Excited about Boiler Design

13»

Comments

  • hot_rod
    hot_rod Member Posts: 24,202

    there is also an ECO built into the WH control, energy cut off, high limit control. I would not reuse that device!

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mknmike
    mknmike Member Posts: 167

    thank you! I ordered that hole saw, and it should be here tomorrow.

  • jesmed1
    jesmed1 Member Posts: 931
    edited January 15

    Great, you'll be cutting through your old brick like a hot knife through butter.

    Hardest part is just getting the bit started, because it will want to wander. You may need a simple guide to hold the bit steady as it begins to bite. I would take a piece of scrap plywood and cut a 3-1/2" circle out of it with a jigsaw. Then fix it in place on the brick wall, either by wood screws into the sill plate above or by Tapcon masonry screws into the brick. Once the bit starts cutting, it becomes self-centering and you can remove the guide.

    I also like to have a 5 gallon bucket partially filled with water handy. Stop occasionally to dip the bit in the bucket and knock out the brick chunks. The dips in the bucket ensure you're keeping the bit wet and cool, just in case your continuous water feed while drilling isn't reaching all the way into the hole. If you have a helper with a spray bottle standing with you and spraying the bit as you drill, that's a big help. Otherwise you need to rig up some sort of continuous auto-feed for the water onto the bit.

    Happy drilling, and show us some pics of your handiwork!

  • mknmike
    mknmike Member Posts: 167

    no plans to reuse any of the devises removed from the tank that I scrapped for $4, but I did leave them sitting out front of the garage door in case I discover some magical use for them (boiler drain Valve, pressure relief, and natural gas controls). I will probably keep them all a few years before discovering they are wasting space. Some day when all my projects are done I will need far fewer tools and spare parts laying around. Some day.

    Mosherd1
  • mknmike
    mknmike Member Posts: 167

    Hole saw bit arrived, and I need to figure out how to attach a 1.25” -7 thread drive. Maybe I can get one with a long pilot bit.

  • mknmike
    mknmike Member Posts: 167

    A little OT, but my basement is smelling like sewer gas since the water heater failure. Maybe the hot water down the floor drain sewer line or some dead animal in my basement caused it, but it doesn’t smell near the laundry room floor drain, more around the area that another above-ground cast sewer line goes into the ground. There are “french drains” around it that could be letting out gasses that are finding their way out of the ground. I don’t know. The outside ground is surely frozen right now. So maybe some dinosaur is decomposing under my house, or maybe I just have a sewer gas leak, or maybe something got wet that I’ve yet to discover. Anyway, now I’m looking to buy a sewer gas leak detector. Methane? Natural gas? I guess a natural gas sniffer might be good to have, I don’t know,

  • mknmike
    mknmike Member Posts: 167

    yes. Thank you. SDS Plus adapter in the same brand as the core saw was available for $24 and should arrive tomorrow. So, as soon as I’ve got my positions marked and the business around the holes cleaned up, I should be ready to roll. The tolerances will be tight with the 3.5”. It should work great.

    jesmed1
  • mknmike
    mknmike Member Posts: 167

    I will have to assure I have time to deal with core material getting stuck in the hole saw. I tested it on the ice in the pool today and discovered the issue. Not sure if it’s going to be better or worse with brick, but having a long chisel prepared to break up brick might need to be part of the plan. (Ice can just melt.)


    jesmed1
  • jesmed1
    jesmed1 Member Posts: 931

    It sounds like you have it set on "hammer plus drill" mode. You need to turn off the hammer by rotating the switch to "drill only." Hammering will destroy the bit.

    mknmike
  • mknmike
    mknmike Member Posts: 167

    Thank you. I knew what I had it set to, but I did not know that it would hurt the bit. I hope I didn’t already damage it on the ice. I figure that’s a safe place to be sure to keep the bit cool and probably wet too. I can certainly see how this will likely require a second person to spray with a hose while someone operates the drill, probably drilling at a slightly downward angle so there is some hope of the water getting to where it’s needed.

    jesmed1
  • jesmed1
    jesmed1 Member Posts: 931

    No, you were OK with hammering on the ice. You just don't want to do that on brick or concrete.

