Advice for Designing Radiant System for Small Cabin

Hi there,

I'm early in the process of designing a small cabin to be built near the coast in Northern California. Where the cabin will be has lows averaging between 41F (winter) and 51F (summer) and highs between 55F (winter) and 74F (summer). The cabin is going to be small at about 900sqft. It's one-story, though the main part of the cabin will have quite high ceilings as there is a lofted room.

I am the general contractor on the build, and plan to use hydronic radiant heat for the home. Because of the site conditions, a concrete slab is not possible. I planned to use some sort of warmboard type material to install the pex underneath some wood floors. Additionally, if possible, I would prefer to leverage a system that only relies on electricity as there is no access to natural gas at the site.

I'm fairly early on in the design process, and am looking for general advice on how to even approach designing the system, as well as advice on what products to consider. On designing the system, I've done a lot of research but it is quite easy to get lost in all the details and all the information out there. I have a plumber lined up for the build, and while he is a skilled plumber, he isn't someone that can design the heating system. At different points, I've reached out to vendors of various products who often say conflicting or contradictory things, or have a limited set of information based on the part of the system they sell. Does anyone have any recommendation for individuals who consult to do heat load calculations and help design the system?

As far as recommendations on parts of the system - do people have recommendations for a pex track system? Warmboard? Thermalboard? Runtal? Again, this is being installed above a plywood subfloor and underneath 3/4" (or maybe 1") Monterey Cypress floors.

Lastly, what heating sources might people recommend I look in to? Given I'm hoping only to use electricity, I have been considering the SANCO2 air to water heat pump. I had one of the most confusing (on many levels) calls with a rep at Small Planet Supply which included him telling me that the SANCO2 shouldn't be used for in floor heating unless it's a concrete slab - though many sources (including their website) seem to suggest it would/does work fine. One issue he brought up was the water inside the tank can get destratified which would effect your ability to use the system for domestic hot water as well. It may be expensive, but I wonder if you can just have one HP + tank for the radiant floors and another for DHW, keeping the two systems completely separate? It's not clear to me why it would matter in this case if the tank was destratified.

As I head down the path to building this cabin, any nudges or pushes in the right direction would be much appreciated.

-matt kat

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,095

    Hi Matt..your project sounds exciting.

    1. Heatloss
    2. Consider using Gypcrete (lighweight) so you can have more of a high mass system. It makes such a difference in "feeling" the warmth of the radiant. Alot of people are a bit disappointed otherwise.

    3. You can put any floor covering you want over it.

    Let's see what Uncle Richard of All Island Radiant can add to that . Mad Dog

    GGross
  • Jamie Hall
    Jamie Hall Member Posts: 25,991

    Calling @Alan (California Radiant) Forbes !

    And may I suggest looking into air to water heat pumps? One of those might be a good fit…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • DCContrarian
    DCContrarian Member Posts: 1,117

    I can help you with a back-of-the-envelope heat loss calculation that will at least give an idea of what kind of system you need.

    What are the dimensions of the cabin? Length, width, height, number of floors. What is the construction, particularly the insulation level? Walls, ceilings and floors.

    To get weather data, go to this link:

    https://ashp.neep.org/#!/product/34581/7/25000/95/7500/0///0

    Click on the box on the right side of the page that says "Advanced Data — System Sizing." Put in your zip code, and then the drop-down box below the zip code input will show a list of nearby weather stations. Decide which one most closely matches your climate. Report that back here.

  • Hot_water_fan
    Hot_water_fan Member Posts: 2,190

    also consider an electric boiler. It’ll be more expensive to run but so much cheaper to installer. For a small space in a warm climate, it’ll probably make sense to pay higher bills than drop the money on an air to water heat pump.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    I'll offer five options for going all-electric:

    1. Resistance electric water heater, underfloor hydronic tubing. This has the highest operating cost, and high install cost, although lower than #2.
    2. Air-to-water heat pump, underfloor hydronic tubing. Lowest operating cost, highest install cost.
    3. Underfloor electric resistance heat. Highest operating cost, low install cost. There's really no benefit to #1 compared to this.
    4. Baseboard resistance electric. Highest operating cost, lowest install cost. No "toasty toes."
    5. Air-to-air heat pump. Lowest operating cost, low install cost. No "toasty toes." Air conditioning.

    Depending on how the heat load calculations work out, the "toasty toes" may be over-rated, in low heat loss situations the floor temperature can be barely noticeable.

    mark3885
  • DCContrarian
    DCContrarian Member Posts: 1,117

    "Consider using Gypcrete (lighweight) so you can have more of a high mass system. It makes such a difference in "feeling" the warmth of the radiant. Alot of people are a bit disappointed otherwise."

