New Crown boilers - updated piping
redheadgenes
redheadgenes Member Posts: 43
edited January 2025 in Strictly Steam
Hi all
I received a great deal of help on this forum via this post
Let me know if I should have added these pictures/this updated question to that post, but because the feed got so long I thought I would restart.
I had my plumber come back and install new main vents - he didn't admit to wrong doing but he didn't argue with me and I didn't pay. Thank you so much to members of this forum who caught that he had not installed new main vents - this was even in my quote, and he didn't do it. He still installed them weirdly. See pictures.
Boiler 1 apt is working fine, it is not losing water. Still, piping looks incorrect. Plumber said "this was also an ok way to install." I am worried this will mean it will fail early or cause other problems. I think based on the book (which i now have) this install will cause energy loss.
Question: Should I make him reinstall while I have his labor under contract?
Boiler 1 picture here:
Next question…
Boiler 2 is losing water - that was the subject of my original post. It is still losing water, needs to be refilled every 5-6 days. Replacing the main vent didn't seem to do anything for that.
Boiler 2 pictures here:
Question: is this main vent set up potentially contributing to water loss? Either way, would you have the plumber redo it (same question as above).
Meanwhile I am replacing vents and looking at valves in boiler 2's apartment, given advice in the last post, as a potential source of water loss. I want to know if these main steam vents should be repiped.
So far I have replaced 3 vents (out of 7) and that hasn't seemed to help much.
If the main steam vent is fine, and I replace all the vents/valves, and I still have water loss, I will look at hiring a better steam pro to come in with a thermal camera. Other ideas let me know. Thankful to this community
«1
    mattmia2 Member Posts: 16,672
    did you flood the boiler to look for a leak above the water line? Is the return for both essentially the main sloping toward the boiler and dropping down at the boiler, is that all the piping that there is?
    The vent looks a little unconventional but fine(although others will have to comment on the size).
    We need to see pictures of what happens to the return at the base of the boiler, there are a couple important piping details in how that is done.
    Try looking around with a mirror and see if it fogs the mirror at valve packings and unions and such if flooding the boiler doesn't show a leak.
    Also check the manual and make sure it says you can use only one riser on that model boiler. I suspect it will say you can on that small a boiler but you should check that and the pipe sizes against the manual.
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    The main vent setup is excellent to provide a lot of space between any water and the vent.
    The vent itself, however, is a bit questionable. Cannot determine the size from the photo but it doesn't appear to be typical of a main vent.
  • delcrossv
    delcrossv Member Posts: 2,203
    That's a tiny main vent. Should be a Gorton #1 minimum.
  • geemalar
    geemalar Member Posts: 98
    edited January 2025
    Likely because I don’t understand what type of system this is, but I thought the main line vent was supposed to be at the end of the main. Is that not the case?
    Edit……
    I now see that these are the return lines, I did not see that when I first looked at the pictures.
    EBEBRATT-Ed Member Posts: 20,145
    The piping looks ok based on what we can see as far as configuration goes. The pipe size will have to be checked against the manual.
    Vents probably not large enough. Did he skim the boiler?
  • redheadgenes
    Thanks to all. For clarification I have a 2 family house, 2 separate gas fired 1 pipe steam systems.
    Here are better images of boiler 1 piping:
    Here's a closer picture of the main vent. It doesn't have a brand on it.
    Steamhead Member Posts: 18,465
    Looks like they bought the cheapest vents they could find. That one came from Home Depot.
    How long are your steam mains, and what pipe size? This determines the vents to use.
    Consulting
  • redheadgenes
    Here are pictures of boiler #2 piping
    edited January 2025
    I'm not sure about the pipe size for the second boiler but I think it is just something weird about the perspective from the angle of the pictures.
    with all that extra dope everywhere it will definitely need skimming a couple times.
    What is happening here:
    Does the riser from the boiler go in to a tee and the main goes off in 2 directions? what happens at the other ends of the mains? If they join in to a return then that return needs to be below the water line to keep steam from one main from going in to the other main and keeping one of the mains from venting.
    Long Beach Ed
  • redheadgenes
    edited January 2025
  • redheadgenes
    Thanks
    Should I measure the pipe that is coming into the radiators? I don't know the steam main length. What is the best way to estimate that? Based on the home depot info alone (I reversed image searched it - looks like its from Lowes) I can complain as his quote specified Hoffman main vent (no specified size). This was the second call back - the first time, this plumber left old radiator vents on the main. Does the piping look ok or have I been taken to the cleaners? Mixed results about piping on this feed.
  • redheadgenes
    I am confused by what you're asking but I will provide further pictures. Thanks
  • redheadgenes
    Skinny pipe off end of main I think. Looks wrong to me. Plumber said it was "fine to do it this way."
    What happens here? Is there a tee here?
    No, just the mains, starting at the boilers and ending at the vents.
    Consulting
  • redheadgenes
    edited January 2025
    No it doesn't connect at all to the insulated pipe as you've drawn it. does that make sense? If you're talking about the pipe with the main vent on it.
    are you talking about the pipes behind the main vent in this picture? (partly insulated pipes) I can take another picture
    delcrossv
    not the return, that is the pipe with the vent on it. the pipes where the steam supply comes from the boiler and distributes around the building. if there is only one return it should only go in one direction.
    redheadgenes
  • redheadgenes
    Ok thanks - will take another picture and post it later
  • dabrakeman
    dabrakeman Member Posts: 1,001
    I think it is the T at the top of this photo that is being questioned. Are they both mains feeding multiple radiators or is one a takeoff to a single radiator and the other the main that goes around the the whole basement ending at the new vent? Neither situation would be ideal but they should not come back together anywhere above the waterline.
    Measure the OD of that pipe going to the new main vent and then check an online schedule 40 pipe chart to see the nominal pipe size. You will want to do the same on the main to answer Steamheads question. For main lengths you can just pace off and it is close enough.
  • redheadgenes
    They look like they are both mains feeding multiple radiators. The main vent is on a pipe headed in another direction. I am confused - apologies. I can send further pictures but maybe this is where I need advice from someone in person. Does this piping look dangerous or like I should take this plumber to the business bureau? I think it's clear the main vent is too small
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,833
    As far as water usage, that problem is likely the result of leaks upstairs on radiator valve stems and unions, and - let me guess - the plumber never looked upstairs. You may want to flood the boiler up past the top of the gauge glass just to make sure it's not leaking in the steam area. Who knows? Maybe the installer threw it off the truck.
    The tee connecting the mains of course is bad practice. Each main should be separate takeoff from the header. At least the first one off the header should enter the header at 45-degrees. The use of Chinese malleable fittings instead of cast fittings is indicative of poor workmanship, as is the sloppy application of pipe dope everywhere. This guy couldn't even put down a couple of concrete blocks to get the thing off the ground??
    There's no excuse for the use of $5 Home Depot radiator vents on the mains, but it's no surprise considering the overall quality of the work. I'd be remiss to not comment on the unsupported PEX feed line to the boiler. That would fail the most liberal inspection around here.
    I would request that this installer pipe each main supply separately from the header, (the first at 45-degrees to the header), replace the PEX with rigid pipe or properly support it, and replace the vents with (at least) a Hoffman or preferably a Gorton main vent as he was contracted to provide.
    ethicalpaul Member Posts: 8,741
    edited January 2025
    No it's not dangerous. It's nearly correct. You are not going to get anywhere with any customer protection agency regarding this, nor with the local inspector (by the way, did your installer pull a permit and get it inspected?).
    The vents are indeed main vents, they are just not very good. It would be a better use of your time to purchase a couple new vents yourself and ask this guy if he would be willing to install them or hire even a handy person type person to do it. Or you can do it yourself if you are handy.
    Edit: my words above are moot if the situation described in the messages below is accurate. I was speaking about the main vents on the boiler in the photo just posted
    there is a different issue here. either the mains are improperly tied together at the other end or there is nowhere for the condensate to return for one of the mains. this issue was created by whoever split up the floors in to 2 boilers.
    delcrossvLong Beach Ed
  • delcrossv
    edited January 2025
    Yep. Where is the end of the main that has doesn't come back to the boiler?
  • redheadgenes
    Thanks. I don't understand enough about this to know if this is what is happening. I have looked at the near boiler piping in the book but I'm confused. Would it make sense for me to take a video of the set up and post it here?
    This boiler (boiler 2) is not having water loss issues or any other issues really, it is heating its apt fine - but clearly the main vent is cheap and bad. In terms of what you describe with the mains being improperly tied together / or nowhere for condensate to return — what kind of problems does this cause or would it not cause problems until later?
  • Long Beach Ed
    What is being said is that it appears the riser splits into two mains with that big tee. Each main needs a way to drain the condensate - water - from it. Usually mains slope away from the boiler and at the end they drop down to a return that runs back to the boiler. But a main can instead be a counterflow main, which slopes back to the boiler and drains its condensate back to the source against the steam flow.
    We're trying to figure out what you have here, and knowing what's on the end of the mains would tell us.
    The "Improperly tied together" assessment regards the use of a tee to split steam into two mains. Proper practice dictates that each main should be connected separately to the header. Using a tee for this purpose can cause some problems as could connecting a counterflow main into an undersized pipe serving two mains.
  • dabrakeman
    The "improperly tied together" supposition is also referring to what is or may be happening at the far end of the mains. We are hoping that the two mains do not join each other at their far end resulting in only the single main extension (return) shown back at the boiler with the main vent attached. IF everything is heating fine and balanced then perhaps we should not worry about this boiler and instead only focus on the water loss of boiler #1. Just for my understanding boiler 1 and boiler 2 are wholly independent, not sharing any piping, right?
    Long Beach Ed
  • redheadgenes
    edited January 2025
    This is all really helpful, thank you so much. I will show this discussion to a proper steam guy when I eventually have to get one in.
    FWIW boiler 1 is heating ok and the system is relatively balanced - it's a bit imbalanced (one side of the apt getting hotter/ quicker) but I don't have adjustable vents on everything. in general it's heating ok and is comfortable. I had to fill the boiler after about 6 weeks of daily-ish use. According to the boiler manufacturing, that is ok as far as water loss.
    Note: I looked at the manual and it looks like this model (both boilers are the same) has an option for a single riser. I have attached the manual picture below. That might be the T in question? Although I'm unsure.
    Boiler 2 is independent (no shared piping) and needs water every 6ish days. Manual specifies water should not be added more than once a month.
    It seems like at least this plumber specified a gordon main valve in his quote and didn't put that in. A cheap main vent will fail early correct? I paid for quite a bit of this on my credit card. If he refuses to change the main vent or doesn't respond, I could get a quote from a better steam guy, and contest the amount of that quote against the original plumbers charge on my credit card. Unless people in this group think this is a bad thing to do. I texted the plumber who put in the bad main vent once already about this and he has so far not responded. I will continue to ask him to make it right but I may have to go the credit card route.
  • redheadgenes
    Here's the single riser set up for this boiler:
    The single riser refers to the boiler to the header, not the header to split mains. If it is balanced and doesn't hammer it might be ok.
    The risk of the mains being teed together is that one side might heat before the other in some cases so much so that it can't be balanced.
    The risk of the returns being tied together above the water line is that steam in one will reach the vent first and close it stopping the other main from venting and making that main heat more slowly.
    delcrossv
  • delcrossv
    It's the combination that makes it unworkable. A teed supply with separate drops to the wet return is balancable. Not easily, but doable. If they're connected at both ends above the waterline, steam will take the easy path.
    He's probably done with you. If he specced a Gorton and put in that thing then yes, that was bad practice on his part. If you do a chargeback, you'll never have him as a plumber again (which might be a good thing). The Gorton would cost him about $45, the one he put on was probably under $20.
    To me that's "walk away money" but maybe not to you, I can't choose for you.
    redheadgenes
  • dabrakeman
    I'm still confused as to whether:
    1. You know what main vent size you needed which requires an estimate of the total mains length and pipe size and:
    2. Whether relative to the water loss you went around and did what @ethicalpaul asked in the last thread:
      To see if vents are working, you set up a long call for heat, like make the system have to gain like 5 degrees. Then you run around to all the radiators to see if they are filling with steam. That tells you the vent is letting air out like it should.
    Then you keep running around to all the radiators until they start to completely fill up with steam all the way to the vent. When steam gets to a vent and makes it "steam hot" the vent should close and not allow any steam to escape. You can hold a spoon in front of the little hole in the vent to see if it's letting out steam.
    Also check the valve (note the difference between a steam vent, and the radiator's valve that has a handle on it) to see if it is leaking, hissing, or dripping.
    You don't want to see any hissing, fogging of the spoon, or dripping anywhere because you should only be having to add like a gallon per month to these boilers.
    No doubt to me if Gorton is spelled out in the quote a Gorton should be installed. I assume based on your boiler size maybe a #1 is enough but perhaps it should be a #2 (much more expensive).
    In addition to the fogging on a spoon or mirror just your phones flashlight can help pickup steam release. Just make sure the last section and vent are steam hot and that the boiler is still firing when you pass judgment on the vent.
    ethicalpauldelcrossv
  • redheadgenes
    Many thanks. Re: question 1. No I'm not sure. Before I go head to head with the plumber about replacing it I will figure out what size main vent I need. I may just walk away if I don't need a large vent. However, I won't work with this guy again either way.
    Re question 2: I did exactly this and replaced 3 vents and replaced the gasket material/ tightened one valve, all based on hissing and fogging. That seemed to help a bit re water loss. But boiler 2 is still losing too much water — again, every 6 days. Today I went in and replaced the rest of the vents just in case I was missing something and tightened another valve. if that doesn't work, based on other posts on this wall it seems I need to get someone in with a thermal camera or someone who is not this plumber and is going to do a better job to identify a leak. Other thoughts, let me know.
    In terms of the teed issue - boiler 1 is working ok and not hammering. I understand that teed main and/or teed return can cause issues with balancing. I have radiators in the boiler one apt that heat up before the rest but it's not a huge issue. I will show this feed to the steam professional I get to come in.
    Did they repipe it after they installed it or is that how they installed it? As I see it they used a cheap vent and didn't fix some issues someone in the past left behind. They didn't do the best job but didn't do an awful job either.
    redheadgenesLong Beach Ed
  • redheadgenes
    Thanks, this is helpful to know re not the best job but not an awful job either.
    Boiler 2 (the one losing water) was re-piped. Then its old boiler (from the early 70s) died anyway and I had to have the boiler replaced as well. Boiler replacement didn't fix the water loss issue. The repiping job also didn't fix the water loss issue. This plumber's quote for repiping said it would fix water loss. When it did not, he told me to replace all the vents / valves, as others on this forum suggested. If that still doesn't work, I could come back to his repiping quote and point out that I still have a water loss issue.
    Boiler 1 was simply replaced. When I moved into the house, the boiler was dead on arrival (also from the early 70s). Every plumber I talked to (I got 4 quotes) said the original piping was bad. I picked this plumber after reading "we got steam heat" because he measured my radiators and seemed to know what he was doing. But then I get stuck with this cheap main vent and clearly not fixing the old piping issues, which he said he would do. I am leaning toward a charge back after consulting another steam guy on the piping job and how much fixing it will cost. I need to figure out if I need larger main vents. Thanks
  • RTW
    RTW Member Posts: 285
    Posted by OP"
    "Boiler 2 (the one losing water) was re-piped. Then its old boiler (from the early 70s) died anyway and I had to have the boiler replaced as well. "
    "Boiler 1 was simply replaced. When I moved into the house, the boiler was dead on arrival (also from the early 70s)."
    My circa 1964 Boiler operates as well as the day it was installed, though I made some improvements adding Main Vents, a better oil burner and balancing the system vents. These newer boilers look tinny to me, with a fraction of the life span of the older cast iron boilers of the past - from everything Ive read on this site. Im just a homeowner, but those Ive spoken with in the heating business say they get a bonus if they talk a customer into replacing an older boiler, notwithstanding it just needs some TLC.
    Not sure what you mean by "died" or "dead" that gives no mechanical explanation?
    This post is mostly for those with older working boilers to beware and find themselves in this OP situation
    All the Best,
    RTW
    delcrossv
  • dabrakeman
    So water loss is still the issue. I might be confused between the different threads or two different boilers but I seem to recall you saying there was a noticeable leak from the near boiler piping (on boiler 2?) after the repiping job and they had to come back out and fix that. Are you sure it is fixed? There may not be steam noticeable from the top of the stairs but have you checked the nbp locations that were leaking before in a similar manner to how you checked the radiator vents and valves? Any rusty areas developing near any of the piping joints?
    Long Beach Ed
  • redheadgenes
    Jealous of your boiler! I got 4 quotes, every plumber told me to replace. It was an expensive repair related to the wiring. The plumber who had been making small repairs to the wiring every year for the old owner told me he wouldn't work on it anymore.
    after 4 different plumbers recommended replacement, I went with that. Apparently the original near piping job was also a mess.