    Surface tension will draw water along the bit and into the hole even if it's horizontal, and you can always pull the bit out occasionally and spray directly into the hole. The brick shouldn't take long to drill through, so periodic interruptions for water spray shouldn't slow you down much.

    So I wouldn't worry too much about trying to drill slightly downhill. As long as you stay roughly level and aren't going uphill, water will reach the bit end if you keep a constant spray going and pull out occasionally.

    mknmike
  • mknmike
    mknmike Member Posts: 167

    so now that I know my natural gas water heater(s) are on their way out, I am starting to plan for a heat pump water heater in my setup. The current remaining natural gas water heater might function as a hydronic buffer tank, but it’s clear that it won’t have much life as a DHW storage tank, and it probably just makes sense to add the heat pump water heater, if anything. Planning for the room layout / space, I want to make sure I’ve got room to do this layout. Again, the heat pump water heater would be primarily used for summer water heating and just a storage tank (or emergency unit) the rest of the time.

    I’m not sure I understand the diagram below with respect to the aquastat in the tank that seems to force the tankless hot water heater to run. I guess I was expecting more of a “mixing” or just running everything through the tank either before or after the tankless hot water heater. The diagram below with the aquastat must send water back to the tankless water heater any time the water gets below some temperature. It’s nice that it also offers a bypass. So…

    • go away on vacation, shut off aquastat.
    • Come home from vacation and tank is cold. Open bypass
    • Want to plan ahead in winter, shutoff bypass and heat the tank with aquastat
    • Want to just use heat pump / electric in summer, shut off the bypass and add a bypass for the tankless water heater to be able to not use the tankless/boiler at all.

    I’m not sure how I will add an aquastat to a heat pump hot water heater, but that will likely be a requirement for my design.

  • mknmike
    mknmike Member Posts: 167
    edited January 20

    working on my layout, I’ve noticed that the higher vertical space available between joists would be better for large 3” holes, and I was planning to go out the back side of the house that has side-to-side joists. While I could drill holes and support the joists, it certainly would be my preference to not cut them. I may be looking to reduce to 2” PVC as my boilers allow for that, or perhaps using a concentric vent. Maybe even going up through the floor under the kitchen cooktop. Well, in any case, this is going to be a bit trickier than I’d thought to drill holes. The window idea might end up getting used after all. I could probably do that in a way that I don’t lose any more basement light than we’ve already lost with the driver vent taking one window pane.

    I think using 3” vent holes will be far superior, enabling me to up-size if ever needed. With 2”, I could be revisiting this mess in short order.


    Going out the foundation wall and digging on the outside of the house may be what the doctor orders here.

  • jesmed1
    jesmed1 Member Posts: 931

    Don't hack up your joists. I would do as you say and core the 3" through the foundation wall. More work to dig outside, but better to do it right the first time.

    mknmike
  • mknmike
    mknmike Member Posts: 167

    As is most of the eastern US right now, we are having some of the lowest temps in years. Lows below 10 F and highs below 20 F. I am wondering I the new boiler will be able to keep up.

    And I see my electric and natural gas bill that’s due soon just came in at $713. That’s over $20/day. It doesn’t sound as bad when you hear we have an EV and $433 of the bill is natural gas (under $15/day) with two tank water heaters, 290k BTU of total potential. I am keeping an eye on things with my concept of replacing all that with only 155k BTUs. It will be interesting to see how things come in over the next two days.

  • hot_rod
    hot_rod Member Posts: 24,202

    refer to a joist drilling guide before you drill or cut weight bearing lumber.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mknmike
  • mknmike
    mknmike Member Posts: 167

    I believe I should trust you guys here more than a YouTube short that YouTube fed me, but I believe this short provides information contradictory to what I believe I read here. Does a water softener help or hurt water heaters? Different for tank and tankless? I wonder how I should design my combi + (electric heat pump) tank setup.

  • mknmike
    mknmike Member Posts: 167

    regarding my sizing/consumption. Tuesday and Wednesday this week are two days where I burnt bonfires to help with the heating and just left the thermostats to run their programs including the morning (upstairs) and evening (downstairs) increases beyond the 62 F setting.

    I was pleased to see that it looks like the new boiler should be able to (at a minimum) hold the 62 F setting when running full tilt. Since it will be unlikely to heat the place anywhere near as fast as the current boiler, we will probably need to keep the temps higher than 62 F to be able to feel as comfortable getting out of bed in the morning. I wish I could pretend I’m the type of guy that would be able to get up early and start a fire, but maybe there will be some additional heat source I will be able to add in the future that will perhaps focus just on the master bedroom as opposed to the entire house. These are some of the reasons that I wonder if keeping the old boiler for a bit of time might be good to do until I can prove out the new boiler. Two primary loops? One for each boiler? Maybe put the garage boiler in the house instead of the garage? Or just buy a third identical boiler for the house? Just trying to plan ahead.


    Seeing that the reported low from the power company only gets as low as 9 F, I need to wait for a few more days of data to come in bc I think I heard on the radio that it was 6 F this morning. It’s been sunny though, and our roof is painted black. Some neighbors expressed some concern about the energy required for cooling when I was painting, but I quickly responded that we spend far more on heating than cooling here.

  • mknmike
    mknmike Member Posts: 167

    ok. Data has come in for Tuesday and Wednesday, the coldest days we’ve had in years. I think I may need to take a look at the stove which we used only to cook rice both Tuesday and Wednesday, but I’m going to guess that spikes at 11 PM must have been from showers and the single 40k BTU water heater chiming in along with the heater. No temps get turned up automatically, and I’m unaware of any doors being left open at 11-12 PM Wednesday night. So the natural gas peak usage seems strange at that hour. Maybe my wife increased the temps? I may want to have something like the AirThings that I have in the basement that logs temps bc I don’t know a way to look at the setting history on my thermostats.

  • mknmike
    mknmike Member Posts: 167

    Knowing my water heater tank requirements are pretty limited, I thought I might search FB Marketplace for some water heaters and came across more Indirect Water Heaters, but keep coming back to the concern of the boiler temps required to fire one. This article here talks of someone with a similar situation to what I am looking to create. They have a 125k BTU TT Combi and are considering adding an indirect, but are advised to add an electric to solve the problem.

    Considerations in adding an indirect tank to a combi system — Heating Help: The Wall

    Basic electric water heaters can be had so cheap. Like there's a "new" one on FB Marketplace for $250. Throwaway money almost. HD seems to have lower prices on Heat Pump Water Heaters than Lowes, and seem to start at $1600 and go up to $3000.

    Search Results for heat pump water heater at The Home Depot

    So, in my layout design, if I opt for a heat pump water heater, I want that to be more centralized in my setup where it can dispersed the cold air better than being stuffed in a closet area. So, I guess the thing to do is put it in the open space no matter what. Maybe save all the money and test with no tank at first, but plan ahead to add a tank nearly immediately. I could use my remaining natural gas water heater as a storage tank, but if I really need additional BTU's that would make me SOL. It's better to plan to use the old natural gas water heater for a boiler water buffer tank. THAT can be stored in a closet, perhaps helping it lose fewer BTU too.

  • hot_rod
    hot_rod Member Posts: 24,202

    if you use an old gas heater for a buffer, I would disable the aquastat, maybe pull it out and free up a port. Block off the flue on top and bottom. You will still get some heat off it as jacket loss.

    It’s sounding like the air volume that HPWH manuals are suggesting, 700 sq ft, may not be adequate. This according to Larry and his friend Gary that is deeply involved in the HPWH analysis in actual run time

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mknmike
  • mknmike
    mknmike Member Posts: 167

    700 cubic feet is apparently the minimum requirement. Thanks for bringing this up. Currently the laundry room where I plan to install is about 12x10' with 7 foot tall ceilings, only about 840 cubic feet MINUS all the stuff we plan to have in there. So, the room itself will likely be too small, but we ALWAYS leave the door open. Also, I've cut the bottom 6" of wall out on one side, AND during the summer, we typically leave a fan running in there to circulate air in the basement to help assure it is kept dry. The plan will be to use the heat pump water heating only in summer when we want to cool and/or dehumidify the basement. Also, a vent up to the kitchen that is immediately above could be a really ideal setup. The closet that I am considering putting the boiler water storage tank into has a floor that I would like to re-do, and would be an ideal place to put some vents to enable some exchange / flow of air with the upstairs. I'm liking this idea! Thank you!!

  • mknmike
    mknmike Member Posts: 167

    I had to do some research to figure out whether the ProTerra or Performance Platinum was the higher level model. It sounds like the ProTerra is the higher end only offering these extras:

    • Leak Detection
    • Auto-shutoff

    You can buy the same energy factor, annual operating cost, and warranty duration for $200 extra. With this model, they just add a leak detection and auto-shutoff feature.

    I guess I will have to figure out if either of those will benefit me or cost me any extra. In the 40 gallon size, it's $1700 instead of $1600. So, in not chinsing out, I guess I'd probably opt for the extra $100. It will probably be less after I apply a coupon when I ultimately buy too.

    Rheem Proterra vs Performance Platinum - Which Water Heater is Better? (2025) | Today's Homeowner

    The next thing to figure out is whether there's be benefit to a size any larger than 40 gallons. We have had two 40 gallon tanks at low temps and rarely ever ran out of hot water. Now that we are on a single water heater, I've bumped up the temp, also reading about legionnaires and wondering if we really should have had higher temps all along. Then there's the concept of either "mixing" or bypassing the water heater altogether when using the tankless inside the combi. All those things make me feel like a smaller tank might be more ideal as we are getting by with a 40 gallon natural gas tank in the WINTER, and in the summer hot water is needed less. There will always be the Combi having the ability to make hot water too if we end up in some scenario in the summer where the heat pump won't cut it. I understand they are SLOW though if you want to be efficient. So if we do not want to use the combi in summer and be as efficient as possible, a larger tank might be the only way to do it. So…
    40, 50, 65 or 80 gallons?

    3 showers, considering adding an outdoor shower and a basement full bathroom too. Two dishwashers. 4+ bathroom sinks, a bar sink, and currently 5 people living in the house. Even though one is off to college next year, we will still have occasions where everyone is home. We could turn on the combi DHW then though. So. Maybe 40 Gallons just to be frugal with the initial purchase… or just get a regular electric tank on FB Marketplace for $250 or less. There's a good chance that these heat pump water heater prices will come down even more as they become more standard.

    No rush here but clearly making sure I have ventilation will be ideal.

  • mknmike
    mknmike Member Posts: 167

    This morning, I watched at least part of this video on building a custom flue that runs horizontally before exiting the building. It has me thinking about adding a heat exchanger for the hydronic system to a custom wood stove exhaust. I would think that these exhaust systems should have a bypass to be able to exit straight out and bypass the horizontal heat exchanger setup. But it seems in this scenario, they extract enough heat in the block they build. It looks like it might be a somewhat common design because I stumbled upon a very similar build in another video. And after a few more minutes of searches on Rocket Stoves, I see that this is a popular design. I would expect to see some rules of thumb about horizontal length, but I guess everything is trial and error with these guys. Anyway, it has me thinking more and more about my wood burning designs for my basement that I want to finish when I get the HVAC all done.

  • mknmike
    mknmike Member Posts: 167

    I learned something watching Season 18 episode 3 of This old house. “Pipe thread wicking” for old pipe threads. In nearly 30 years of house work, i hadn’t used that but will be sure to add some to the tool box for when I try to tap into these old pipes.

  • yellowdog
    yellowdog Member Posts: 233

    If I sold a HPWH to a house with 5 people living in it, it would be a 65 gallon minimum and I would push them towards an 80 gallon.

  • mknmike
    mknmike Member Posts: 167

    Thank you for the comment. Would it make much difference if you knew that the plan was to only use it for summer hot water heating and just as a storage tank for winter hot water heating? That's my plan, as I'd like to use it as a dehumidifier / basement air conditioner in summer, perhaps with air-exchange with the kitchen above. But I assume the Combi functionality of the ModCon Combi boiler I've purchased will be more ideal for winter hot water. I guess there could be scenarios where we might want to have them both operational at the same time getting heat out of both, but if I can keep the kids from taking 60-minute showers, that would be ideal. I've read that it could be ideal to keep the kids bathrooms on a small tank with slow recovery and keep the master bath on an endless supply of tankless.

    This diagram is the baseline for my plan to have a tank added to the tankless DHW.



  • hot_rod
    hot_rod Member Posts: 24,202

    Do you have off peak electric rates? If so run the HPWH tank to 140F on the low rate, then have a mixer on it set to 120. With an 80 gallon that should get you a days worth of dhw.

    But 60 minutes showers may take a lot more horsepower :) That is where a tankless or combi shine, non stop at the achievable delta.

    Not all tankless will accept pre-heated water. He is what I got from a Rinnai trainer.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Martial_7erran
    Martial_7erran Member Posts: 36

    I have seen antique and modern wood-fired water-circulating systems. But, do not try to add wood fire heating to an existing hot water (gas fired) system. Wood can generate heat above 1400 degrees F and higher, any you cannot predict the temperature nor the pressure in any pipes. Burn wood if you must, but do not try to add wood heat to an existing pipe system. Consider a rocket-mass-heater system, using chimney through mass to distribute heat from wood fire.

  • mknmike
    mknmike Member Posts: 167

    Reading from Rinnai, this stuff seems like it could get complicated quickly.

  • mknmike
    mknmike Member Posts: 167

    Thanks for that. I see that in scenarios where water doesn’t move fast enough, you quickly get boiling that can be a serious pressure increase. I wonder if a setup could be created with a pressure sensor that would assure a pump goes nuts if the pressure gets high (enough).


    But yeah. I get it. The hydronic is simply a way to enable the heat from the fire to go anywhere the thermostats need it, and reduce my dependence on natural gas. However, if using an outdoor reset, I guess it could be both good and bad if it would cause the boiler to not run bc the target temps get exceeded.

  • Martial_7erran
    Martial_7erran Member Posts: 36

    "I wonder if a setup could be created with a pressure sensor that would assure a pump goes nuts if the pressure gets high (enough)."

    I think you could not realistically depend upon a "pressure sensor" nor depend upon an electric "pump" to protect from a woodfire induced steam explosion within the pipes. Once the 400 degree steam is suddenly in existence, pop goes the pipes, and then increasing flow through a pump will make no difference. Some woods, like ironwood (horned hopbeam) and ultra-dry wood will start to melt your stove itself, so you cannot predict the temperature nor the resulting pressure.

  • mknmike
    mknmike Member Posts: 167

    sorry I forgot to answer about the off-peak. We don’t have lower rates any time of day, but there is a “peak load calculation” or “peak load contribution” that can be up to maybe 25% of the bill and our delivery charges overall seem to be approximately equal to the cost we pay per kWh, like a $250 electric bill will likely be $125 of usage charges and $125 of delivery charges, probably including the PLC in the delivery charges. So we charge the Tesla Model 3 RWD (base vehicle with best mile/kwh) at night, just before we are scheduled to depart each day. Aside from no AC running, we used the electric heavily last month, even space heaters and some 1500 watt heat tape on the pool ice trying to assure it didn’t put pressure on the pool walls. It was $280 while the natural gas was $430, $710 overall. Coldest month we’ve had in the house.

    In any case, I like the idea of having the electric on a timer, assuring it will not use electricity between noon and 8 pm, our peak hours.

  • mknmike
    mknmike Member Posts: 167

    This question may be worthy of another thread, but I’m curious how much heat I’ve put into the drafty den heating zone this year. It has its own pump, so maybe there could be a way of recording the water temp and the run time to do some calculations of how much heat each zone has consumed. I imagine this would be helpful to have in properties where rental units share a common heat source. I will want to research if that is something I might be able to add. A “zone meter” for hydronic??

  • mknmike
    mknmike Member Posts: 167

    I realized I’ve stalled, but I’ve been trying to get my basement organized before this next project really gets fired up. Sorry for the delay to anyone that might be following. Still deciding on exactly where to mount the new boiler in the basement. I’m not looking to try and make the change before warmer weather comes, where I might be able to go a few days without the boiler. I’m hoping the existing water heater and boiler can last. I will be quite embarrassed if they fail before I get this new boiler running.

    I was looking at the gas lines and how I will be able to drastically simplify the gas lines in the basement and what will need to be capped. I think there’s going to be some significant demo that needs to be done in the basement to do this right. That also means cleaning up the garage so I can move stuff out of the basement and into the garage.