first day with new vent mains and vaporstat

hi guys
so yesterday i finished adding some vents to the mains and vaporstat. i set vaporstat(0-4psi) at 1 psi with 8oz diff.
yesterday the temperature was maintained without ever coming near the .5 psi. cut out (i have 3 psi gauge installed). So i was looking forward to stare at the boiler the AM to watch the recovery from 69 to 71. I usually do 68 at night but didnt want to push that much today. so the boiler ran till thermostat temp got about 70/70.5 till it hit the cutoff, pressure dropped quickly but also raised quickly when it come back on so the boiler ran for maybe 2-3 min before hitting the cutoff again…it did that twice before the thermostat was satisfied. I guess thats short cycling? any recommendations to make to vaporstat? 1 pipe steam weil McClain
Comments
-
Yep, this is short cycling. But I wouldn't worry about it as it sounds pretty typical for an oversized boiler. What is your measured radiator EDR and the capacity of your boiler?
I have an oversized boiler and I've installed a vaporstat. I cycle on pressure when it gets below 30F outside. Some things to consider:
- Perhaps raise your cut out pressure a bit to say 12-14oz and your differential to 8-10oz less than your cut out. Still very reasonable pressures and the wider differential gives the boiler a bit more time between cycles.
- My system works best when I "set it and forget it". I've found no measurable financial savings when using setbacks. I keep it at 68F and it cycles much less, especially since there is no recovery. Perhaps on a perfectly sized and balanced system this wouldn't apply but on my oversized system it does more harm than good.
1 -
hey thx for reply
I never did the calculations (complete laziness) but am pretty sure it’s oversized.
I’ll try your recommendations. What would be acceptable amount of time to run after it atarts again?
I’ll also have played around with leaving it on 70 all the time, might just do that
0 -
-
-
i increased the set back a bit (also back in the 20's today)and it short cycled 5 times but still satisfied the thermostat….is that still acceptable?
0 -
-
Acceptable is up to you to determine. I assert that for atmospheric gas steam boilers, the term "short cycling" doesn't really apply. If you can't notice it while sitting on your couch, it's fine.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements