14 year old peerless boiler started leaking

satberhoxhaj
satberhoxhaj Member Posts: 3
edited December 21 in Gas Heating

peerless boiler 63/64 349,000 BTU been doing a lot of research but i think its way over sized so I'm trying to get the correct size I have a 6unit building 5 rooms apartment and 5 radiators in each apartment radiators each radiator measuring 24" high

  1. 5 tubes 12 sections 40edr
  2. 3 t 10sec 22
  3. 3t 10sec 22
  4. 4t 10sec 27
  5. 6t 8sec 30
  6. 5t 12sec hallway 40

my calculations I'm getting 140 per apartment X 6 plus the hallway I'm getting 880 EDR now to get boiler size BTU 880x240 = 211,000 BTU can anyone tell me if I'm doing this wrong or right

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,988

    You've gone one step too far. Compare the EDR totals of your radiation to the EDR rating of the boiler. Do NOT try to convert to BTUh.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • satberhoxhaj
    satberhoxhaj Member Posts: 3

    Hey Jamie thanks for the super quick response i'm looking at the burnham steam max 250,000 BTU but i don't see an EDR rating of the boiler

  • jesmed1
    jesmed1 Member Posts: 763

    Look in the first table under "Net AHRI Rating" and you will see a column for "steam (sq. ft.)"

    https://s3-us-west-2.amazonaws.com/catsy.782/SteamMax+Product+Data+Sheet.pdf

    satberhoxhaj
  • satberhoxhaj
    satberhoxhaj Member Posts: 3

    steam max 250 is 646 sqft steam

  • jesmed1
    jesmed1 Member Posts: 763
    edited December 21

    Correct. Read this explanation from heating pro Dan Holohan, who started this site:

    https://heatinghelp.com/systems-help-center/boiler-ratings-explained/

    So your steam boiler ratings include a 33% "pickup factor" to allow for heat loss in the pipes.

    I'm just a homeowner, not a heating pro, so I won't presume to give you any advice. But if you want to get into the weeds further, you'll find plenty of debate here amongst heating pros as to whether or not that 33% pickup factor results in steam boilers being oversized for their application. Some steam boiler owners here have done fine with boilers that were sized with little or no pickup factor. YMMV.

    Following is one such debate on the subject.

    https://forum.heatinghelp.com/discussion/199165/sq-ft-of-steam-sq-ft-of-edr/p1

  • EzzyT
    EzzyT Member Posts: 1,350
    edited December 21

    If your total square footage of steam is 880 then the Burnham Steammax 350 or the Crown 49-350S would be the right match to what you need.

    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    satberhoxhaj