How do I get this pressure gauge off?
need help getting this off, tried and it’s not budging.
Comments
-
It looks like you need to use a wrench rather then pliers ….
There was an error rendering this rich post.
0 -
Wrench are too big to fit here :(
Do I have to grab one piece while turning the other?
0 -
The brass plug the gauge is mounted on has 1/4" pipe threads. It appears to be threaded into a 1/4 X 3/4" iron reducer bushing. If you remove the reducer bushing from the tee, the gauge will come with it.
I assume you are wanting to replace the gauge with a new one. When you do, use a new reducer bushing too. In addition to iron, these bushings are available in brass and stainless steel too.
Some heat might help getting these fittings apart.
Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.2 -
Heat on whichever part of the assembly you want to leave in place.
And use a wrench which fits! Not vise grips. Not pliers. Not a pipe wrench. A Crescent wrench if you have to, but a fixed jaw wrench if you can get one which fits.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
small pipe wrench on the reducing bushing.
0 -
I presume you are finished with that gauge otherwise you would not remove it.
So, take a big pipe wrench and put it on the OD of the gauge. Probably break it away from the the brass connection and now you have plenty of room to work. You could then get a decent pipe wrench on the brass connection and it will come right out of the bushing.
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements