PressureTrol Settings
Giovanni722
Giovanni722 Member Posts: 19
hi all, could you please help me confirm that my pressure trip settings are right. Before this was set to 2.5 psi and I have dropped it a bit since my last post but I didn’t touch the left lever. Could you please help me make sure that what I have is right? 1700 sqft house with 9 steam radiators. Much appreciated as always!
    Jamie Hall Member Posts: 27,007
    That will do for one pipe steam and "normal" two pipe, although you could go a bit lower on the main scale.
  • Giovanni722
    thanks as always @Jamie Hall, drop is to 2? Or below 2?
    Try just a shade below 2
    ethicalpaul Member Posts: 8,373
    I’d put the diff at 1 probably, but these devices are so poorly calibrated that it’s impossible to tell what they’re actually doing unless you have a 0-3psi gauge next to them that you can refer to as they operate
  • Giovanni722
    Im starting to hear a lot of clanging in my pipes after the heat cuts off… could this have anything to do with the pressure settings? I replaced all of the steam vents… how can I bleed the system of air? Thanks! @Jamie Hall @ethicalpaul
    banging is from steam or water getting where it’s not supposed to be due to incorrect piping and/or surging from bad water.
    Do your radiators have one pipe or two?
    I can’t get a good read on your piping from those pictures
  • Giovanni722
    the radiators have one pipe so I have them pitched back to the valve. @ethicalpaul
    edited January 2025
    Don't worry about the pitch. I was asking to find out if you had a 1-pipe or 2-pipe system 🙂
    Since you have a 1-pipe system, no the pressuretrol settings are not causing your banging.
    Can you show some pictures of your wet return (the pipe you probably have that is near the floor that returns water to the boiler)? and some more of the pipes above your boiler? (take the photos from a few feet away and several angles so we can see all the pipes and the boiler from the floor to the ceiling.)
    I really want to see the side opposite your pressuretrol. It looks like that's where your return reconnects to the boiler but I can't tell for sure.
  • Giovanni722
    @ethicalpaul these were the best I could do! Thanks!
    Thank you, that's very good. It may be that the hartford loop is too high. I'll show you a cutaway of what I'm talking about.
    You don't want this to be at the waterline or I think it can bang. You might try a lower or higher waterline temporarily to see if the banging goes away.
    tcassano87
    This part is good. It's good to have the wet return very low like this:
  • tcassano87
    tcassano87 Member Posts: 112
    pressuretrol should be
    2 at Main
    1.5 at differential
    So you will have a high of 2psi and a low of .5psi
  • tcassano87
    Hartford Loop should be 2” below the water level
    edited January 2025
    The header construction seems odd too, I can't quite figure it out even from the new pictures. I think the two supply pipes are on opposing sides of a cross with the mains being fed from the other opposing sides.
    Do you see the water level dropping more than about 1/2" during steam production?
    mattmia2 Member Posts: 16,007
    Are you sure this noise is water hammer and not expansion and contraction of the piping or other parts?
    It is a little unusual for water hammer to start after the boiler stops.
    Your near boiler piping is….creative.
    The fact that the skim port looks like it has never been used doesn't look like a good sign. What happens to the water level during a cycle?
  • Giovanni722
    I bought this house 2 years ago and inherited this boiler so it’s my first time ever having a steam boiler lol it may not be a water hammer… it sounds more like a gong up in my bedroom… but the. While I’m sitting in my living room, I hear bangs downstairs by the boiler… doesn’t happen a lot but enough to annoy me… yeah I agree that the piping is… interesting… also it seems I should be upping the main psi to 2 and differential to 1.5 in the pressuretrol? And yeah I’ve never used the skim port? Should I be? Should I get a professional here? I appreciate all the responses!
    The skim port should have been used by the installer to remove the oils from the boiler when it was installed.
    The pressuretrol should be at more like 8 oz/in^2 but that control doesn't go that low. it needs almost no pressure for the steam to move. Like a couple in wc.