Air to Water Heat Pumps
John Ruhnke
John Ruhnke Posts: 1,024
edited January 2025 in Radiant Heating
Hi Everyone,
I just graduated from the Heat Geeks ATWHP engineering courses. It is three courses on ATWHPs and totals over 100 hrs. I am now a Heat Geek Heating Engineer!!
Currently I am a Designer, Trainer and Consultant for hydronic systems. I help you add a ATWHP to your existing hydronic systems.
I love to talk about ATWHP Hydronic Systems! Most of the systems I design have radiant heating. I started out as a Apprentice in Plumbing and Heating back in 1983.
I am the walking Deadman
Hydronics Designer
Hydronics is the most comfortable and energy efficient HVAC system.
Dan FoleyMad Dog_2EdTheHeaterMan
«13456
  • jesmed1
    jesmed1 Posts: 1,631
    Hi John, thanks for your post.
    I maintain a 4-unit condo building in Boston, built around 100 years ago with original cast iron radiators and gravity conversion hot water system.
    We burn 1200 gallons of oil per year in two Weil-McLain WGO-5 boilers. (DHW is from a natural gas water heater.) So our heating bill is a large portion of our operating costs.
    Because we have so much cast iron radiation, I believe we could heat the building on a design day with 110-120 degree supply water. Our heat load on design day is 80,000-100,000 BTU/hr depending on which numbers you choose. The 100,000 BTU/hr appears to be conservative.
    I did some research last year on converting to an air-to-water system. I contacted a local Massachusetts heating company with expertise in heat pump conversions, and the ballpark $$ they gave me over the phone was shockingly high, so that put the kibosh on any conversion plans.
    But I would be interested in any thoughts you might have that could make a conversion more cost effective.
  • John Ruhnke
    Proper Design and training is the easiest way to make things more cost effective.
    Hydronics Designer
    jesmed1
  • Kaos
    Kaos Posts: 1,003
    Can't be conservative when you are sizing heat pumps as extra capacity costs a lot. 1200gall should be closer to 70kBTU load which you can feed with a pair of larger AWHP units at your low temps.
    Won't be cheap, but should not be out there.
    Since you are in an area that needs cooling, your best bet is individual air to air units as these will heat and cool for significantly less money than anything air to water. Plus each unit would have their own and cover the cost of running it.
  • jesmed1
    edited January 2025
    Thanks, yes, I was thinking 2 large AWHP's, like 40kBTU each.
    Individual air-to-air units would be less costly, but the way the house is built would make it difficult to run ducts or mini-splits. So the only practical heating solution would be AWHP's.
    Maybe the most cost effective solution would be to install just one AWHP sized for 50% of design heating load, and keep one of the two existing boilers as supplemental heat.
  • DCContrarian
    DCContrarian Posts: 1,588
    "Maybe the most cost effective solution would be to install just one AWHP sized for 50% of design heating load, and keep one of the two existing boilers as supplemental heat."
    I guess it's ingrained to think that way. To my thinking, either a heat pump makes sense or it doesn't. If it makes sense then half a heat pump doesn't make sense.
    Hot_water_fanLRCCBJ
  • DCContrarian
    The two things to look out for are 1. low temperature capacity and 2. water temperature. Although you said you thought you could heat the place with 120F water.
    Is there an obvious way to split the system into two zones? Two heat pumps on the same zone would fight each other for control. If you could split it up I think a pair of five-ton nominal heat pumps would do the job.
  • Kaos
    Kaos Posts: 1,003
    Seig shows them piped to low loss header on a hydraulic sep.
    For an older gravity feed setup, I can't see why they can't be piped direct to load in a parallel without anything else( maybe a check valve and flow setter to balance). Each will supply about half the GPM the setup needs, since the RWT to both is never mixed, each unit will sense building load properly.
    jesmed1
  • jesmed1
    edited January 2025
    The heat pump efficiency makes sense, but one of our hurdles as a 4-unit condo association is the up-front cost. Owners are not going to make a huge up-front investment when they may not be planning to own here long-term enough to recoup their investment in energy savings. So a less-expensive first step that still saves some energy is an easier sell.
    Also, "half" a heat pump may end up providing more than half the BTU's in a heating season, since a 40kBTU heat pump could provide 100% of the heat on days above 35 degrees, and 50% of the heat on zero degree days. So a seasonal average could end up giving us 75% or so of our heat from that half a heat pump.
