EK E130 errors
Comments
-
I would like to add a perspective from a customer who had this system ( Resolute rt) for a bit longer than 3 years. Before pulling the trigger on one of these, look into who will be servicing your unit, and what is their
hourly rate.Here in Southern MA we have exactly one dealer/EK certified service provider. They happen to be pretty expensive. True, some parts have a lifetime warranty, but many common parts ( pump, igniter, solenoid, Air inducer and the like) are only covered for 3 years. My Resolute worked like a dream for the first 3 years. If you asked me a year ago, I would have given it a 5 start review. Quiet, clean. efficient. I did not even know it had a reset button.
A couple of months ago started having trouble with sporadic "ho flame" lockouts. 3 service visits later the Solenoid was diagnosed to be faulty, and replaced to the tune of $580. This did not fix the sporadic lockouts, but made them less frequent. To this day, it has never been definitively diagnosed what causes these.
I notice a couple of days ago the air inducer become loud, makes a sound like a bearing screech. Likely will have to be replaced, the part is about $400. I am getting an estimate tomorrow on labor. The return temp gets unreasonably hot, to the point that the unit throws E130 errors (seen 3 in the last 3 months). Maybe it is related to the air inducer. maybe some sensor…
My impression is that it works great when it works, but the maintenance can be a problem. It sounds like an attractive proposition, but the repair costs in the past couple of month will likely wipe out any savings I may have achieved due to the high efficiency. Plus there is an extra premium up front.Perhaps there is something to be said about a less efficient, common, simpler system, that any average burner tech can work on, at some reasonable hourly rate. Knowing what I know now, I would probably not chose an EK system again.
1 -
Thank you for your post, @mrcoder .
Please PM me or contact us with your location so we can connect you with our territory manager in your area to help you can get support and a quick resolution. We’d like to find out more about your specific circumstances and what is happening with your system. For reference, the E130 diagnostic code is often a circulator issue, and, like the solenoid valve you mentioned, both parts are industry standard and not unique to the system.
Thank you,
Roger
President
Energy Kinetics, Inc.1 -
-
-
-
-
@mrcoder, we've started a new discussion for you here so that your questions don't get lost at the bottom of an older discussion. This will help avoid confusion as we help resolve any issues with your system.
Forum Moderator
4 -
Kudos to EK for their outstanding customer support, and standing behind their product.
The Air inducer was replaced, and the Taco 007E circulator was proactively replaced by a simpler, more robust model. My EK territory manager Brian came on-site with my service provider to give a hand with the Air Inducer upgrade. The new an improved Air inducer looks good, quiet as a mouse.
Brian noticed my high return temperature, and he immediately replaced the return temp heat sensor. The burner now shuts off if it goes over 170 -180, as it should. It is likely the sensor was the reason for the E130 errors.
Just an FYI, about 8 days ago I added a couple of oil rated check valves at the oil exit point at the tanks. This was recommended by Carlin. This is also recommended by Roth. It did not make an apparent difference. Just for yucks I checked the 4 nuts on the 2 flex lines to the Tigerloop. These all seemed a bit loose, I was able to turn them about 1/4 turn without putting a lot of torque on them.It is unclear why these came loose, as they worked fine for the first 3 years.. The bottom line: I did not have a single lockout since I tightened these nuts, going on now for a week.
2
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements