Replacement steam boiler: short cycling on LWCO + NBP BANGING

Options

hi folks, happy holidays

Homeowner here, about 60mi NW of NYC in a single-pipe, 21-radiator c1840 single family two story + basement residence.

Requesting your collective wisdom please.

25yr-old Weil McLain cracked and died a few weeks ago. Old boiler and the overall single-pipe system had been running great all these years (we've been in the house 30yrs). Replaced with same make/model to try to reduce variables (Model EG-75 - https://www.weil-mclain.com/products/eg-series-6-gas-boiler) . I requestd team to replicate NBP precisely, but found some slight differences (will call them out below)

New boiler observations below. The following steps are reproduceable every time thermostat calls for heat:

  1. Thermostat calls for heat, new boiler fires
  2. Takes a few min to get up to temp and start producing steam
  3. Next two steps occur at same time:
    1. Two Mains (each with Gorton #1's) begin to vent
    2. As they vent, gauge glass water level drops to zero/below zero (not visible)
  4. Since water level drops completely, LWCO fires & shuts down burners
  5. Within a few seconds, as condensate starts to form, HUGE amt of banging begins (can't exactly tell if banging location is in header and/or Hartford loop) and lasts a few seconds
  6. Condensate returns to boiler, raising water level, so LWCO resets, boiler refires, and whole process repeats about 3-4 times

*AFTER 3-4 SHORT-CYCLES, sysetm seems to operate fine and provides heat and function as expected.

Questions:

  1. Why the main vent—>LWCO—>resulting banging & short-cycling? e.g.
    1. Insufficient in A- or B-dimensions?
    2. Insufficient Hartford loop piping diameters?
    3. Insufficient Hartford loop "T" location relative to mid-gauge-glass?
    4. Error-prone 'horizontal' header run after risers, before step-down, piping in equalizer? (see pics)
  2. Why does it 'correct itself' after a few cycles?
    1. I notice the mains vent MOST on first cycle, then LESS each subsequent cycle. How is the venting related to 'pulling' down the water level ? I'm not familiar with that pressure relationship. Is it 'pushing' hot water into the returns during venting?

Anything I'm leaving out of the story?

NBP-Before.jpg NBP-After.jpg

happy to provide more info from homeowner perspective

Thanks in advance

Frank

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,397

    Two things come mind right away. First, did anyone thoroughly skim that new boiler, or did they just pipe it up and light it off? What you are hearing sounds as though it is surging badly, and it is very likely that a good skimming will help immensely.

    Second… That header (the big horizontal pipe above the boiler). It shouldn't be copper, but even more important does it pitch strongly to the equalizer? Put a level on it and see. It's hard to tell from the pictures — and I can't see all of it — but it almost looks as though it may be pitched the wrong way. That isn't going to help any…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • neilc
    neilc Member Posts: 3,185

    a better full picture of the header,

    and of the Ptrol settings,

    what pressure do you get up to when the water leaves the boiler?

    known to beat dead horses
    CLamb
  • ethicalpaul
    ethicalpaul Member Posts: 8,868

    Within a few seconds, as condensate starts to form, HUGE amt of banging begins 

    This isn't condensate starting to form. This is the boiler water being where it shouldn't be due to surging. There is probably a lot of oil in the boiler that the installer didn't skim.

    Condensate returns to boiler, raising water level

    This isn't the condensate returning to the boiler, this is the boiler water returning to the boiler.

    Here is a video of what is happening from when I didn't know hardly anything about my boiler:

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    edited December 2024

    The EG-75 has an input of 282K BTUH. This is sufficient to heat a small apartment building (I have done it with less). It absolutely requires 3" risers and a minimum of a 4" header………………one could make a good argument for a 5" header.

    You have none of that.

    Instead of doing the right thing and determining exactly what size boiler you require based upon the radiation, you install a giant EG-75 with totally improper near boiler piping (in copper !!) by unqualified idiots and you expect it to actually work.

    Good luck with that.

    Chiwoody08
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,236

    Supposedly installed the same boiler with the same piping. Probably wrong but probably worked before.

    Skim it or have it skimmed with TSP or washing soda and post more pictures of the boiler and the piping up and around it

    ethicalpaul
  • LRCCBJ
    LRCCBJ Member Posts: 1,043

    The operative word is "supposedly". You certainly know that this is impossible. Just look at the header.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,236

    According to the OP,

    "Replaced with same make/model" 

    You can't see enough of the header to see what they changed if anything. The only thing I can see is a reduced equalizer.

    ethicalpaul
  • LRCCBJ
    LRCCBJ Member Posts: 1,043

    I see a 3" header. But, I'm partially blind…………..😉

  • ethicalpaul
    ethicalpaul Member Posts: 8,868

    I and all of us are prone to frustration sometimes but I hope we can avoid blaming victims who did nothing wrong other than assume a licensed professional would be able to read a manual.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    rynoheatCLamb
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    edited January 2025

    Absolutely correct. I'm personally at wits end seeing endless installations that can be better accomplished by an 8 year old with a good reading ability.

    I don't quite understand why they come here AFTER THE FACT.

  • ethicalpaul
    ethicalpaul Member Posts: 8,868

    Because before the fact, they are probably under the impression that the professional they hired knows what they are doing. Then after the fact, they realize that not all of them do.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    rynoheatCLamb
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    edited January 2025

    Yes, sadly, you are correct. Barely ANY of them do.

    ethicalpaul