    Yes, the house is already split into 2 zones, one per side of the house, each zone serving 2 units. Hence the 2 boilers, one per zone. So my thinking was one 40kBTU heat pump per zone instead of the oil boilers. But I don't think the owners would go for the up-front cost, which is why I'm wondering if it makes more sense to try and start with a single heat pump that could probably provide 75% of the BTU's to both zones in a season.
  • DCContrarian
    "Also, 'half' a heat pump may end up providing more than half the BTU's in a heating season, since a 40kBTU heat pump could provide 100% of the heat on days above 35 degrees, and 50% of the heat on zero degree days. So a seasonal average could end up giving us 75% or so of our heat from that half a heat pump."
    It's really hard to get a boiler and heat pump to work together like that.
  • John Ruhnke
    It makes sense to use gas or oil as a back up and one HP for 50% design load. With an HBX controller you can set up the heat pump to run when it is warmer outside and with lower water temps. Then run the boiler at higher temps when it is colder outside. During those conditions the SCOP will be much higher on the HP. You could average 4 or 5. That means 400 to 500% efficient. While using a Heat Pump for full load might deliver a SCOP of 3. (Seasonal Coeffient of Performance)
    Hydronics Designer
    jesmed1LRCCBJMad Dog_2EdTheHeaterMan
  • John Ruhnke
    Hi Kaos,
    "For an older gravity feed setup, I can't see why they can't be piped direct to load in a parallel without anything else"
    The HP needs a delta tee of 10 and the radiant heating usually is designed for a delta tee of 20. Anyway the HP needs a lot of flow through it without extra resistance. The HP pump is bigger than the system pump. That is where you need a low loss header.
    You can design a system to operate with one pump. But you will have to size the pump properly to handle the flow rate through the HP to a delta tee of ten and handle the resistance through both the HP and system. You would use TRVs that reduce the flow but never fully shut off to regulate the zones. If you do it this way you can have a system with a very High SCOP of over 4. You would do either Outdoor or indoor reset to run the pump all the time.
    Projects with lots of zones or where piping already exists and you don't want to rip up walls to repipe require a buffer tank to balance the system out, prevent short cycling separate out the flow to the HP from the flow to the system.
    John
    Hydronics Designer
  • DCContrarian
    edited January 2025
    "With an HBX controller you can set up the heat pump to run when it is warmer outside and with lower water temps. Then run the boiler at higher temps when it is colder outside. During those conditions the SCOP will be much higher on the HP. You could average 4 or 5. That means 400 to 500% efficient."
    Right, that's pretty easy to do. But that's not what Jesmed1 was talking about. He wants the heat pump to run even when it's cold, but if it doesn't have the capacity then the boiler "helps" it out.
    My point is that the only reason to do that would be if at the cold temperatures the heat pump is cheaper to operate than the boiler, but it just doesn't have the capacity. I argue if that's the case you're better off just having a heat pump that has the capacity you need and running it all the time.
    There are heat pumps that have a boiler control output, to run the boiler only when the heat pump can't keep up, I know US Boiler makes one. What I don't know is whether they truly run the boiler only as much as needed and let the heat pump run as much as possible.
  • John Ruhnke
    edited January 2025
    To DCContrarian:
    "He wants the heat pump to run even when it's cold, but if it doesn't have the capacity then the boiler "helps" it out."
    You are right in thinking the control is either using the boiler or using the Heat Pump.
    With the HBX I can set up the system to do what Jesmed1 wants just a little differently. 75% or so of the heat from the Heat Pump. Most heat emitters are very oversized. With oversized heat emitters the max temp can be set lower than most people think it is capable of doing. Also our R32 unit can run at 140F now.
    Hydronics Designer
  • jesmed1
    edited January 2025
    How does the plumbing work to get the boiler and the HP working together simultaneously on a design day to heat the same zone? I'm a beginner here, so I'm just learning, but I was imagining something like a primary/secondary with both the boiler and the heat pump on the same primary. On a milder day, the controller would have the HP only feeding the primary. On a colder day, the controller would have both HP and boiler feeding the primary.
    But I suspect there's going to be some sort of water temperature mismatch problem with that concept. I imagine that's the difficulty @DCContrarian was referring to. Maybe the answer is some sort of buffer tank arrangement with a heat exchanger.
    Mad Dog_2
  • John Ruhnke
    Jesmed1,
    You can't run both the boiler and the heat pump at the same time. You can run both in the same day. The Heat Pump might run during the day and then automatically switch over to the boiler when the temperature drops after dark and when the next day comes the boiler switches back to the heat pump when it warms up outside. You can have the Heat pump provide 75% of the seasonal load and boiler provide 25% of the seasonal load.
    Its not an exact science though there are variables. Some years are warmer, some colder than others. Some systems ending up being oversized, some undersized. You can design for a 75% seasonal load from the HP and 25% from the boiler. That is easy. But the actual conditions that vary will determine the actual % split that occurs.
    Its fully automatic once it is set up. But you can tweek it. Suppose the price of oil drops and is suddenly $1 a gallon. You can switch the controls to run more or even 100% from the boiler. You can also adjust the controls to rely on the HP more often if the price of oil goes to $10 a gallon.
    Hydronics Designer
    jesmed1Mad Dog_2
  • John Ruhnke
    The Heat pump and boiler run off of a outdoor reset curve on the HBX. They keep the buffer tank at the proper temp. The reset curve maintains the right temp in the buffer tank. If it is 5F outside and the system design temp needs to be at 170f then the boiler is running to 170f. Once it warms up to say 10f ODT then it runs the buffer at 160f temp. Lets say at 25F ODT it needs 140f. The HBX control then switches to run the Heat Pump and the Boiler turns off. Now the heat pump maintains the buffer tank at 140. now it warms up to 50F and it runs the HP to maintain 110f. Then it gets colder, 30f and the HP runs at 135f. 25 ODT and the HBX switches from the HP to the boiler to maintain 140 in the buffer tank. Temp drops to 10f ODT and the boiler runs at 160f to maintain boiler temperature.
    Hydronics Designer
    jesmed1Mad Dog_2EdTheHeaterMan
  • jesmed1
    OK, thanks John. I see Arctic already has our system designed. 🙂 I like the flexibility of that dual-source concept, because as you say, you can adjust the how much you rely on either source depending on current energy prices, and also because of redundancy in case one source fails.
    Hot_water_fan
  • John Ruhnke
    edited January 2025
    I am the manufacturers rep for Boston. That lead will be coming to me. Unless it was completed before March of 2024. Then it could have gone elsewhere. I started full time in March. Was working part time since 2021 for Arctic.
    Hydronics Designer
    Mad Dog_2
    hot_rod Posts: 28,708
    90° SWT on a 45° ambient for me to get 4 COP on my Viessmann system. Are those typical design conditions in the UK? It seems panel radiators are the main type of heat emitters over there.
  • John Ruhnke
    Heat Geeks use oversized heat emitters to deliver really low temperatures. You can do that with our AHU units, Fan Coils, Radiant Heat or Radiators. Just size everything for low temps.
    Hydronics Designer
    must be massive radiators to work at 95 or lower swt. Got any pics?
  • DCContrarian
    I'd like to offer an analysis, the data is in a spreadsheet at
    https://docs.google.com/spreadsheets/d/1KmnOjq_MEQ2fNqj5AZvLSXHkNx3dwDPvn_SNBV2iHMA/edit?usp=sharing
    @John Ruhnke had sent me a performance sheet for the 5-ton Arctic (050ZA(BE)) I used that for performance curve of COP and output vs. outdoor temperature. I used weather statistics from Boston Logan Airport for the hours per year at each temperature. I assumed an electricity cost of $.27 per kWh and an oil cost of $3.50/gallon, maybe someone closer to Boston can check those for me. I assumed 80% efficiency for the oil burner.
    I modeled a building with a heating load of 35,000 BTU/hr at a design temp of 13F, based upon the discussion above.
    I calculate that this building needs 80,115,978 BTU of heat for the winter.
    To get that 80 million BTU using fuel oil would take 731 gallons and cost $2558 per year.
    To get that 80 million BTU using only the heat pump, and supplementing with resistance electric when the capacity of the heat pump is insufficient would take 8471 kWh and cost $2287 per year — savings of $271 or 11% over oil.
    I then modeled three other scenarios:
    Scenario 1 is the oil burner is only used to supplement the heat pump at times when the heat pump output is insufficient, basically the oil burner is used instead of resistance electric. This saves $24.33 per year compared to the all-electric scenario.
    Scenario 2 is the oil burner is used for all heat when the temperature is so low that the heat pump costs more to run than a boiler. In this scenario, the break-even temperature is 10F. This saves $34.18 per year compared to the all-electric scenario.
    Scenario 3 is the oil burner is used for all heat below a certain temperature where the heat pump is assumed to be unable to produce hot enough water to meet the heating need. I used 25F because that was what John had assumed in his hypothetical. This saves $21.92 per year compared to all-electric and $293 per year compared to all-oil.
    Some conclusions: in this climate, for this building, a heat pump will save money compared to an oil burner. But it's modest, 11% of annual fuel cost. It's probably only worth considering when the boiler is due for replacement anyway. Other improvements, like weather-sealing and regular maintenance of the boiler, may be more cost-effective ways of seeing savings.
    The payback period of any scheme to combine a boiler and heat pump is going to be decades if not centuries. If the existing radiation is insufficient to meet the heating load with the temperature water that a heat pump is capable of producing, it's hard to justify a heat pump for part of the heating load, you're better off sticking with the boiler. Alternately, it may be worthwhile either to increase the radiation or improve the weather-sealing in the building to the point that a heat pump becomes effective.
    I welcome criticisms of my methodology. Some notes on that. First, I came up with 731 gallons of fuel oil used per season for my hypothetical building, which is significantly different from the 1200 gallons that was reported. So something isn't being accounted for. Is the boiler also used for hot water?
    I am probably over-estimating the amount of electricity used by the heat pump. I set up my spreadsheet for air-to-air heat pumps, which provide part-load capacity and efficiency numbers. Arctic only provides full-load numbers, and heat pumps tend to have higher COP at lower loads so actual COP is probably higher than what I'm seeing. Also, I'm assuming a constant water temperature of 122F, in reality outdoor reset would be used which would give better performance at warmer outdoor temperatures.
    But I don't feel that any of those issues affect the conclusions.
    John Ruhnkebjohnhyjesmed1tim smith
    nice data, thanks
    What type of heat emitters would be use with 122 SWT.
    How would you get to the 4 plus COP that Heat Geek claims?
  • John Ruhnke
    I talked with Glyn Hudson the founder of OpenEnergyMonitor.org. He is the one who recommended I take the Heat Geek courses. This is a video showing him retrofitting a house with a system. It is a complete install including heat emitters.
    https://www.youtube.com/watch?v=bHsp7fDw_bg
    Hydronics Designer
  • John Ruhnke
    Glyn Hudson and Adam Chapman over in the U.K are the geniuses that put all of this together. I am just the student. I am on my way though.
    That is how you start down the path to over 4 SCOP. If you have a project in mind I can work with you and help you get there.
    Hydronics Designer
  • DCContrarian
    "What type of heat emitters would be use with 122 SWT."
    That comes from @jesmed1 in the first response in this thread: "Because we have so much cast iron radiation, I believe we could heat the building on a design day with 110-120 degree supply water." I'm just assuming that he's correct.
    "How would you get to the 4 plus COP that Heat Geek claims?"
    From what I've read, there really isn't much more to it than having lots of radiation and really low water temperatures.
    Note that they're claiming SCOP, seasonal COP, which is normalized to exclude the effect of climate and not directly comparable to the calculated COP I'm showing.
    Apparently guys who are really good at it get SCOP's in the 5.5 range. This article has some details:
    https://arstechnica.com/science/2024/07/the-hunt-for-the-most-efficient-heat-pump-in-the-world/?fbclid=IwY2xjawH2VwlleHRuA2FlbQIxMQABHfKALOmCjmEXQAGBtiNnsnbf-oHDPA7H6uxXmaPQyAuTPi4CPuwMTkgKpw_aem_Oq4kXweijwakCFct0PrJFA
  • John Ruhnke
    edited January 2025
    When I was a kid, early twenties I wanted to be a pro race car driver. I rebuilt a car engine back then with all the bells and whistles that made it fast!! I discovered my true passion!! I liked building the race car and tweeking it for speed better than actually racing the car. When I discovered radiant heating I fell in love with tanks, pumps and pipes!! Now all I want to do is build the best performing Heat Pump out there. The Brits are way ahead of us wet heads right now. Just as I was sure I could build a amateur race car and win a championship. I won the SCCA NARRCC road race championship in 1988. I am sure us Americans can build the worlds most efficient HP system and beat out those Brits!!
    The Competition is on!!
    Only problem is I am broke. Spent all my money funding the Business Start Up, Hydronic Systems LLC. Can't afford to do my house now. But I am sure I will find a interested client. It might take a few years to hone my skills but I am sure I will get there!! OR WE!! will get there.
    Hydronics Designer
    jesmed1Mad Dog_2
  • jesmed1
    Thank you, that is fabulous. You just did a way better job of what I should have done to start with!
    I think your analysis is excellent and offers me the surprising result that heat pumps would not save us nearly as much as I expected. The key parameter is the "break even" COP of 2.48, which is much higher than I would have expected. I figured we'd get a seasonal COP average of somwhere in the 2-3 range, and your analysis shows that, in fact, a seasonal COP in that range is not going to save us much. Which is surprising to me.
    Just to clear up any ambiguities in our numbers, for our 4-unit condo building, we have:
    4800 sq ft
    1200 gallons oil/yr
    Design heat loss at zero degrees: 80,000-100,000 BTU/hr
    (I like to use zero degrees which is lower than the standard 9 degrees in my area, just to be conservative).
    The design heat loss numbers are based on actual oil consumption from boiler run times at various outside temps, the Green Building Advisor method for calculating heat loss based on actual oil consumption and recorded HDD's for a cold month, and various other methods. All methods end up somewhere in the 80-100kBTU/hr range.
    None of that changes your conclusions. The house is split down the middle by a demising wall, with each half heated by its own boiler. So the 35,000 BTU/hr heat loss number you used is about what one half of the house uses, and the 700 or so gallons of oil you derived is a bit more than what one half the house uses. So we would just double your numbers to get the results for the entire house.
    But your bottom line finding that a heat pump would not save us as much as I expected is, I think, correct. So thank you for that excellent analysis.
    DCContrarian
    Id like to find out which Viessmann product they are talking about in that link 5 COP??
    To get 5 COP on the VitoCal it would be 95 SWT with 68 ambient?
    I don’t even start my system until it is 65.
  • DCContrarian
    "the 700 or so gallons of oil you derived is a bit more than what one half the house uses."
    DUH! I had completely forgotten that I was only doing half the house!
    jesmed1
  • DCContrarian
    "But your bottom line finding that a heat pump would not save us as much as I expected is, I think, correct. So thank you for that excellent analysis."
    The numbers that I have the least confidence in, and have the biggest impact on the conclusion, are the cost of oil and electricity.
  • jesmed1
    You are actually quite close. We were paying $3.50/gal until last week, when the price started to trend up. Not sure what our current electric rate is, but Google AI says the current average in MA where I live is 33 cents/kWh.
  • DCContrarian
    At 33 cents and $3.50 oil is cheaper.
    jesmed1
  • jesmed1
    Ummm….wow. Well, that saved me a lot of wasted effort. Thanks!
  • JakeCK
    JakeCK Posts: 1,502
    I've kicked around the idea of a A2W HP for a few years now. I wonder how the math would work for me...
  • DCContrarian
    It's not a simple calculation, it's not something you can apply a rule of thumb to.
    It depends on your location, both for the climate and for the local cost of energy. It depends on the house, both for the heating load of the house and also for the existing radiation. And it depends upon the choice of heat pump.
    It's probably best to start a new thread, but if you gather:
    1. your zip code
    2. The cost of electricity where you are in cents per kWh
    3. The cost of your existing fuel, whatever it is (or your preferred fuel)
    4. An estimate of your house's heating load, using this method:
    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
    I can create a spreadsheet for you comparing like the one above. I'd do it for the Arctic because that's what I already have the performance curve for, I don't believe that any of the heat pumps on the market right now have radically different performance curves.
    The other practical question would be whether your existing radiation could support your heating load with the kind of water temperature a heat pump is going to provide, around 120F. If not you would have to add more radiation.
  • Kaos
    Kaos Posts: 1,003
    One thing to keep in mind, you can always make your own power for AWHP, can't do that with oil or gas.
    Utilities have to be careful charging that much for power. At $0.33, PV has a pretty quick ROI even just to offset regular use.
    DCContrarian
  • JakeCK
    JakeCK Posts: 1,502
    This weekend ill try to find time to gather all the info up.
    a friend of mine has a PV business. He bought a container load of modules for $.20/ watt He claims he could fence his property cheaper with modules than wood fencing!
  • JakeCK
    JakeCK Posts: 1,502
    I wonder how my city would feel about me replacing my fence with solar panels. Lol