffles.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream