Power vent heater
I have a power vent water heater which I think made a strange sound today for about two seconds.
I was thinking it could be the draft inducer's motor / fan assembly. I put my hand on the motor
while it was running and it seemed pretty hot.
So I'm wondering if that's normal ?
Id prefer to use numbers rather than "feels hot" because we have no way of knowing what that means.
Do you have an IR thermometer?
Good point, no I don't but, I have to remove my hand after twenty seconds or it will start to burn.
So maybe 135* ?
I have a temperature strip sticky that came with my mixing valve, I'll put that on it and see.
Fwiw
Short of letting it run another half hour it looks like it topped off at 125* surface temperature.
And the cooling fan is blowing air.
Just a bump, I would say this is normal, anyone disagree ?
Whats the room temperature?
The motor is rated for 2.8 amps. Actual is…?
it look pretty dirty in the cooling slots, blast it out with some compressed air. Can hurt.
Good ideas guy's, thanks..
It wasn't as dirty as it looked but I cleaned it anyway.
Running at that temperature 120/125* it was drawing 2.26 amps… at 64* room temp..
Drawing 2.26 and rated for 2.8 Not bad. ASSUMING the voltage is 115.
it is…