    The latest thinking is that you get better comfort from a low heat capacity system that is able to shift temperature quickly and respond to changes in the load. That's what systems like Warmboard pride themselves on. A lot of what was attributed to "thermal mass" in the past turns out to be due to other properties of the material. What makes concrete work is not its nor its heat capacity, but rather the fact that it's a good conductor of heat so it spreads the heat evenly. Warmboard has a continuous layer of aluminum, which is an excellent conductor and gives even heating.

    A benefit that is touted of high heat capacity emitters is that they warm slowly and cool slowly, so they emit heat continuously. A low heat capacity emitter with a properly calibrated outdoor reset will give the same kind of continuous heat while also being much more responsive to changes in the heating load.

    Mad Dog_2
  • hot_rod
    hot_rod Member Posts: 25,011

    Of the systems I have installed I like the Roth panels. They allow you to use 6” on center spacing. That allows low water temperature, give you quick start up also. The 3/8” three version is 1/2” thickness. I think Uponor has a similar foam panel now also.

    Some areas work best with lightweight, fast responding radiant.

    AC not needed or wanted?

    Pace Supply is a hydronic friendly supplier, in that area. they would know the knowledgable hydronic installers near you.

    Osborne Sales reps many hydronic products in your area. They know the players also.
    Do you have good solar access. Passive solar options, PV incentives.

    www.dsireusa.org

    is the database for programs

    Make it as fireproof as possible!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Member Posts: 1,117

    "I have been considering the SANCO2 air to water heat pump. I had one of the most confusing (on many levels) calls with a rep at Small Planet Supply…"

    I honestly don't know how SANCO stays in business. I've heard so many stories like that, of people looking into it and going a ways down the path before eventually discovering it just wasn't going to work for them. I don't know what situations it does work in, but it seems like a vanishingly small confluence of circumstances.

    I've had a little bit of sales training, and one of the things I learned was that the first step in the sales process is to qualify the customer. Are they buying what you're selling? Because if they're buying apples and you're selling oranges there's no point in wasting both of your time. Just say, "sorry, at this time we're selling oranges and not apples, I hope in the future you'll consider us for all your orange and orange-related needs" and move on. For some reason SANCO seems resistant to do that.

  • hot_rod
    hot_rod Member Posts: 25,011

    give a shout out to member Teemok He is a knowledgeable hydronics contractor experienced in your area

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Teemok
  • mjkatsaros
    mjkatsaros Member Posts: 5
    edited January 21

    Thanks for all the helpful advice and suggestions. Lots of good suggestions to look in to here. Do folks have suggestions of models or makers of electric boilers that they like?

    Also - do people recommend Warmboard? I assume it comes at a premium $, but I do like that I would have one vendor as a point of contact for the whole system. So far, it has been tricky trying to act as the conduit linking up whatever material is holding the pex with the manifolds with the heating supply etc. It seems like having one firm helping to design the whole system would make for a much simpler setup.

    @DCContrarian thanks so much for the offer. I'll DM you now.

  • GGross
    GGross Member Posts: 1,492

    I feel like most contractors aren't big fans of warmboard, they would rather install their own preferred brand tubing and manifolds. If you are doing this as a DIY job warmboard will be OK. The panels themselves seem nice. Pretty much every barrier tubing pex manufacturer offers complete systems and design services these days. Uponor, Viega, Rehau, Legend Valve many others. One thing to note is when I have customers involved in the warmboard jobs they always come back to me for a manual J, warmboard wouldn't supply them with one. So not too sure how the system design is all that great when they skip step one.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    OK, got the data. Based on the measurements I estimate a design heating load of around 12,250 BTU/hr. 99th percentile design temp is 31F, average annual low is 25F. My understanding is California requires you to size between those two numbers. The lower one would put you at 14,100 BTU/hr, I think in either case you're looking at a 2 ton heat pump. I don't think any 2-ton heat pump on the market would have trouble putting out 14K BTU/hr at 25F, I'm not aware of anyone who makes a unit less than 2 ton (other than SANCO, who I wouldn't recommend).

    I'd think about cooling. The weather station data shows a 99th percentile cooling temp of 91F and an average annual high of 103F, in a small building you'll roast in weather like that.

    It seems like the meat of your heating season is around 47F. While you want to insure comfort at the coldest temperatures, if you're going to the trouble of doing heated floors you want them to be delivering their effect most of the time, not just on the few coldest days of the year. At 47F your load is about 10,000 BTU/hr, if you were to put heating under the entire 850 square feet that would be 11.8 BTU/sf, which would mean a floor temperature about 6F above room temperature, or 78F in a 72F room. That isn't noticeable. I would instead target a small part of the house to be at 85F when it's 47F out. That would give 26 BTU/SF, you'd need about 400 SF of it. Then I'd have a second zone — which could be another 160 SF of floor, or a radiator or a fan unit — that provides up to another 4000 BTU/sf when the primary zone can't keep up.

    Finally, don't take my word for all this. This is just to get you started. My understanding is California will want to see a real Manual J calculation.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    I get the annual heating load is 24,521,349 BTU. With a heat pump the average COP comes in at 3 and electricity usage is 2,456 kWh. Multiply that by your electric cost to find annual cost. The other alternative would be straight resistance electric, which would be 3 times that.

    I'd check whether California would allow that, they have their own energy code and it's pretty strict.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    The thing about Warmboard is it's really expensive, if I recall correctly about $10 per square foot just for the panels. It is the gold standard, you get even heat with low heat capacity and quick responsiveness. There are lots of ways to install a heated floor, the question becomes whether you can get equivalent results with cheaper materials.

    When working with heat pumps you really want to keep the water temperature down, it's the key to efficiency. Which means you really want an even floor temperature, which means you want something highly conductive under the floor. With Warmboard it's a continuous layer of aluminum.

  • hot_rod
    hot_rod Member Posts: 25,011

    Warmboard us a structural panel so it serves a double purpose. In some cases I think you can widen the joist spacing since it is 1-1/8” plywood, maybe save some framing bucks

    Noticed where I routered across the panel and cut out the aluminum layer. It shows the power of the continuous aluminum conduction

    The back 1/2 of this sheet has carpet over it

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mjkatsaros
    mjkatsaros Member Posts: 5

    Wow thanks so much for all that. Incredibly helpful. I really appreciate it very much.

    I looked up where the Sonoma County NOAA weather station is that provides those temps, and it's much further inland from where I'll be. Within the county, temperatures can vary quite a lot, especially if you're close to the coast like this cabin will be. Being so close to the ocean, the weather is much more temperate - lows are not quite as low and highs are definitely not as high as most of the inland part of the county. This site (https://weatherspark.com/y/360/Average-Weather-in-Sea-Ranch-California-United-States-Year-Round) has the average annual lows closer to 40 and highs closer to 75 (it's hard to imagine it getting to 103 ever; but definitely not an average yearly high). There is most often strong winds or at least some breeze coming off the ocean, so even on the few days it heats up, I'm banking on being able to open the window and being just fine (and as soon as the sun goes down it cools down significantly if you're coastal). Anyhow, that's all to say that those numbers are super helpful and should be a fairly conservative estimate for what I'll need.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,821

    Hi @mjkatsaros , I'm a fan of making the shell of the house really efficient so the heating/cooling is easy. As you're in planning still, have you looked at building with SIPS (structural insulated panel system)? Done right, they can be quite fire resistant, and are far better in earthquakes than normal stick framing.

    I'm familiar with the coastal Sea Ranch area and it is tempered by the ocean, with some wind as the cypress trees show you. I don't remember any buildings there having AC. Overhangs and a light roof are probably all you need for cooling. Are you planning on having a wood stove as backup?

    Yours, Larry

    GGross
  • DCContrarian
    DCContrarian Member Posts: 1,117

    Ultimately it's going to be your local building official that decides.

    My understanding is that California has a strict energy code, Title 24. It's not the same as the code used in the rest of the country, it divides the state up into zones. Before proceeding any further you should check in with your local officials and find out what they're going to want from you, both in terms of insulation levels and system sizing. This is something your architect should have already done but they don't always do, they often want to leave it to the HVAC sub and insulation sub. What you don't want to do is go down the road and find out that something that would have been an easy fix in the planning stages is now a big problem.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    I don't think a wood stove is going to be a good match for this cabin. The heating load is tiny, it's going to be hard to run a fire without overheating the building. The local code is going to require them to build it tight which generally isn't a good match with wood burning. And a wood stove is going to take up a lot of space, which is at a premium in this design.

    And why are people always looking to install backup heat with electric? Do you install backup heat with gas? Backup heat just creates more problems than it solves.

  • mjkatsaros
    mjkatsaros Member Posts: 5

    Good point about Title 24. I’ll be sure to see if I can find that zone information as we continue our design. As part of the process for developing our permitted set of drawings, we are required to hire a certified energy/title 24 consultant who does a full energy analysis on our proposed design. So insulation and building envelope will be determined and assessed by that point.


    We are going to have a very small wood stove. I agree it will make the place quite hot when it’s running, but this area is prone to frequent and, at times, prolonged power outages.

  • hot_rod
    hot_rod Member Posts: 25,011
    edited January 22

    Here is the woodstove I have in my camper. I heat and cook on it with scrap 2x4 wood, free at most any joibsites. The inventor developed it for sailboats, as he struggled to find a good quality stove for this own boat.

    It burns very clean with a bit of a gasification section in the design.

    It's about 12" square, takes up little room.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingarten
  • DCContrarian
    DCContrarian Member Posts: 1,117

    That actually looks pretty cool.

    The picture says "certified," do you know if it is EPA-certified and UL-Listed? We can't install if it's not. Insurance company is even pickier.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,821

    Hi, If you do go with a wood stove, make sure it's designed to be able to use outdoor air for combustion. That way you're less likely to cool down other parts of the house and less likely to have smoke in the living space.

    Yours, Larry

  • LDT
    LDT Member Posts: 5

    Hi: I have a hydronic radiant floor in a 980 sf house and I absolutely love it. I was pressured to go with mini splits but I didn't want the fan sound and also — there's nothing like a warm floor. Of course, I'm in New England (-8 last night) so in CA you could easily get away with (what should be) less expensive mini splits along with a WELL INSULATED floor. Depends on what you want to feel and hear.

    One more detail: I have two neighbors who had hydronic piping installed in certain areas, but not connected; they both later went through sticker shock re: the cost of a boiler. In the end, both installed simple electric DHW tank type heaters, as they each had enough excess solar PV production to supply the kWh. And they're both very happy. They got a plumber to install the water heater (after some persuasion). Much simpler and easier than trying to modify a heat pump DHW (with all its pre-programmed control algorithms) to this purpose.

  • DCContrarian
    DCContrarian Member Posts: 1,117

    "Much simpler and easier than trying to modify a heat pump DHW (with all its pre-programmed control algorithms) to this purpose."

    A heat pump water heater is completely unsuitable for space heating. It takes heat from within the conditioned space, it's like trying to build a perpetual motion machine.

    An air-to-water-heat pump takes heat from the outside air.

  • hot_rod
    hot_rod Member Posts: 25,011

    I see they have added some accessories for the Cubic minis. A little water tank for making boiling water and a grill attachment.

    Mine has a pipe connection at the air intake. I guess it could get air from outside. I like to crack a window regardless. And keep the CO detector running.

    I have one of the heat motor fans also to help dry clothes in front of it.

    I visited the factory years ago when I was in Montreal doing trainings. Nice people.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,821

    Hi, I like that last photo. It's essentially a modern range boiler, with no pressure. Some old cast iron kitchen stoves had a similar hot water tank. Simple and effective 👍️

    Yours, Larry

  • DCContrarian
    DCContrarian Member Posts: 1,117

    From the website it looks like the stove is UL-listed but not EPA certified.

  • TeddyHertel
    TeddyHertel Member Posts: 10

    Hi there. You’re definitely on the right track. I just finished a radiant install on my own house (2k sqft) and it is by far the best way to heat your house. We are in coastal Humboldt county so similar climate. We used Ecowarm panels on top of the plywood subfloor, under Fir wood flooring. Gas boiler but eventually prob switch to heat pump. Ecowarm is way cheaper than warmboard and essentially the same thing (sorry if I’m making anyone mad) but they both do the same thing. I’m now working on another radiant project for an ADU that specs out a heat pump radiant/dhw system and is seems sweet. I’ll attach the plans they gave me from the rep. Good luck and you definitely came to the right place for info, some knowledgeable folks on here. Cheers

  • Patrice
    Patrice Member Posts: 2

    Ha ha. You think 900 square feet is small. That's twice as big as a few condos I have had in Cambridge.

  • Teemok
    Teemok Member, Email Confirmation Posts: 760
    edited January 30

    It's been a long time since I've done a radiant floor with full dimension wood floor. He wants to use self-milled* cypress. Stable enough but soft (insulation*). Fast recovery* is usually desired in vacation spots. Small floor area* with a fair amount of glass*. wind* and fog* are of residence. I'd pad up any load calcs. This is not just an 1:45 away* it's also an edge of the continent elevated driving risk*. Small project* budget?* Mechanical space*? I'd like 6" spacing with a thinner harder surface to know it will deliver heat fast and even. Masonry,tile, stone. The first thing that came to mind was a masonry strip area under the glass tall ceiling area's. This would allow for higher SW temp without wood damage worry and give fast recovery. I Like DC's small focused area but I think he was thinking about better foot feel and a window strips isn't that. High capacity forced air convectors run at low temperature straight to HP? Dry pack between sleepers over foam with omega aluminum ? There's a lot of asterixis above. I'm afraid my price would be high. I'm still thinking about it Matt. I have to recheck with building department about me doing an A@WHP with my C-4 class license. They had no objections last time but ya never know with changing bureaucracy.

  • mjkatsaros
    mjkatsaros Member Posts: 5

    Do folks here recommend Arctic atwhp systems? I’m not in an especially cold climate but it seems like a nice system at first glance